Air Conditioning Repair Installation and Evacuation Procedures — Questions and Answers
Question 1: What is the minimum recommended vacuum level (microns) before closing service valves and charging a residential AC system?
- 500 microns (Correct answer)
- 1000 microns
- 2000 microns
- 5000 microns
Correct answer: 500 microns
Most manufacturers and industry standards require a vacuum of 500 microns or lower to ensure all moisture and non-condensables are removed.
Question 2: When installing a split-system AC, the indoor air handler should be level or slightly tilted in which direction?
- Tilted slightly toward the drain outlet (Correct answer)
- Perfectly level in all directions
- Tilted slightly away from the drain outlet
- Tilted toward the refrigerant line set
Correct answer: Tilted slightly toward the drain outlet
The air handler should pitch slightly toward the condensate drain outlet so gravity assists condensate removal and prevents pan overflow.
Question 3: Which tool is used to flare the end of copper tubing for refrigerant line connections?
- Flaring tool (Correct answer)
- Pipe cutter
- Swaging tool
- Tube bender
Correct answer: Flaring tool
A flaring tool is used to create a conical flare on the end of copper tubing that mates with flare fittings for leak-free refrigerant connections.
Question 4: What is the purpose of installing a P-trap on a condensate drain line?
- To prevent sewer gases from entering the unit (Correct answer)
- To increase condensate flow rate
- To filter debris from condensate
- To measure condensate volume
Correct answer: To prevent sewer gases from entering the unit
A P-trap creates a water seal that prevents sewer gases and odors from being drawn into the air handler through the drain line.
Question 5: During a standing vacuum test, if micron gauge readings rise rapidly after the pump is isolated, this most likely indicates:
- A leak in the system or connections (Correct answer)
- The vacuum is too deep
- Normal refrigerant outgassing
- The gauge is malfunctioning
Correct answer: A leak in the system or connections
Rapid micron rise after pump isolation indicates a leak allowing air or moisture to enter the evacuated system.
Question 6: What is the correct sequence for connecting refrigerant manifold gauges to a system?
- Low-side blue hose to suction, high-side red hose to liquid/discharge, center yellow hose to refrigerant source (Correct answer)
- High-side red hose to suction, low-side blue hose to liquid, center hose to vacuum pump
- Center yellow hose first, then high-side, then low-side
- Low-side to discharge, high-side to suction, center to manifold
Correct answer: Low-side blue hose to suction, high-side red hose to liquid/discharge, center yellow hose to refrigerant source
Standard manifold gauge protocol connects blue (low) to suction service port, red (high) to liquid/discharge port, and yellow center hose to refrigerant cylinder or vacuum pump.
Question 7: When running refrigerant line sets through walls or floors, technicians must use:
- Grommets or bushings to protect tubing from abrasion (Correct answer)
- Standard drywall anchors only
- PVC conduit rated for gas service
- Metal strapping without cushioning
Correct answer: Grommets or bushings to protect tubing from abrasion
Grommets or bushings protect copper refrigerant tubing from abrasion at wall penetrations, preventing wear-through that could cause leaks.
Question 8: What happens if a technician charges an AC system with non-condensable gases (such as air) still present?
- High-side pressure will be abnormally elevated (Correct answer)
- System will cool more efficiently
- Suction pressure will drop below normal
- Refrigerant will condense faster
Correct answer: High-side pressure will be abnormally elevated
Non-condensable gases raise head pressure above normal because they occupy condenser volume without condensing, reducing system efficiency and capacity.
Question 9: The recommended maximum lineset length without adding extra refrigerant charge for most mini-split systems is typically:
- 25 feet (pre-charged factory amount) (Correct answer)
- 100 feet
- 50 feet
- 10 feet
Correct answer: 25 feet (pre-charged factory amount)
Most mini-split systems are pre-charged at the factory for approximately 25 feet of lineset; additional refrigerant must be added for longer runs per manufacturer specs.
Question 10: Which type of copper tubing is required for ACR (Air Conditioning and Refrigeration) refrigerant line sets?
- Dehydrated, nitrogen-charged ACR copper tubing (Correct answer)
- Standard Type M plumbing copper
- Galvanized steel tubing
- CPVC plastic tubing
Correct answer: Dehydrated, nitrogen-charged ACR copper tubing
ACR-grade copper tubing is cleaned, dehydrated, and sealed with nitrogen to prevent moisture and contamination that would damage refrigerant systems.
Question 11: When insulating suction line tubing on an AC installation, the insulation must be:
- Continuous with no gaps, joints sealed, and of adequate wall thickness (Correct answer)
- Applied only at the outdoor unit connection
- Limited to areas exposed to direct sunlight only
- Installed over the liquid line only
Correct answer: Continuous with no gaps, joints sealed, and of adequate wall thickness
Suction line insulation must be continuous and fully sealed to prevent condensation, heat gain, and capacity loss throughout the entire lineset run.
Question 12: What is the primary reason technicians perform a nitrogen pressure test before evacuating a new AC system?
- To identify and locate leaks before pulling a vacuum (Correct answer)
- To purge contaminants from the lineset
- To pre-charge the system with nitrogen
- To test electrical connections under load
Correct answer: To identify and locate leaks before pulling a vacuum
Nitrogen pressure testing at 150–300 psig reveals leaks at joints and connections before the vacuum process, since a vacuum cannot identify leak locations.
Question 13: An outdoor condensing unit must be installed at least how far from the structure to ensure adequate airflow?
- Per manufacturer specifications, typically 12–18 inches minimum clearance (Correct answer)
- No clearance is required on any side
- At least 10 feet from the structure
- Only the discharge side needs clearance
Correct answer: Per manufacturer specifications, typically 12–18 inches minimum clearance
Manufacturers specify minimum clearances (commonly 12–18 inches on sides) to ensure adequate airflow and prevent hot discharge air recirculation.
Question 14: When brazing copper refrigerant lines, nitrogen should be flowing through the tubing during the brazing process to:
- Prevent oxidation (scaling) inside the copper tubing (Correct answer)
- Speed up the cooling process after brazing
- Increase braze filler flow rate
- Purge refrigerant oil from the line
Correct answer: Prevent oxidation (scaling) inside the copper tubing
Flowing dry nitrogen through copper tubing during brazing displaces oxygen, preventing copper oxide scale formation that could contaminate the refrigerant system.
Question 15: A dual-stage vacuum pump should have its oil changed:
- After each use or when the oil appears dark and contaminated (Correct answer)
- Only when the pump fails to reach target vacuum
- Once per year regardless of use
- Every 500 operating hours only
Correct answer: After each use or when the oil appears dark and contaminated
Vacuum pump oil absorbs moisture during system evacuation and should be changed after every use to maintain the pump's ability to achieve deep vacuums.
Question 16: What is the correct refrigerant line sizing rule regarding the suction line versus the liquid line?
- The suction line is always larger in diameter than the liquid line (Correct answer)
- Both lines are always the same diameter
- The liquid line is always larger than the suction line
- Line diameter depends only on refrigerant type, not pressure side
Correct answer: The suction line is always larger in diameter than the liquid line
Suction line carries low-pressure vapor (low density) and must be larger diameter than the liquid line to maintain proper refrigerant velocity and oil return.
Question 17: When an AC outdoor unit is installed on a rooftop, the mounting platform must:
- Be structurally rated for the unit weight and allow for vibration isolation (Correct answer)
- Be constructed of wood for flexibility
- Be elevated exactly 12 inches above the roof surface
- Be secured with standard wood screws only
Correct answer: Be structurally rated for the unit weight and allow for vibration isolation
Rooftop installations require structurally adequate, properly rated supports with vibration isolation pads to protect both the unit and the roof structure.
Question 18: Which EPA regulation governs the handling and recovery of refrigerants during AC service and installation?
- Section 608 of the Clean Air Act (Correct answer)
- OSHA 1910.119
- Section 407 of the Energy Policy Act
- ASHRAE Standard 90.1
Correct answer: Section 608 of the Clean Air Act
EPA Section 608 prohibits venting refrigerants and requires certified technicians to use approved recovery equipment during service, maintenance, and installation.
Question 19: What is 'triple evacuation' (also called 'three-step evacuation') used for?
- Removing moisture more effectively by breaking vacuum with dry nitrogen between pulls (Correct answer)
- Charging the system in three stages to prevent slugging
- Testing system performance at three different load conditions
- Evacuating three separate refrigerant circuits simultaneously
Correct answer: Removing moisture more effectively by breaking vacuum with dry nitrogen between pulls
Triple evacuation involves pulling vacuum, breaking with dry nitrogen, then repeating twice more — each cycle draws out more moisture than a single long pull.
Question 20: The condensate drain line for a horizontal air handler installed in an attic should include:
- A secondary drain pan with a separate overflow drain or safety switch (Correct answer)
- Only the primary drain — secondary systems are optional
- A check valve to prevent backflow
- A UV light to sterilize condensate
Correct answer: A secondary drain pan with a separate overflow drain or safety switch
Attic-installed air handlers require a secondary condensate pan with drain or float switch to prevent ceiling water damage if the primary drain clogs.
Question 21: When installing a ductless mini-split, the wall sleeve (line set hole) should be drilled at a slight downward angle toward the outside to:
- Allow condensate from the wall sleeve area to drain outdoors (Correct answer)
- Improve refrigerant flow velocity
- Reduce vibration transmission into the wall
- Allow easier electrical wire routing
Correct answer: Allow condensate from the wall sleeve area to drain outdoors
A slight downward pitch toward the exterior ensures any water that enters the wall sleeve hole drains outward rather than into the structure.
What is the minimum recommended vacuum level (microns) before closing service valves and charging a residential AC system?
What Practice Test Geeks adds beyond an AI chat for Air Conditioning Repair
An AI chatbot can quiz you, but it can't reproduce the exam conditions or keep your record. Here you get:
- A timed, full-length Air Conditioning Repair mock exam — 100 questions in 120 minutes with a 70% pass mark, modeled on the official exam's question count and time limit, followed by a score report broken down by exam domain.
- A fixed Air Conditioning Repair question bank: the same test every attempt, so your score is comparable from one try to the next instead of changing with every regenerated quiz.
- Progress saved on your device: completed tests, scores and missed questions stay in My Progress, so you can retake only what you got wrong.
- A printable Air Conditioning Repair cheat sheet you can print or save as a PDF.
- Air Conditioning Repair flashcards built from the same question bank.
Practice questions written with AI assistance and published by Nathan Beja, founder of Practice Test Geeks. They are not real exam questions. We have not yet matched this exam's facts to an official source, so confirm fees, dates and rules with the exam body. Editorial policy