TN LLE Electrical Safety Practices — Questions and Answers
Question 1: Per OSHA 1910.333, what is the minimum approach distance for an unqualified person near exposed energized parts at 300 volts to ground?
- 3 feet
- 10 feet (Correct answer)
- 42 inches
- No specific distance, just 'stay away'
Correct answer: 10 feet
OSHA 1910.333(c)(3) Table S-5 specifies that unqualified persons must maintain at least 10 feet from exposed energized parts operating at 300V to 750V.
OSHA 1910.333(c)(3) Table S-5 provides approach distances for unqualified persons. For voltages from 301V to 750V, the minimum distance is 10 feet. For voltages up to 50V, no specific distance is required. Between 51V and 300V, the distance is 3.5 feet. These distances are significantly greater than qualified worker distances because unqualified persons lack the training and PPE to safely work near energized conductors.
Question 2: What is the primary purpose of an energized electrical work permit per NFPA 70E?
- To document insurance coverage
- To formally evaluate the hazard and justify why de-energizing is infeasible (Correct answer)
- To assign blame if an accident occurs
- To schedule the work with the utility company
Correct answer: To formally evaluate the hazard and justify why de-energizing is infeasible
An energized electrical work permit per NFPA 70E 130.2 documents the justification for not de-energizing and ensures proper safety measures are in place.
NFPA 70E Section 130.2 requires an energized electrical work permit when work will be performed on energized conductors or circuit parts that have not been placed in an electrically safe work condition. The permit must document: the description of work, justification for not de-energizing, shock and arc flash hazard analysis results, safe work practices to be employed, PPE requirements, and management approval. This formal process ensures that energized work is only performed when de-energizing creates a greater hazard or is infeasible.
Question 3: What does the term 'lockout/tagout' (LOTO) refer to in electrical safety?
- Locking the main entrance during electrical work
- Applying a physical lock and warning tag to energy-isolating devices to prevent re-energization (Correct answer)
- Tagging electrical panels for identification
- Locking tools in a secure location during breaks
Correct answer: Applying a physical lock and warning tag to energy-isolating devices to prevent re-energization
LOTO involves physically locking energy-isolating devices in the off position and attaching a warning tag to prevent accidental re-energization during maintenance.
Lockout/tagout (LOTO) per OSHA 1910.147 and NFPA 70E involves applying a lock and tag to each energy-isolating device (disconnect switch, circuit breaker, valve) to physically prevent re-energization while workers perform maintenance. Each worker applies their own lock, and the equipment cannot be re-energized until all locks are removed. Tags provide identification of who applied the lock and when. LOTO is the foundation of establishing an electrically safe work condition.
Question 4: Per NFPA 70E, what must be done to verify an electrically safe work condition after de-energizing equipment?
- Visual inspection only
- Test with a voltmeter to verify absence of voltage (Correct answer)
- Ask a coworker to confirm the circuit is off
- Check the breaker position only
Correct answer: Test with a voltmeter to verify absence of voltage
NFPA 70E requires testing each conductor with an adequately rated voltage detector to verify absence of voltage before establishing an electrically safe work condition.
NFPA 70E 120.5 requires that after de-energizing and applying LOTO, each conductor or circuit part must be tested with an adequately rated voltage detector to verify it is de-energized. Before and after testing, the voltage detector must be verified on a known voltage source to confirm it is functioning properly. This 'test-before-touch' protocol with a live-dead-live verification sequence ensures the voltage tester itself is working correctly and the circuit is truly de-energized.
Question 5: What class of fire extinguisher is required for electrical fires?
- Class A
- Class B
- Class C (Correct answer)
- Class D
Correct answer: Class C
Class C fire extinguishers are rated for fires involving energized electrical equipment. The extinguishing agent is non-conductive.
Class C fire extinguishers contain non-conductive extinguishing agents suitable for fires involving energized electrical equipment. Common Class C agents include CO2 and dry chemical. Many extinguishers carry multiple ratings such as ABC, meaning they can handle ordinary combustibles, flammable liquids, and electrical fires. Once the electrical equipment is de-energized, the fire becomes a Class A or B fire depending on the burning material. Tennessee LLEs should ensure appropriate fire extinguishers are available when performing electrical work.
Question 6: What is the minimum arc flash PPE category for work on a 480V motor control center with the doors open per NFPA 70E Table 130.7(C)(15)(a)?
- Category 1
- Category 2 (Correct answer)
- Category 3
- Category 4
Correct answer: Category 2
NFPA 70E Table 130.7(C)(15)(a) typically assigns PPE Category 2 for working on 480V MCCs with doors open under normal conditions.
NFPA 70E Table 130.7(C)(15)(a) provides arc flash PPE categories based on equipment type and task. For 480V motor control centers, working with doors open typically requires PPE Category 2, which includes arc-rated clothing with a minimum rating of 8 cal/cm2, arc-rated face shield or flash suit hood, safety glasses, hearing protection, and leather gloves. The specific category can vary based on the available fault current and clearing time — an incident energy analysis may indicate higher or lower requirements.
Question 7: Per OSHA regulations, at what voltage level do electrical safety standards begin to apply for work on exposed energized conductors?
- 24 volts
- 50 volts (Correct answer)
- 120 volts
- 240 volts
Correct answer: 50 volts
OSHA considers voltages above 50 volts as potentially hazardous, and electrical safety work practices apply at this threshold.
OSHA 1910.333 and NFPA 70E establish 50 volts as the threshold at which electrical safety practices become mandatory. Below 50 volts, the shock hazard is generally considered minimal for most situations, though exceptions exist (wet conditions, conductive environments). Above 50 volts, workers must follow safe work practices including approach boundaries, PPE requirements, and lockout/tagout procedures. This 50-volt threshold is widely recognized in electrical safety standards worldwide.
Question 8: What is the purpose of ground fault circuit interrupter (GFCI) protection on construction sites per NEC 590.6?
- To prevent overloads on temporary circuits
- To detect imbalances in current flow and disconnect before lethal shock occurs (Correct answer)
- To protect equipment from power surges
- To prevent unauthorized use of temporary power
Correct answer: To detect imbalances in current flow and disconnect before lethal shock occurs
GFCI protection detects current imbalances as small as 4-6 milliamps and rapidly disconnects the circuit to prevent electrocution.
NEC 590.6 requires GFCI protection for all 125V, single-phase, 15- and 20-ampere receptacles used for temporary wiring on construction sites. GFCIs detect a difference of approximately 4-6 milliamps between the hot and neutral conductors, indicating current is flowing through an unintended path — potentially through a person. The device trips in approximately 1/40th of a second, fast enough to prevent ventricular fibrillation. On construction sites, the wet and dusty conditions increase the risk of ground faults.
Question 9: When working on electrical panels, what is the 'one-hand rule' and why is it practiced?
- Only use your dominant hand for better control
- Keep one hand behind your back or in your pocket to prevent current from flowing through your chest (Correct answer)
- Hold a flashlight in one hand and work with the other
- One hand operates the disconnect while the other works
Correct answer: Keep one hand behind your back or in your pocket to prevent current from flowing through your chest
The one-hand rule minimizes the chance of creating a hand-to-hand current path through the heart during accidental contact with energized conductors.
The one-hand rule is a safety practice where an electrician keeps one hand behind their back or in a pocket when working near or testing energized equipment. If accidental contact occurs with one hand, the current path would flow from that hand through the body to the feet (with shoes providing some insulation) rather than hand-to-hand across the chest. A hand-to-hand path passes directly through the heart, making ventricular fibrillation much more likely. This simple practice can be the difference between a painful shock and a fatal one.
Question 10: Per Tennessee state requirements, what training documentation must a Limited Licensed Electrician maintain regarding electrical safety?
- No specific documentation required
- Only CPR certification
- Records of safety training relevant to the work performed (Correct answer)
- A college degree in electrical safety
Correct answer: Records of safety training relevant to the work performed
Tennessee licensing requirements include maintaining records of relevant safety training, which may be audited during license renewal or inspections.
Tennessee's Board of Licensing Contractors requires licensed electricians, including LLEs, to maintain documentation of relevant safety training. This includes OSHA training records, NFPA 70E awareness, CPR/first aid certification, and any continuing education related to electrical safety. These records may be requested during license renewal or job-site inspections by state or local authorities. Additionally, employers are required by OSHA to document all safety training provided to employees.
Question 11: What is the correct procedure if an electrical tool or cord is found to be damaged on a job site?
- Wrap it with electrical tape and continue working
- Remove it from service immediately and tag it as defective (Correct answer)
- Use it only for light-duty tasks
- Report it at the end of the work day
Correct answer: Remove it from service immediately and tag it as defective
Damaged tools and cords must be immediately removed from service and tagged or labeled as defective to prevent others from using them.
Per OSHA 1926.405(a)(2) and general duty requirements, damaged electrical tools, cords, and equipment must be immediately removed from service. The item should be tagged or labeled as 'DEFECTIVE - DO NOT USE' and stored separately from serviceable equipment. Continuing to use damaged electrical equipment creates shock and fire hazards. Repairs must be made by qualified personnel, and the item must be tested before being returned to service. Daily inspection of cords and tools before use is a required safe work practice.
Question 12: Per NFPA 70E, what is the shock protection boundary called that requires PPE to cross?
- Flash protection boundary
- Limited approach boundary
- Restricted approach boundary (Correct answer)
- Prohibited approach boundary
Correct answer: Restricted approach boundary
The restricted approach boundary is where shock PPE (insulated gloves and tools) is required. Only qualified persons with appropriate PPE may cross this boundary.
NFPA 70E defines four shock protection boundaries around exposed energized conductors: (1) Arc flash boundary — where incident energy equals 1.2 cal/cm2, (2) Limited approach boundary — only qualified persons may cross, (3) Restricted approach boundary — requires PPE (insulated gloves, tools) to cross, and (4) Prohibited approach boundary — treated the same as making contact with the energized part. The restricted approach boundary is the critical line where direct shock protection PPE becomes mandatory. Each boundary distance varies based on the system voltage.
Per OSHA 1910.333, what is the minimum approach distance for an unqualified person near exposed energized parts at 300 volts to ground?
What Practice Test Geeks adds beyond an AI chat for TN LLE
An AI chatbot can quiz you, but it can't reproduce the exam conditions or keep your record. Here you get:
- A timed, full-length TN LLE mock exam — 40 questions in 120 minutes with a 73% pass mark, modeled on the official exam's question count and time limit, followed by a score report broken down by exam domain.
- A fixed TN LLE question bank: the same test every attempt, so your score is comparable from one try to the next instead of changing with every regenerated quiz.
- Progress saved on your device: completed tests, scores and missed questions stay in My Progress, so you can retake only what you got wrong.
- A printable TN LLE cheat sheet you can print or save as a PDF.
- TN LLE flashcards built from the same question bank.
These practice questions were written with AI tools. They are not real exam questions. Exam facts are checked against the official sources listed below. Not reviewed by a subject-matter expert. Editorial policy
Sources & references
Exam facts on this page (fees, format, dates, passing scores) are checked against these official sources; the date is our last check. Editorial policy
- tn.gov — Score validity, exam information · verified Oct 2026
- test-takers.psiexams.com — Exam information · verified Nov 2026
- tnboi.provexam.com — Test delivery, fees, exam format, passing score, retake fee, retake policy, score release, time limit, exam information · verified Oct 2026