HERS Blower Door & Duct Testing — Questions and Answers
Question 1: During a blower door test, what effect does a large open fireplace damper have on the result?
- It has no measurable effect
- It increases the measured CFM50, making the house appear leakier (Correct answer)
- It decreases the measured CFM50 by creating a backdraft
- It causes the fan to stall
Correct answer: It increases the measured CFM50, making the house appear leakier
An open fireplace damper is a large pathway to outside and will increase the measured infiltration (CFM50), inflating the apparent leakage of the building shell.
Question 2: What is the primary reason HERS raters must depressurize ducts to a specific pressure (typically 25 Pa) during a duct leakage test?
- To replicate worst-case wind conditions
- To standardize results so tests from different homes and raters are comparable (Correct answer)
- To maximize airflow through the ducts
- To satisfy fire code requirements
Correct answer: To standardize results so tests from different homes and raters are comparable
Standardizing at 25 Pa ensures that duct leakage measurements are consistent and comparable across different test conditions, homes, and raters.
Question 3: In a duct leakage test, CFM25 total is measured at 300 cfm and CFM25 out is measured at 180 cfm. What is the duct leakage to outside?
- 480 cfm
- 300 cfm
- 120 cfm (Correct answer)
- 180 cfm
Correct answer: 120 cfm
Duct leakage to outside equals total leakage minus leakage to conditioned space: 300 − 180 = 120 cfm.
Question 4: Which condition must be established before starting a blower door test according to RESNET standards?
- All interior doors must be open (Correct answer)
- The HVAC system must be running at full capacity
- Combustion appliances must be turned off and flues sealed
- Windows must be left partially open for pressure relief
Correct answer: All interior doors must be open
RESNET requires all interior doors to be open so that the entire conditioned envelope is pressurized or depressurized uniformly during testing.
Question 5: What does a high ELA (Effective Leakage Area) value indicate about a home?
- The home has excellent air sealing
- The home has a large equivalent hole size and poor air sealing (Correct answer)
- The HVAC system is oversized
- The windows are energy efficient
Correct answer: The home has a large equivalent hole size and poor air sealing
A high ELA means the combined leakage pathways are equivalent to a large hole, indicating poor envelope air tightness.
Question 6: During duct leakage testing, why is it important to seal all supply and return grilles before testing?
- To prevent dust from entering the duct system
- To isolate duct leakage from building envelope leakage (Correct answer)
- To increase duct pressure above 25 Pa
- To comply with OSHA confined space rules
Correct answer: To isolate duct leakage from building envelope leakage
Sealing grilles ensures that airflow measured by the duct blaster represents only leakage through duct seams and connections, not intentional supply/return openings.
Question 7: A home tests at 6 ACH50. Which HERS reference home air leakage rate would this most closely correspond to for a typical new construction standard?
- It exceeds the typical new construction benchmark of 3 ACH50 (Correct answer)
- It meets the ENERGY STAR requirement of 7 ACH50
- It is at the Passive House standard of 0.6 ACH50
- It equals the IECC 2021 mandatory maximum
Correct answer: It exceeds the typical new construction benchmark of 3 ACH50
A common new construction benchmark is 3 ACH50 or less; 6 ACH50 is twice that limit, indicating the home is leakier than typical code expectations.
Question 8: What is the purpose of the pressure pan test in duct diagnostics?
- To measure total duct leakage at 25 Pa
- To locate which registers have the greatest duct leakage to outside (Correct answer)
- To verify that the air handler is operating at design airflow
- To calibrate the duct blaster fan
Correct answer: To locate which registers have the greatest duct leakage to outside
A pressure pan placed over each register measures the pressure difference behind it, identifying registers associated with ducts that leak outside the conditioned space.
Question 9: During a blower door test, which measurement channel on the manometer typically reads building pressure with respect to outside?
- Channel A
- Channel B
- The differential channel (B-A or A-B) (Correct answer)
- The absolute pressure channel
Correct answer: The differential channel (B-A or A-B)
The differential channel measures the pressure difference between inside and outside (or across the blower door fan), which is the key value for calculating air leakage.
Question 10: A rater finds that CFM25 out (duct leakage to outside) exceeds the RESNET threshold for the home size. What is the most appropriate next step?
- Report the result and recommend duct sealing, then retest (Correct answer)
- Increase fan speed and retest immediately
- Seal the blower door and cancel the test
- Replace all ductwork before filing the HERS rating
Correct answer: Report the result and recommend duct sealing, then retest
When duct leakage exceeds thresholds, the rater reports the finding, recommends corrective duct sealing by the contractor, and then conducts a retest to verify compliance.
Question 11: What term describes duct leakage that exits into an unconditioned space such as an attic or crawlspace?
- Duct leakage to inside
- Duct leakage to outside (Correct answer)
- Envelope leakage
- Balancing bypass
Correct answer: Duct leakage to outside
Duct leakage that goes into unconditioned spaces (attic, crawlspace, garage) is called duct leakage to outside because it effectively leaves the conditioned envelope.
Question 12: Which instrument is used to simultaneously measure fan flow and building pressure difference during a blower door test?
- Duct blaster only
- Digital manometer connected to the blower door fan and building (Correct answer)
- Infrared camera
- CO2 meter
Correct answer: Digital manometer connected to the blower door fan and building
A digital manometer measures both the pressure difference across the building envelope and the flow through the blower door fan, allowing CFM50 to be calculated.
Question 13: For HERS rating purposes, what does 'verified duct leakage' mean when ducts are entirely inside conditioned space?
- Only leakage to outside matters and is measured separately
- Total duct leakage is zero by definition
- The rater may use a default duct leakage value without testing (Correct answer)
- Duct leakage to outside is assumed to equal total leakage
Correct answer: The rater may use a default duct leakage value without testing
When all ducts are confirmed to be within the conditioned envelope, RESNET allows raters to use a default duct leakage assumption rather than requiring a measured test.
Question 14: What is the typical baseline depressurization target for a blower door test per ASTM E779?
- 10 Pa
- 25 Pa
- 50 Pa (Correct answer)
- 75 Pa
Correct answer: 50 Pa
ASTM E779 and RESNET protocols specify 50 Pascals as the reference depressurization pressure, which is why results are expressed as CFM50.
Question 15: A rater suspects that wind is affecting blower door readings. Which technique helps compensate for wind-induced pressure fluctuations?
- Run the test only at night
- Take multiple fan pressure readings and average them (Correct answer)
- Block all exterior openings before testing
- Use a higher test pressure of 75 Pa
Correct answer: Take multiple fan pressure readings and average them
Averaging multiple readings or using a data-logging manometer to record many samples over time compensates for short-term wind pressure fluctuations.
Question 16: Which metric best represents the air tightness of a home independent of its volume?
- CFM50
- ACH50 (Correct answer)
- ELA
- CFM25 out
Correct answer: ACH50
ACH50 (air changes per hour at 50 Pa) normalizes CFM50 by home volume, allowing meaningful comparisons between homes of different sizes.
Question 17: During a duct blaster test, the technician notices pressure in the duct system won't reach 25 Pa even at maximum fan speed. What is the most likely cause?
- The duct system is extremely tight with no leaks
- There is a large unsealed duct opening or disconnected duct section (Correct answer)
- The manometer battery is dead
- The outside temperature is too cold
Correct answer: There is a large unsealed duct opening or disconnected duct section
If the duct blaster cannot reach 25 Pa, it usually means there is an extremely large leak—such as a disconnected duct section or an unsealed chase—allowing air to escape faster than the fan can pressurize the system.
Question 18: What is the formula for converting CFM50 to ACH50?
- ACH50 = CFM50 × 60 / conditioned volume (ft³) (Correct answer)
- ACH50 = CFM50 / floor area (ft²)
- ACH50 = CFM50 × conditioned volume / 60
- ACH50 = CFM50 / 50
Correct answer: ACH50 = CFM50 × 60 / conditioned volume (ft³)
ACH50 = (CFM50 × 60 min/hr) ÷ conditioned volume in cubic feet, converting the per-minute flow to an hourly air change rate.
Question 19: In a duct leakage test, what does a very low CFM25 out reading (near zero) with a relatively high CFM25 total reading suggest?
- The duct system has significant leaks, all within the conditioned space (Correct answer)
- The duct system has no leaks at all
- The blower door fan is malfunctioning
- The home fails ENERGY STAR duct criteria
Correct answer: The duct system has significant leaks, all within the conditioned space
High total leakage with near-zero outside leakage means ducts are leaking significantly but all the leakage goes into conditioned space, not to unconditioned areas.
Question 20: Which RESNET-recognized testing method allows duct leakage to be measured without pressurizing or depressurizing the entire duct system?
- Duct pressurization test (duct blaster)
- Pressure pan test
- Delta Q method (Correct answer)
- Tracer gas decay method
Correct answer: Delta Q method
The Delta Q method estimates duct leakage to outside by comparing house pressure with the air handler running versus off, without using a duct blaster.
Question 21: A blower door test is performed on a home with a conditioned floor area of 2,500 ft² and 8 ft ceilings. CFM50 = 1,200. What is the ACH50?
- 2.88 ACH50
- 3.6 ACH50 (Correct answer)
- 6.0 ACH50
- 0.48 ACH50
Correct answer: 3.6 ACH50
Volume = 2,500 × 8 = 20,000 ft³; ACH50 = (1,200 × 60) / 20,000 = 72,000 / 20,000 = 3.6 ACH50.
During a blower door test, what effect does a large open fireplace damper have on the result?
What Practice Test Geeks adds beyond an AI chat for HERS
An AI chatbot can quiz you, but it can't reproduce the exam conditions or keep your record. Here you get:
- A timed, full-length HERS mock exam — 55 questions in 120 minutes with a 73% pass mark, modeled on the official exam's question count and time limit, followed by a score report broken down by exam domain.
- A fixed HERS question bank: the same test every attempt, so your score is comparable from one try to the next instead of changing with every regenerated quiz.
- Progress saved on your device: completed tests, scores and missed questions stay in My Progress, so you can retake only what you got wrong.
- A printable HERS cheat sheet you can print or save as a PDF.
- HERS flashcards built from the same question bank.
These practice questions were written with AI tools. They are not real exam questions. Exam facts are checked against the official sources listed below. Not reviewed by a subject-matter expert. Editorial policy
Sources & references
Exam facts on this page (fees, format, dates, passing scores) are checked against these official sources; the date is our last check. Editorial policy
- resnet.us — Eligibility, passing score, renewal, test delivery, fees, exam format, score release, time limit · verified Oct 2026