Air Conditioning Repair Refrigeration System Repair — Questions and Answers
Question 1: A technician measures suction pressure that is too high and discharge pressure that is too low. What is the most likely cause?
- Overcharged system
- Faulty compressor valves (Correct answer)
- Restricted liquid line
- Low refrigerant charge
Correct answer: Faulty compressor valves
Faulty compressor valves (worn or leaking) allow high-pressure gas to bypass back to the suction side, raising suction pressure and lowering discharge pressure.
Question 2: Which refrigerant is classified as an A2L (mildly flammable) and is commonly used as a replacement for R-22 in new equipment?
- R-410A
- R-32 (Correct answer)
- R-134a
- R-407C
Correct answer: R-32
R-32 is classified as A2L (mildly flammable) and is increasingly used in new equipment as an environmentally preferable alternative.
Question 3: When replacing a filter-drier on a refrigeration system, what is the correct procedure after installing the new drier?
- Immediately recharge the system
- Pull a deep vacuum before recharging (Correct answer)
- Pressurize with nitrogen to check for leaks only
- Flush the system with refrigerant before evacuating
Correct answer: Pull a deep vacuum before recharging
After replacing a filter-drier, a deep vacuum must be pulled to remove air and moisture before recharging with refrigerant.
Question 4: A refrigerant sight glass shows bubbles even though the system appears to have adequate charge. What could cause this besides low charge?
- Overcharged system
- High ambient temperature
- Pressure drop across a restriction in the liquid line (Correct answer)
- Condenser fan running too fast
Correct answer: Pressure drop across a restriction in the liquid line
A restriction in the liquid line causes a pressure drop that can flash refrigerant into vapor, producing bubbles in the sight glass even with sufficient charge.
Question 5: What is the purpose of a suction line accumulator in a refrigeration system?
- Store extra refrigerant charge
- Prevent liquid refrigerant from entering the compressor (Correct answer)
- Remove moisture from the refrigerant
- Separate oil from the refrigerant
Correct answer: Prevent liquid refrigerant from entering the compressor
A suction line accumulator catches any liquid refrigerant before it can reach the compressor, protecting it from liquid slugging damage.
Question 6: A technician finds the compressor running but no cooling occurring and the refrigerant charge appears correct. The metering device is a TXV. What should be checked first?
- Condenser coil cleanliness
- TXV bulb contact and charge (Correct answer)
- Evaporator fan motor
- Liquid line size
Correct answer: TXV bulb contact and charge
A TXV with a lost bulb charge or poor bulb contact will stay closed, preventing refrigerant flow and causing a no-cooling condition.
Question 7: Which condition would cause a refrigeration system to short-cycle (compressor turns on and off rapidly)?
- Oversized metering device
- Low refrigerant charge tripping the low-pressure switch (Correct answer)
- Dirty air filter on the return
- High discharge superheat
Correct answer: Low refrigerant charge tripping the low-pressure switch
A low refrigerant charge causes suction pressure to drop below the low-pressure switch cutout, cycling the compressor off, then on again repeatedly.
Question 8: What does a high subcooling reading combined with high discharge pressure most likely indicate?
- Low refrigerant charge
- Non-condensables in the system (Correct answer)
- Faulty TXV
- Low condenser airflow
Correct answer: Non-condensables in the system
Non-condensables such as air in the system raise discharge pressure and subcooling because they occupy condenser space without condensing.
Question 9: When recovering refrigerant from a system, the technician must use equipment certified to which standard?
- UL 94
- SAE J2788 (Correct answer)
- ARI 700
- UL 1995
Correct answer: SAE J2788
SAE J2788 certification is required for refrigerant recovery/recycling equipment used on motor vehicle AC systems; EPA Section 608 requires similar certification for stationary systems.
Question 10: A tech notices the evaporator coil is freezing up only at the inlet. What is the most likely cause?
- Overcharge of refrigerant
- Low airflow across the evaporator
- Metering device feeding too much refrigerant (Correct answer)
- High suction superheat
Correct answer: Metering device feeding too much refrigerant
When the metering device feeds excessive refrigerant, it floods the evaporator inlet, causing ice formation at the entry point where liquid refrigerant accumulates.
Question 11: What is the minimum evacuation level (microns) typically required before recharging a residential air conditioning system?
- 10,000 microns
- 5,000 microns
- 500 microns (Correct answer)
- 100 microns
Correct answer: 500 microns
Industry standard requires pulling the system down to 500 microns or below to ensure adequate moisture and air removal before charging.
Question 12: A compressor has a burnt motor winding. After replacing it, what additional step is critical before restarting?
- Adding extra oil to the compressor
- Flushing the system to remove acid and debris (Correct answer)
- Increasing refrigerant charge by 10%
- Bypassing the crankcase heater
Correct answer: Flushing the system to remove acid and debris
A burnt motor leaves acid contamination that must be flushed out and a liquid-line suction filter-drier installed to prevent damage to the new compressor.
Question 13: Which type of oil is used in systems charged with R-410A refrigerant?
- Mineral oil
- Alkylbenzene oil
- Polyol ester (POE) oil (Correct answer)
- Polyalkylene glycol (PAG) oil
Correct answer: Polyol ester (POE) oil
POE oil is required in R-410A systems because it is miscible with HFC refrigerants and properly lubricates the compressor throughout the system.
Question 14: What does a negative superheat reading at the evaporator outlet indicate?
- Metering device is underfeeding
- System is low on charge
- Liquid refrigerant is leaving the evaporator (Correct answer)
- Condenser is oversized
Correct answer: Liquid refrigerant is leaving the evaporator
Negative superheat means the refrigerant temperature at the evaporator outlet is below saturation temperature, indicating liquid refrigerant is leaving the coil.
Question 15: A technician is diagnosing a system with low suction pressure, high superheat, and normal condenser performance. What is the most likely cause?
- Overcharged system
- Restricted or underfeeding metering device (Correct answer)
- Faulty compressor valves
- Non-condensables in system
Correct answer: Restricted or underfeeding metering device
A restricted or underfeeding metering device starves the evaporator of refrigerant, causing low suction pressure and high superheat simultaneously.
Question 16: What is the purpose of a crankcase heater on a compressor?
- Warm refrigerant before it enters the compressor
- Prevent refrigerant from migrating into and diluting the compressor oil during off cycles (Correct answer)
- Heat the discharge line to prevent freeze-up
- Maintain oil viscosity during operation
Correct answer: Prevent refrigerant from migrating into and diluting the compressor oil during off cycles
A crankcase heater keeps the compressor warm during the off cycle to prevent refrigerant from migrating and mixing with the oil, which could cause slugging on startup.
Question 17: When using an electronic leak detector on an HFC system, which type of sensor is most appropriate?
- Heated diode (heated pentode)
- Infrared sensor (Correct answer)
- Ultrasonic detector
- Halide torch
Correct answer: Infrared sensor
Infrared sensors are highly accurate for HFC refrigerants and are not destroyed by exposure to refrigerant the way heated diode sensors can be.
Question 18: A system using a fixed orifice metering device shows high suction pressure in winter. What adjustment is typically required?
- Add more refrigerant charge
- Install a larger orifice or piston
- Replace with a TXV (Correct answer)
- Clean the condenser coil
Correct answer: Replace with a TXV
Fixed orifice devices cannot modulate with changing conditions; replacing with a TXV allows proper refrigerant metering across varying outdoor temperatures.
Question 19: What symptom would a technician observe if the reversing valve on a heat pump is stuck in the heating position?
- No cooling in summer, heating works normally (Correct answer)
- No heating or cooling available
- Cooling and heating work but efficiency is low
- Compressor overheats only in heating mode
Correct answer: No cooling in summer, heating works normally
If the reversing valve is stuck in heating mode, the system will heat in both summer and winter, providing no cooling when switched to cooling mode.
Question 20: Which condition is indicated by oil streaks or staining around refrigerant line fittings and joints?
- Normal oil migration through the system
- Refrigerant and oil leak at that location (Correct answer)
- High oil concentration in the refrigerant
- Condensation from humidity
Correct answer: Refrigerant and oil leak at that location
Oil streaks at joints indicate refrigerant is leaking there, since refrigerant oil escapes along with refrigerant gas through any leak point.
Question 21: A technician measures discharge superheat of 90°F. Normal discharge superheat is 50–70°F. What does this indicate?
- Overcharged system
- Low suction superheat
- Insufficient refrigerant or low suction pressure (Correct answer)
- Condenser subcooling is too high
Correct answer: Insufficient refrigerant or low suction pressure
Excessively high discharge superheat indicates the compressor is compressing very hot, low-density gas, typically caused by low refrigerant charge or high suction superheat.
A technician measures suction pressure that is too high and discharge pressure that is too low.
What is the most likely cause?
What Practice Test Geeks adds beyond an AI chat for Air Conditioning Repair
An AI chatbot can quiz you, but it can't reproduce the exam conditions or keep your record. Here you get:
- A timed, full-length Air Conditioning Repair mock exam — 100 questions in 120 minutes with a 70% pass mark, modeled on the official exam's question count and time limit, followed by a score report broken down by exam domain.
- A fixed Air Conditioning Repair question bank: the same test every attempt, so your score is comparable from one try to the next instead of changing with every regenerated quiz.
- Progress saved on your device: completed tests, scores and missed questions stay in My Progress, so you can retake only what you got wrong.
- A printable Air Conditioning Repair cheat sheet you can print or save as a PDF.
- Air Conditioning Repair flashcards built from the same question bank.
Practice questions written with AI assistance and published by Nathan Beja, founder of Practice Test Geeks. They are not real exam questions. We have not yet matched this exam's facts to an official source, so confirm fees, dates and rules with the exam body. Editorial policy