E2 NEC Compliance 2 — Questions and Answers
Question 1: Under NEC Article 230, what is the maximum number of service disconnects permitted for a single commercial occupancy?
- 2
- 4
- 6 (Correct answer)
- 8
Correct answer: 6
NEC 230.71 allows a maximum of six service disconnects for a single commercial occupancy grouped in one location.
Question 2: NEC 210.19(A) requires that branch circuit conductors have an ampacity of at least what percentage of the continuous load they serve?
- 100%
- 115%
- 125% (Correct answer)
- 150%
Correct answer: 125%
Conductors must be sized at 125% of the continuous load to account for heat buildup under sustained operation.
Question 3: According to NEC 450.13, a dry-type transformer rated 112.5 kVA or less must have a minimum clearance of how many inches from combustible material?
- 6 inches
- 12 inches (Correct answer)
- 18 inches
- 24 inches
Correct answer: 12 inches
NEC 450.13(A) requires at least 12 inches of separation between a dry-type transformer and combustible material unless the transformer is separated by a fire-resistant, heat-insulating barrier.
Question 4: NEC 700.12 requires emergency system sources to supply full load within how many seconds of normal power failure?
- 5 seconds
- 10 seconds (Correct answer)
- 15 seconds
- 30 seconds
Correct answer: 10 seconds
Emergency systems must restore power within 10 seconds of normal source failure per NEC 700.12.
Question 5: Under NEC 404.2(C), a switch controlling a lighting outlet in a bathroom of a commercial occupancy must be located where?
- Outside the bathroom
- Inside the bathroom, away from the tub or shower (Correct answer)
- Adjacent to the panel
- At the entrance to the building
Correct answer: Inside the bathroom, away from the tub or shower
NEC 404.2(C) permits switches inside bathrooms if they are not within reach of a tub or shower.
Question 6: NEC 517.13 requires that patient care areas in healthcare facilities have what special grounding provision for receptacles and fixed equipment?
- Double-pole GFCI protection
- An insulated equipment grounding conductor in addition to the metallic raceway path (Correct answer)
- Isolated ground receptacles throughout
- AFCI protection on all circuits
Correct answer: An insulated equipment grounding conductor in addition to the metallic raceway path
NEC 517.13 mandates a redundant grounding path: both the metal raceway and an insulated EGC must be present to ensure continuity in patient care areas.
Question 7: According to NEC 225.30, a commercial building may have a maximum of how many feeder or branch circuit supplies from outside the building?
- One (Correct answer)
- Two
- Four
- Six
Correct answer: One
NEC 225.30 limits outside feeder or branch circuit supplies to one per building or structure, with specific listed exceptions.
Under NEC Article 230, what is the maximum number of service disconnects permitted for a single commercial occupancy?