E2 NEC Compliance — Questions and Answers
Question 1: Under NEC Article 230, what is the maximum number of service disconnects permitted for a single commercial occupancy?
Correct answer: 6
NEC 230.71 allows a maximum of six service disconnects for a single commercial occupancy grouped in one location.
Question 2: NEC 210.19(A) requires that branch circuit conductors have an ampacity of at least what percentage of the continuous load they serve?
- 100%
- 115%
- 125% (Correct answer)
- 150%
Correct answer: 125%
Conductors must be sized at 125% of the continuous load to account for heat buildup under sustained operation.
Question 3: According to NEC 450.13, a dry-type transformer rated 112.5 kVA or less must have a minimum clearance of how many inches from combustible material?
- 6 inches
- 12 inches (Correct answer)
- 18 inches
- 24 inches
Correct answer: 12 inches
NEC 450.13(A) requires at least 12 inches of separation between a dry-type transformer and combustible material unless the transformer is separated by a fire-resistant, heat-insulating barrier.
Question 4: NEC 700.12 requires emergency system sources to supply full load within how many seconds of normal power failure?
- 5 seconds
- 10 seconds (Correct answer)
- 15 seconds
- 30 seconds
Correct answer: 10 seconds
Emergency systems must restore power within 10 seconds of normal source failure per NEC 700.12.
Question 5: Under NEC 404.2(C), a switch controlling a lighting outlet in a bathroom of a commercial occupancy must be located where?
- Outside the bathroom
- Inside the bathroom, away from the tub or shower (Correct answer)
- Adjacent to the panel
- At the entrance to the building
Correct answer: Inside the bathroom, away from the tub or shower
NEC 404.2(C) permits switches inside bathrooms if they are not within reach of a tub or shower.
Question 6: NEC 517.13 requires that patient care areas in healthcare facilities have what special grounding provision for receptacles and fixed equipment?
- Double-pole GFCI protection
- An insulated equipment grounding conductor in addition to the metallic raceway path (Correct answer)
- Isolated ground receptacles throughout
- AFCI protection on all circuits
Correct answer: An insulated equipment grounding conductor in addition to the metallic raceway path
NEC 517.13 mandates a redundant grounding path: both the metal raceway and an insulated EGC must be present to ensure continuity in patient care areas.
Question 7: According to NEC 225.30, a commercial building may have a maximum of how many feeder or branch circuit supplies from outside the building?
- One (Correct answer)
- Two
- Four
- Six
Correct answer: One
NEC 225.30 limits outside feeder or branch circuit supplies to one per building or structure, with specific listed exceptions.
Question 8: NEC 310.15(B) permits ambient temperature correction factors to be applied to conductor ampacity. What reference temperature is used for conductors rated 60°C through 90°C in standard NEC tables?
- 25°C
- 30°C (Correct answer)
- 40°C
- 60°C
Correct answer: 30°C
The NEC ampacity tables are based on a 30°C (86°F) ambient temperature; correction factors must be applied for other ambient conditions.
Question 9: Under NEC 408.36, panelboards used as service equipment in commercial occupancies must be rated for use as service equipment, which requires what additional protection?
- GFCI on all circuits
- A main overcurrent protective device or multiple main breakers not exceeding 6 (Correct answer)
- A separate disconnect outside the panel
- Surge protection on the feeder
Correct answer: A main overcurrent protective device or multiple main breakers not exceeding 6
NEC 408.36 requires panelboards used as service equipment to have a main overcurrent device or not more than six circuit breakers to serve as the main disconnect.
Question 10: NEC 285.25 requires Type 1 SPDs installed on 120/240V single-phase services to be connected to which conductors?
- Each ungrounded conductor and the neutral (Correct answer)
- Each ungrounded conductor and the equipment grounding conductor
- The neutral and grounding electrode conductor only
- Line-to-line across the two ungrounded conductors only
Correct answer: Each ungrounded conductor and the neutral
Type 1 SPDs must connect between each ungrounded conductor and the neutral to provide proper surge protection across all legs.
Question 11: What does NEC 230.95 require on solidly grounded wye services of more than 150 volts to ground but not exceeding 600 volts phase-to-phase?
- AFCI protection
- Ground-fault protection of equipment (GFPE) (Correct answer)
- Differential relaying
- Double-ended switching
Correct answer: Ground-fault protection of equipment (GFPE)
NEC 230.95 mandates ground-fault protection of equipment for solidly grounded wye services over 150V to ground to prevent equipment damage from arcing ground faults.
Question 12: Per NEC 314.28(A)(1), straight pulls in pull boxes require the box length to be at least how many times the trade size of the largest raceway?
- 4 times
- 6 times
- 8 times (Correct answer)
- 12 times
Correct answer: 8 times
For straight pulls, NEC 314.28(A)(1) requires the box length to be at least eight times the trade size of the largest raceway entering the box.
Question 13: NEC 501.15 governs conduit seals in Class I hazardous locations. Where must seals be installed relative to the boundary of the hazardous area?
- Within 36 inches of the enclosure
- Within 18 inches of the enclosure or the boundary, whichever is less
- Within 18 inches of the hazardous area boundary (Correct answer)
- At every junction box within the hazardous area
Correct answer: Within 18 inches of the hazardous area boundary
Conduit seals must be placed within 18 inches of the hazardous area boundary to prevent ignitable vapors from traveling through the conduit system.
Question 14: According to NEC 250.66, the minimum size of the grounding electrode conductor for a service using 350 kcmil copper service conductors is:
- 4 AWG copper
- 2 AWG copper (Correct answer)
- 1/0 AWG copper
- 3/0 AWG copper
Correct answer: 2 AWG copper
NEC Table 250.66 shows that 350 kcmil service conductors require a minimum 2 AWG copper grounding electrode conductor.
Question 15: NEC 410.116(B) requires fixtures installed in fire-rated ceilings to be marked with which designation?
- UL Listed
- IC-rated (Correct answer)
- AT (Airtight)
- Listed for Through-Ceiling Penetration
Correct answer: IC-rated
Recessed luminaires installed in fire-rated assemblies must be IC-rated (Insulation Contact rated) and marked for installation in fire-rated ceilings.
Question 16: Under NEC 600.5, a sign or outline lighting system rated at 1200VA or less requires a branch circuit of at least what ampere rating?
- 15 amperes
- 20 amperes (Correct answer)
- 30 amperes
- 40 amperes
Correct answer: 20 amperes
NEC 600.5(A) requires each commercial occupancy sign to be supplied by a dedicated branch circuit rated at least 20 amperes.
Question 17: Per NEC 358.20, what is the minimum trade size for Electrical Metallic Tubing (EMT) permitted in commercial wiring?
- 1/2 inch (Correct answer)
- 3/8 inch
- 1/4 inch
- 3/4 inch
Correct answer: 1/2 inch
NEC 358.20 specifies that EMT is available in trade sizes 1/2 inch through 4 inches, making 1/2 inch the minimum permitted size.
Question 18: NEC 240.4(D) prohibits the use of overcurrent devices rated above 15 amperes to protect conductors of what size in commercial applications (copper)?
- 14 AWG (Correct answer)
- 12 AWG
- 10 AWG
- 8 AWG
Correct answer: 14 AWG
NEC 240.4(D) specifies that 14 AWG copper conductors must not be protected by overcurrent devices rated more than 15 amperes.
Question 19: According to NEC 215.2(A)(1), the minimum ampacity for feeder conductors must be the greater of the computed load or what percentage of continuous loads plus 100% of noncontinuous loads?
- 100%
- 115%
- 125% (Correct answer)
- 150%
Correct answer: 125%
Feeder conductors must be sized at 125% of the continuous load plus 100% of noncontinuous loads per NEC 215.2(A)(1).
Question 20: NEC 344.10 lists where Rigid Metal Conduit (RMC) is permitted. Which environment is specifically where RMC is permitted but IMC generally is NOT without additional protection?
- Dry, indoor locations
- Concrete encasement in direct contact with the earth (Correct answer)
- Above suspended ceilings
- In cable trays
Correct answer: Concrete encasement in direct contact with the earth
RMC's heavier wall provides corrosion resistance that makes it suitable for concrete encasement and direct burial without extra protection in most conditions.
Question 21: Under NEC 800.113, communications cables installed in commercial buildings in spaces used for environmental air handling must be:
- Plenum-rated (CMP) (Correct answer)
- Riser-rated (CMR)
- General-purpose (CM)
- Conduit-only with no cable jacketing requirement
Correct answer: Plenum-rated (CMP)
NEC 800.113 requires plenum-rated (CMP) cables in air-handling spaces because these cables produce minimal smoke and toxic fumes if involved in a fire.