Air Conditioning Repair Electrical Components and Controls — Questions and Answers
Question 1: A contactor's coil is rated at 24V but the unit reads only 18V at the coil terminals during a call for cooling. What is the most likely cause?
- Low voltage from the transformer secondary (Correct answer)
- Shorted contactor contacts
- Incorrect thermostat setting
- Overcharged refrigerant system
Correct answer: Low voltage from the transformer secondary
Insufficient transformer output or excessive voltage drop in the 24V control circuit causes low coil voltage, preventing the contactor from pulling in fully.
Question 2: What is the purpose of a run capacitor in a single-phase PSC compressor motor?
- To boost starting torque only
- To maintain a phase shift that improves running efficiency (Correct answer)
- To protect against short cycling
- To limit inrush current at startup
Correct answer: To maintain a phase shift that improves running efficiency
A run capacitor stays in the circuit continuously, maintaining the phase shift between run and start windings to improve motor efficiency and power factor.
Question 3: A dual-run capacitor is labeled 40/5 MFD 440V. Which terminal pair connects to the compressor?
- HERM and C (Correct answer)
- FAN and C
- HERM and FAN
- C and GND
Correct answer: HERM and C
The HERM (hermetic) terminal and C (common) terminal form the 40 MFD section used for the compressor motor.
Question 4: Which safety device opens on a rise in discharge pressure and automatically resets when pressure drops?
- Low-pressure switch
- High-pressure switch (auto-reset) (Correct answer)
- Thermistor
- Fusible plug
Correct answer: High-pressure switch (auto-reset)
An auto-reset high-pressure switch opens the control circuit when discharge pressure exceeds its setpoint and closes again once pressure falls below the reset point.
Question 5: A technician measures 240V across a contactor's load-side terminals with the contactor pulled in. What does this indicate?
- Normal operation with load connected
- Open contacts with load disconnected (Correct answer)
- Welded contacts
- Low line voltage
Correct answer: Open contacts with load disconnected
Voltage across open load-side terminals indicates the contactor is not closing; if the contacts were closed, voltage would be near zero across them.
Question 6: What happens to a start capacitor if it remains in the circuit longer than a few seconds?
- It charges to full system voltage
- It overheats and can fail or explode (Correct answer)
- It improves motor efficiency
- It reduces starting torque
Correct answer: It overheats and can fail or explode
Start capacitors are designed for short-duration use only; prolonged energization causes excessive heat buildup leading to failure.
Question 7: A potential relay used in a hard-start kit opens its contacts when which condition is met?
- Compressor discharge pressure rises
- Back-EMF across the start winding reaches approximately 75% of line voltage (Correct answer)
- Outdoor ambient temperature exceeds 95°F
- Suction pressure drops below 70 psig
Correct answer: Back-EMF across the start winding reaches approximately 75% of line voltage
The potential relay monitors the voltage induced in the start winding; once back-EMF rises to the relay's pick-up voltage, it opens to remove the start capacitor from the circuit.
Question 8: What is the primary function of a crankcase heater on a compressor?
- To keep refrigerant subcooled during the off cycle
- To prevent refrigerant migration and oil dilution during the off cycle (Correct answer)
- To warm the discharge line in cold weather
- To maintain suction superheat
Correct answer: To prevent refrigerant migration and oil dilution during the off cycle
Crankcase heaters keep the compressor oil warm so refrigerant does not migrate into the crankcase and dilute the lubricant during shutdown.
Question 9: A time-delay relay in an AC control circuit is set for 5 minutes. What is its purpose?
- To allow the condenser fan to pre-cool before the compressor starts
- To prevent short-cycle compressor restarts (Correct answer)
- To sequence the indoor blower off after the compressor
- To delay thermostat response to setpoint changes
Correct answer: To prevent short-cycle compressor restarts
Time-delay relays prevent short cycling by enforcing a minimum off time before the compressor can restart, protecting it from pressure equalization issues.
Question 10: When testing a capacitor with a capacitance meter, a reading of zero indicates what condition?
- The capacitor is within tolerance
- The capacitor is overcharged
- The capacitor is open (internally broken) (Correct answer)
- The capacitor has a shorted dielectric
Correct answer: The capacitor is open (internally broken)
A zero capacitance reading means the internal element is open and the capacitor cannot store a charge.
Question 11: A compressor is wired to a 208/230V disconnect. Which wire gauge is required for a 30-amp circuit per NEC?
- 14 AWG
- 12 AWG
- 10 AWG (Correct answer)
- 8 AWG
Correct answer: 10 AWG
NEC requires 10 AWG copper conductors for a 30-amp circuit at standard ambient temperatures.
Question 12: What type of transformer is typically used to supply 24V control voltage in a residential split system?
- Autotransformer
- Step-down transformer (Correct answer)
- Step-up transformer
- Isolation transformer with center tap
Correct answer: Step-down transformer
A step-down transformer reduces line voltage (120V or 240V primary) to 24V AC for the low-voltage control circuit.
Question 13: A technician finds a blown 3-amp control fuse repeatedly. What is the correct diagnostic approach?
- Replace with a 5-amp fuse for a permanent fix
- Disconnect control wiring sections to isolate the short before replacing the fuse (Correct answer)
- Replace the thermostat immediately
- Replace the transformer and fuse together
Correct answer: Disconnect control wiring sections to isolate the short before replacing the fuse
Isolating sections of the control circuit identifies the shorted wire or component causing the overcurrent before replacing the fuse.
Question 14: What does a locked-rotor amperage (LRA) rating indicate on a compressor nameplate?
- The maximum current the compressor draws during normal operation
- The inrush current drawn when the motor first starts (Correct answer)
- The current at which the overload protector trips
- The full-load amperage at rated conditions
Correct answer: The inrush current drawn when the motor first starts
LRA is the high initial current drawn by a stalled or starting motor before it reaches operating speed.
Question 15: A variable-speed ECM blower motor is not responding to a speed signal from the control board. After confirming 24V supply to the module, what is the next step?
- Replace the capacitor
- Check the PWM or DC analog signal wire from the board to the motor module (Correct answer)
- Measure discharge air temperature
- Check refrigerant charge
Correct answer: Check the PWM or DC analog signal wire from the board to the motor module
ECM motors receive a speed-control signal (PWM or 0–10V DC) from the board; loss of this signal causes the motor to default to a fixed speed or stop.
Question 16: What is the correct procedure for discharging a capacitor before handling it?
- Short the terminals with a screwdriver blade rapidly
- Use a 10,000-ohm, 10-watt resistor across the terminals (Correct answer)
- Allow the unit to sit unpowered for 10 seconds
- Use needle-nose pliers to short the terminals
Correct answer: Use a 10,000-ohm, 10-watt resistor across the terminals
A resistor safely dissipates the stored charge without the arc that a direct short causes, which can damage terminals and capacitor internals.
Question 17: Which component in a gas furnace/AC system directly controls when the indoor blower comes on after heating ignition?
- Thermostat R terminal
- Fan limit switch or control board fan delay (Correct answer)
- Contactor coil
- Pressure switch
Correct answer: Fan limit switch or control board fan delay
A fan limit switch or control board fan-delay timer delays blower startup until the heat exchanger warms up, preventing cold air distribution.
Question 18: If a compressor's internal overload protects it from overheating but the unit starts immediately after being reset manually, what concern exists?
- The overload is too sensitive
- The underlying cause of overheating was not corrected and the compressor will trip again (Correct answer)
- The refrigerant charge is too high
- The run capacitor is oversized
Correct answer: The underlying cause of overheating was not corrected and the compressor will trip again
Resetting an overload without diagnosing and correcting the root cause (e.g., low refrigerant, dirty coils, high ambient) will result in repeated tripping.
Question 19: What is the purpose of the C (common) terminal on a 24V thermostat circuit?
- It carries the high-voltage power to the compressor
- It provides the return path for 24V AC from the transformer secondary (Correct answer)
- It signals the reversing valve
- It connects to the outdoor unit high-pressure switch
Correct answer: It provides the return path for 24V AC from the transformer secondary
The C wire completes the 24V control circuit by returning current to the transformer's secondary common, allowing smart thermostats and other loads to operate continuously.
Question 20: A technician reads 5 ohms between the compressor's common and run terminals and OL between common and start. What does this indicate?
- The start winding is open (Correct answer)
- The run winding is shorted to ground
- The compressor has normal windings
- The capacitor is faulty
Correct answer: The start winding is open
OL (overload/no continuity) between common and start indicates an open start winding, meaning the compressor motor needs replacement.
Question 21: Which wiring configuration connects the thermostat's Y terminal output back through the equipment to energize the contactor coil?
- Y → condenser fan motor → C
- Y → contactor coil → C (Correct answer)
- Y → compressor run terminal → GND
- Y → high-pressure switch → transformer primary
Correct answer: Y → contactor coil → C
The Y terminal signal travels through any safety switches in series, then through the contactor coil, and returns to the transformer via the C wire.
A contactor's coil is rated at 24V but the unit reads only 18V at the coil terminals during a call for cooling.
What is the most likely cause?
What Practice Test Geeks adds beyond an AI chat for Air Conditioning Repair
An AI chatbot can quiz you, but it can't reproduce the exam conditions or keep your record. Here you get:
- A timed, full-length Air Conditioning Repair mock exam — 100 questions in 120 minutes with a 70% pass mark, modeled on the official exam's question count and time limit, followed by a score report broken down by exam domain.
- A fixed Air Conditioning Repair question bank: the same test every attempt, so your score is comparable from one try to the next instead of changing with every regenerated quiz.
- Progress saved on your device: completed tests, scores and missed questions stay in My Progress, so you can retake only what you got wrong.
- A printable Air Conditioning Repair cheat sheet you can print or save as a PDF.
- Air Conditioning Repair flashcards built from the same question bank.
Practice questions written with AI assistance and published by Nathan Beja, founder of Practice Test Geeks. They are not real exam questions. We have not yet matched this exam's facts to an official source, so confirm fees, dates and rules with the exam body. Editorial policy