S95 Supervisory and Trouble Signals — Questions and Answers
Question 1: A supervisory signal is received at the fire alarm control panel indicating a valve has moved from its normal position. What is the FIRST action required?
- Silence the supervisory signal and log it
- Investigate and restore the valve to its normal position (Correct answer)
- Transmit an alarm signal to the fire department
- Disable the supervisory zone until the next inspection
Correct answer: Investigate and restore the valve to its normal position
Supervisory signals indicate off-normal conditions that must be investigated and corrected by restoring the device to its normal supervised position.
Question 2: Which of the following conditions would generate a TROUBLE signal rather than a supervisory signal?
- A dry-pipe valve that has operated
- A fire pump that has started automatically
- A ground fault on a signaling line circuit (Correct answer)
- A pressure switch indicating low system pressure
Correct answer: A ground fault on a signaling line circuit
A ground fault on a signaling line circuit indicates a wiring or circuit integrity problem, which is classified as a trouble condition.
Question 3: According to NFPA 72, how often must supervisory signals be tested in a system with central station monitoring?
- Monthly
- Quarterly
- Semiannually
- Annually (Correct answer)
Correct answer: Annually
NFPA 72 requires supervisory signal devices to be tested annually unless the authority having jurisdiction specifies a different frequency.
Question 4: A building fire alarm system displays a trouble signal with an 'open circuit' fault on initiating device circuit 3. What does this indicate?
- A device on circuit 3 has activated
- A wire break or disconnection exists on circuit 3 (Correct answer)
- Too many devices are connected to circuit 3
- Circuit 3 has a short circuit condition
Correct answer: A wire break or disconnection exists on circuit 3
An open circuit trouble indicates a wire break, loose connection, or disconnected device that has interrupted the circuit continuity.
Question 5: Which signal type is generated when a sprinkler control valve is closed more than 20% from the fully open position?
- Alarm signal
- Trouble signal
- Supervisory signal (Correct answer)
- Supervisory or alarm depending on local AHJ
Correct answer: Supervisory signal
A tamper switch on a sprinkler control valve generates a supervisory signal when the valve moves significantly from its fully open (normal) position.
Question 6: A sprinkler system water flow switch activates but no sprinkler heads have operated. The MOST likely cause is:
- Pressure surge or water hammer in the system (Correct answer)
- A supervisory signal being converted to alarm
- A trouble condition on the flow switch wiring
- Normal system test in progress without notification
Correct answer: Pressure surge or water hammer in the system
Pressure surges or water hammer can momentarily activate a flow switch without actual water flow, often called a false alarm.
Question 7: When a trouble signal is received at a protected premises FACP, NFPA 72 requires the trouble signal to be:
- Silenced immediately to avoid nuisance
- Acknowledged and investigated within 24 hours (Correct answer)
- Transmitted only if it persists for more than one hour
- Escalated directly to an evacuation alarm
Correct answer: Acknowledged and investigated within 24 hours
NFPA 72 requires trouble signals to be acknowledged and the cause investigated and corrected within 24 hours of receipt.
Question 8: What color is typically used to indicate a TROUBLE signal on a fire alarm control panel?
- Red
- Green
- Yellow or amber (Correct answer)
- Blue
Correct answer: Yellow or amber
Yellow or amber indicators are the industry-standard color for trouble signals on fire alarm control panels, distinguishing them from red alarm signals.
Question 9: A fire pump running signal at the FACP indicates:
- The fire pump has started and may indicate a demand for water (Correct answer)
- A wiring fault in the fire pump circuit
- The fire pump jockey pump has failed
- The main fire pump is shut down for maintenance
Correct answer: The fire pump has started and may indicate a demand for water
A fire pump running signal is a supervisory signal indicating the fire pump has started, which may indicate actual firefighting water demand or an automatic test cycle.
Question 10: Which device monitors the water level in a fire protection storage tank and generates a supervisory signal when the level drops below normal?
- Flow switch
- Tamper switch
- Low water level switch (Correct answer)
- Pressure supervisory switch
Correct answer: Low water level switch
A low water level switch monitors storage tank water levels and sends a supervisory signal when water drops below the minimum required level.
Question 11: According to NFPA 72, a trouble signal audible notification device at the FACP must produce a sound that is:
- Identical to the alarm sound but at lower volume
- A distinctive sound clearly different from alarm signals (Correct answer)
- Continuous tone at 85 dB minimum
- Silent if the panel is in the attended mode
Correct answer: A distinctive sound clearly different from alarm signals
Trouble signal notification must be distinctly different from alarm signals so personnel can immediately differentiate between emergency and maintenance conditions.
Question 12: A cross-zoned detection system requires two separate detection zones to activate before sounding a full alarm. If only one zone activates, the FACP would typically display a:
- Full building evacuation alarm
- Supervisory signal
- Pre-alarm or investigation signal (Correct answer)
- Trouble signal
Correct answer: Pre-alarm or investigation signal
In a cross-zoned system, single-zone activation typically generates a pre-alarm or investigation condition rather than a full alarm until the second zone confirms.
Question 13: Which of the following is classified as a supervisory signal according to NFPA 72?
- An open in the notification appliance circuit wiring
- A smoke detector with reduced sensitivity due to contamination
- A post-indicator valve moved to a partially closed position (Correct answer)
- A power supply failure at the FACP
Correct answer: A post-indicator valve moved to a partially closed position
A post-indicator valve moved from its fully open position generates a supervisory signal because it represents an off-normal condition in the suppression system.
Question 14: The purpose of a 'waterflow retard' on a wet-pipe sprinkler system alarm check valve is to:
- Increase system water pressure during demand
- Delay the alarm signal to reduce false activations from surges (Correct answer)
- Generate a supervisory signal during normal testing
- Monitor the flow switch sensitivity continuously
Correct answer: Delay the alarm signal to reduce false activations from surges
A retard chamber delays the waterflow alarm signal by a few seconds to allow brief pressure surges to pass without triggering a false alarm.
Question 15: In a fire alarm system, a 'loss of AC power' condition at the FACP is categorized as which type of signal?
- Alarm
- Supervisory
- Trouble (Correct answer)
- System reset
Correct answer: Trouble
Loss of AC primary power is classified as a trouble signal because it indicates the system is operating on backup power and the primary power source is compromised.
Question 16: A tamper switch on a fire suppression system valve is designed to generate a signal when the valve is moved from its normal position by as little as:
- 5% of its travel
- One or two turns of the hand wheel (Correct answer)
- 50% of its travel
- The valve must be fully closed to generate a signal
Correct answer: One or two turns of the hand wheel
Tamper switches are designed to activate after just one or two turns of the handwheel so that even slight valve movement is detected and reported.
Question 17: Which of the following BEST describes the difference between a 'Class A' and 'Class B' signaling line circuit in terms of trouble signal capability?
- Class A uses two-wire circuits while Class B uses four-wire circuits
- Class A provides a trouble signal AND maintains communication past a single open fault; Class B loses communication past the fault (Correct answer)
- Class A requires monthly testing while Class B requires annual testing
- Class B provides redundant supervisory monitoring while Class A does not
Correct answer: Class A provides a trouble signal AND maintains communication past a single open fault; Class B loses communication past the fault
Class A circuits loop back to the panel so a single open wire fault still allows the panel to communicate with devices on the intact portion, whereas Class B loses all devices beyond the break.
Question 18: A fire alarm system at a hospital shows a supervisory signal from the kitchen hood suppression system. The MOST likely cause is:
- The kitchen suppression agent nozzle has discharged
- A control valve on the kitchen suppression system is not in its normal position (Correct answer)
- The kitchen hood exhaust fan has failed
- A smoke detector in the kitchen has been removed
Correct answer: A control valve on the kitchen suppression system is not in its normal position
Supervisory signals from a suppression system most commonly indicate that a control valve or other supervised device has moved from its normal operating position.
Question 19: When a monitoring company receives a supervisory signal from a protected premises, the FIRST action required by NFPA 72 is to:
- Dispatch the fire department immediately
- Attempt to contact a designated representative at the protected premises (Correct answer)
- Notify the local AHJ and wait for instructions
- Log the signal and take no action until the building calls in
Correct answer: Attempt to contact a designated representative at the protected premises
NFPA 72 requires monitoring companies receiving supervisory signals to promptly attempt to contact a designated representative at the protected premises to investigate the condition.
Question 20: A carbon dioxide fire suppression system uses pressure switches to monitor the CO2 cylinder bank. A low-pressure reading from this switch would generate what type of signal?
- Alarm
- Supervisory (Correct answer)
- Trouble
- Advisory
Correct answer: Supervisory
Low pressure in a CO2 storage cylinder bank indicates the system may have insufficient agent to suppress a fire and is classified as a supervisory condition requiring investigation.
Question 21: During a fire drill, the fire alarm system is silenced and reset before all occupants have completed their evacuation. According to NFPA 72 best practices, this is:
- Acceptable if the fire marshal has authorized the drill
- Not recommended because resetting could re-silence legitimate alarm conditions (Correct answer)
- Required to prevent occupant confusion during a drill
- Only acceptable if monitoring station is notified first
Correct answer: Not recommended because resetting could re-silence legitimate alarm conditions
Resetting the system during a drill is not recommended because it can mask genuine alarm conditions that may arise during the exercise and cause personnel to ignore them.
A supervisory signal is received at the fire alarm control panel indicating a valve has moved from its normal position.
What is the FIRST action required?
What Practice Test Geeks adds beyond an AI chat for S95
An AI chatbot can quiz you, but it can't reproduce the exam conditions or keep your record. Here you get:
- A timed, full-length S95 mock exam — 35 questions in 53 minutes with a 70% pass mark, modeled on the official exam's question count and time limit, followed by a score report broken down by exam domain.
- A fixed S95 question bank: the same test every attempt, so your score is comparable from one try to the next instead of changing with every regenerated quiz.
- Progress saved on your device: completed tests, scores and missed questions stay in My Progress, so you can retake only what you got wrong.
- A printable S95 cheat sheet you can print or save as a PDF.
- S95 flashcards built from the same question bank.
These practice questions were written with AI tools. They are not real exam questions. Exam facts are checked against the official sources listed below. Not reviewed by a subject-matter expert. Editorial policy
Sources & references
Exam facts on this page (fees, format, dates, passing scores) are checked against these official sources; the date is our last check. Editorial policy
- nyc.gov — Fees, renewal, score validity, eligibility, retake policy, score release, test dates, test delivery, exam format, passing score · verified Oct 2026