Question 1: What is the primary function of an air handler unit (AHU) in an HVAC system?
- Generate refrigeration by compressing refrigerant
- Condition and circulate air throughout the building (Correct answer)
- Control refrigerant flow to the outdoor unit
- Measure and control building humidity only
Correct answer: Condition and circulate air throughout the building
An air handler unit (AHU) conditions and circulates air. It typically contains a blower, heating/cooling coils, filters, dampers, and controls to deliver conditioned air to occupied spaces.
Question 2: What causes 'coil freeze-up' on an evaporator coil?
- Overcharge of refrigerant causing high suction pressure
- Insufficient airflow or low refrigerant charge causing suction pressure to drop below freezing (Correct answer)
- High outdoor ambient temperature reducing system capacity
- Dirty condenser coil reducing heat rejection
Correct answer: Insufficient airflow or low refrigerant charge causing suction pressure to drop below freezing
Coil freeze-up occurs when suction pressure drops low enough that coil surface temperature falls below 32°F. Causes include low airflow (dirty filter, failed blower) or low refrigerant charge, both of which reduce suction pressure.
Question 3: What is the recommended face velocity for evaporator coils in air handling units?
- 100-200 FPM
- 300-500 FPM (Correct answer)
- 600-800 FPM
- 900-1200 FPM
Correct answer: 300-500 FPM
The recommended face velocity for evaporator coils is typically 300-500 FPM (feet per minute). Higher velocities can cause moisture carryover; lower velocities reduce efficiency and increase coil size requirements.
Question 4: What type of coil is used in an air handler for the heating mode in a heat pump system?
- A separate electric resistance coil only
- The same evaporator coil, which acts as a condenser during heating mode (Correct answer)
- A hot water coil fed from a boiler
- A gas-fired heat exchanger coil
Correct answer: The same evaporator coil, which acts as a condenser during heating mode
In a heat pump system, the indoor coil serves dual purposes — it acts as the evaporator in cooling mode and as the condenser in heating mode. The refrigerant flow is reversed by the reversing valve.
Question 5: What does the 'fin spacing' on a coil affect?
- Refrigerant flow rate through the coil
- Heat transfer surface area and airflow resistance (Correct answer)
- Compressor capacity and efficiency
- Refrigerant superheat at the coil outlet
Correct answer: Heat transfer surface area and airflow resistance
Fin spacing (fins per inch) affects the coil's heat transfer surface area and air-side pressure drop. Tighter fin spacing increases surface area for better heat transfer but also increases airflow resistance.
Question 6: What is the purpose of the condensate drain pan in an air handler?
- To collect oil from the compressor
- To collect water condensed from humid air on the evaporator coil (Correct answer)
- To store refrigerant during defrost cycles
- To hold excess refrigerant charge
Correct answer: To collect water condensed from humid air on the evaporator coil
As warm, humid air passes over the cold evaporator coil, moisture condenses on the coil surface and drips into the drain pan, which routes it to a drain. Clogged drain pans cause water damage and microbial growth.
Question 7: What is 'sensible heat ratio' (SHR) and why is it important for coil selection?
- The ratio of total cooling to latent cooling capacity
- The ratio of sensible cooling capacity to total cooling capacity of a coil (Correct answer)
- The ratio of heating to cooling capacity in a heat pump
- The ratio of airflow to refrigerant flow
Correct answer: The ratio of sensible cooling capacity to total cooling capacity of a coil
SHR is the ratio of sensible cooling (temperature reduction) to total cooling (sensible + latent). A lower SHR means the coil removes more moisture. Matching SHR to the application's latent load requirements is critical for comfort and indoor air quality.
Question 8: What material are most residential evaporator coil fins made from?
- Stainless steel
- Copper
- Aluminum (Correct answer)
- Galvanized steel
Correct answer: Aluminum
Most residential evaporator coil fins are made of aluminum because it is lightweight, inexpensive, and has good thermal conductivity. The tubing is typically copper, which provides excellent heat transfer and is easy to braze.
Question 9: What is 'coil bypass factor' in HVAC?
- The percentage of airflow that bypasses the coil without making contact with the coil surface (Correct answer)
- The ratio of entering to leaving air temperature
- The percentage of refrigerant that bypasses the expansion valve
- The coil's resistance to airflow in static pressure
Correct answer: The percentage of airflow that bypasses the coil without making contact with the coil surface
Coil bypass factor (CBF) is the fraction of air that passes through the coil without being fully conditioned — it 'bypasses' the coil surface. A lower bypass factor means more air contacts the coil, improving dehumidification and cooling.
Question 10: What is the most common cause of a clogged condensate drain line?
- Refrigerant leaks into the drain pan
- Algae and biological growth in the drain line (Correct answer)
- Mineral deposits from the condensate water
- Debris from the air filter entering the drain
Correct answer: Algae and biological growth in the drain line
Algae and biological growth (slime, mold, mildew) are the most common cause of clogged condensate drain lines. The warm, dark, moist conditions in the drain pan and line are ideal for microbial growth.
Question 11: What is the correct refrigerant superheat at the evaporator outlet for a TXV-equipped system?
- 0-2°F (at the outlet of the coil)
- 8-12°F (at the outlet of the coil) (Correct answer)
- 20-30°F (at the outlet of the coil)
- 40-50°F (at the outlet of the coil)
Correct answer: 8-12°F (at the outlet of the coil)
For TXV-controlled systems, the target superheat at the evaporator outlet is typically 8-12°F. The TXV modulates refrigerant flow to maintain this superheat, ensuring the coil is fully utilized without liquid refrigerant reaching the compressor.
Question 12: What is 'dirty sock syndrome' in HVAC systems?
- Foul odors caused by biological growth on the evaporator coil when the system cycles (Correct answer)
- Refrigerant contamination causing odors in the airstream
- Duct leakage bringing in outdoor odors
- Condensate water dripping onto the blower motor
Correct answer: Foul odors caused by biological growth on the evaporator coil when the system cycles
Dirty sock syndrome is caused by biological growth (bacteria, mold) on the evaporator coil, typically on coating or brazing materials. The odor is most noticeable at startup when the coil is heating up during the off cycle.
Question 13: What is the purpose of a drain pan float switch on an air handler?
- To measure condensate volume for maintenance scheduling
- To shut down the system if the drain pan fills with water to prevent overflow damage (Correct answer)
- To activate an auxiliary pump when the drain fills
- To monitor refrigerant leaks in the drain pan area
Correct answer: To shut down the system if the drain pan fills with water to prevent overflow damage
A drain pan float switch is a safety device that shuts down the system when the condensate drain pan fills with water, typically due to a clogged drain line. This prevents water overflow and potential water damage.
Question 14: What does 'coil circuiting' refer to in evaporator coil design?
- The electrical wiring pattern of the coil heating elements
- How refrigerant tubes are arranged and connected to distribute refrigerant flow through the coil (Correct answer)
- The pattern in which fins are attached to the tubing
- The airflow pattern directed by the coil baffles
Correct answer: How refrigerant tubes are arranged and connected to distribute refrigerant flow through the coil
Coil circuiting refers to how refrigerant flows through the multiple tube circuits of the coil. Proper circuiting ensures even refrigerant distribution, optimizes superheat across the coil face, and maximizes heat transfer efficiency.
Question 15: What is an 'A-coil' configuration in residential HVAC?
- A coil arranged in a single flat panel
- An evaporator coil arranged in an inverted V or A shape with two slanted coil sections (Correct answer)
- A coil with alternating hot and cold sections
- A coil used exclusively with air-source heat pumps
Correct answer: An evaporator coil arranged in an inverted V or A shape with two slanted coil sections
An A-coil (or 'A-frame coil') has two coil sections arranged in an inverted V (A shape). This configuration increases the coil face area within a smaller footprint, fitting inside a furnace plenum and providing good airflow distribution.
Question 16: What is the purpose of indoor coil subcooling measurement?
- To verify the evaporator coil is operating correctly
- To determine if the refrigerant charge is correct when using the TXV charging method (Correct answer)
- To check the air-side heat transfer efficiency
- To measure moisture removal from the airstream
Correct answer: To determine if the refrigerant charge is correct when using the TXV charging method
Subcooling (measured at the liquid line or condenser outlet) indicates how much the liquid refrigerant has been cooled below its saturation temperature. The subcooling method is used with TXV systems to verify correct refrigerant charge.
Question 17: What causes 'refrigerant flood-back' to the compressor from the evaporator coil?
- Excessive superheat at the evaporator outlet
- Liquid refrigerant returning to the compressor due to low superheat or overcharge (Correct answer)
- High suction pressure causing vapor to condense in the suction line
- Incorrect refrigerant type causing poor evaporation
Correct answer: Liquid refrigerant returning to the compressor due to low superheat or overcharge
Flood-back occurs when liquid refrigerant (not fully vaporized) returns to the compressor. Causes include a defective TXV (stuck open), overcharge, or very low load conditions. Liquid refrigerant damages the compressor through hydraulic slugging.
Question 18: What is the function of a 'hard-start kit' (potential relay and start capacitor) on an air handler?
- It helps the blower motor start under high static pressure conditions
- It reduces starting current for the compressor in systems with long refrigerant lines
- It is not used on air handlers — only on compressors (Correct answer)
- It provides backup power during voltage sags
Correct answer: It is not used on air handlers — only on compressors
Hard-start kits (potential relay + start capacitor) are installed on compressors, not air handlers. They boost starting torque to help compressors start under high pressure differential or during low voltage conditions.
Question 19: How should coil cleaning solution be applied on an evaporator coil?
- Sprayed from the air inlet side in the direction of airflow
- Applied from the air outlet side, against the direction of airflow, to push debris out the inlet (Correct answer)
- Only dry brushing is permitted — no liquids on coils
- Sprayed from both sides simultaneously
Correct answer: Applied from the air outlet side, against the direction of airflow, to push debris out the inlet
Coil cleaner should be applied from the clean air (leaving air) side and rinsed from the dirty air (entering air) side — working against airflow direction. This pushes contaminants out the same way air brought them in.
Question 20: What is 'enthalpy' in HVAC, and how is it relevant to coil performance?
- Total heat content of air (sensible + latent), used to calculate total coil capacity (Correct answer)
- The temperature difference across the coil only
- The refrigerant pressure at the coil inlet
- The efficiency rating of the coil in BTU/hr
Correct answer: Total heat content of air (sensible + latent), used to calculate total coil capacity
Enthalpy is the total heat content of air, combining both sensible heat (temperature) and latent heat (moisture content). Total coil cooling capacity is calculated from the enthalpy difference between entering and leaving air, multiplied by airflow.
Question 21: What is the recommended minimum static pressure test point for verifying airflow in an air handling unit?
- Across the filter only
- At the supply plenum only
- Both entering and leaving the coil/filter section to calculate total external static pressure (Correct answer)
- Only at the return air inlet
Correct answer: Both entering and leaving the coil/filter section to calculate total external static pressure
To verify airflow, technicians measure total external static pressure (TESP) by measuring pressure before the return and after the supply sections and adding the absolute values. This total is compared to the blower performance curve.
Question 22: What causes higher-than-normal wet-bulb temperature at the air handler inlet?
- Low refrigerant charge
- High outdoor humidity and high indoor latent load (Correct answer)
- Dirty evaporator coil
- Undersized ductwork
Correct answer: High outdoor humidity and high indoor latent load
High wet-bulb temperature at the coil inlet indicates high total heat (enthalpy) in the incoming air, usually from high humidity and high temperatures. This increases the total load on the coil and can reduce the system's sensible heat ratio.
Question 23: What is 'distributed fan coil' configuration in commercial HVAC?
- Multiple small fan coil units distributed throughout a building, each with local control (Correct answer)
- A central air handler with ductwork distributed to all zones
- A single large fan coil unit with multiple coil sections
- Fan coils connected to a distributed chilled water loop
Correct answer: Multiple small fan coil units distributed throughout a building, each with local control
Distributed fan coil systems use multiple small fan coil units (FCUs) placed throughout a building. Each FCU has its own fan, coil, and filter, connected to a central chilled water/hot water plant, providing local temperature control.
Question 24: What is the purpose of coil coating (like phenolic epoxy coating) on evaporator coils?
- To improve heat transfer efficiency
- To protect aluminum fins from corrosion in coastal and aggressive environments (Correct answer)
- To reduce airflow noise
- To increase the coil's thermal mass
Correct answer: To protect aluminum fins from corrosion in coastal and aggressive environments
Coil coatings like phenolic epoxy, polyurethane, or ElectroFin protect aluminum fins from corrosion caused by salt air, industrial pollutants, and chemicals. This is especially important in coastal installations and industrial environments.
Question 25: What does a 'chilled water coil' use instead of direct refrigerant expansion?
- Freon vapor at low pressure
- Cold water (typically 44-46°F) circulated from a central chiller (Correct answer)
- Refrigerant in a sealed direct-expansion circuit
- CO2 refrigerant in a cascade system
Correct answer: Cold water (typically 44-46°F) circulated from a central chiller
Chilled water coils use cold water (typically 44-46°F supply, 54-56°F return) circulated from a central chiller plant. Water picks up heat from the airstream and returns to the chiller for re-cooling. This is common in large commercial/institutional buildings.
Question 26: How is airflow (CFM) typically measured across an air handler coil?
- Using a refrigerant pressure gauge at the coil inlet
- Using the temperature rise method (for electric heat) or the static pressure/blower curve method (Correct answer)
- By counting the number of supply registers
- Using an anemometer at the coil face only
Correct answer: Using the temperature rise method (for electric heat) or the static pressure/blower curve method
Airflow is most accurately measured using the temperature rise method with electric or gas heat (CFM = BTU/hr ÷ (1.08 × ΔT)) or by measuring total external static pressure and referencing the blower performance curve.
Question 27: What is the typical leaving air temperature from an evaporator coil in a standard comfort cooling application?
- 35-40°F
- 45-55°F (Correct answer)
- 55-65°F
- 65-75°F
Correct answer: 45-55°F
The typical leaving air temperature from an evaporator coil in comfort cooling is 45-55°F. The supply air temperature delivered to the space (after duct heat gain) is typically 55-65°F.
Question 28: What is a 'hot gas bypass' valve and when is it used on a coil?
- A valve that bypasses the heat exchanger during defrost
- A valve that feeds hot discharge gas to the evaporator to prevent coil freeze-up at low loads (Correct answer)
- A valve that diverts hot refrigerant away from the condenser coil
- A pressure relief valve on the high side
Correct answer: A valve that feeds hot discharge gas to the evaporator to prevent coil freeze-up at low loads
A hot gas bypass valve feeds hot discharge gas directly to the evaporator inlet during low-load conditions. This artificial load prevents suction pressure from dropping too low (and coil temperature from falling below freezing) when the system is oversized for the current load.
Question 29: What is the primary cause of microbial contamination in drain pans and coils?
- High refrigerant charge
- Standing water, organic debris, and warm temperatures providing ideal growth conditions (Correct answer)
- Metallic corrosion products from the coil fins
- Chemical reactions between refrigerant and coil materials
Correct answer: Standing water, organic debris, and warm temperatures providing ideal growth conditions
Drain pans and coils provide ideal conditions for microbial growth: standing water (moisture), organic debris carried by the airstream (nutrients), and moderate temperatures. Regular cleaning and biocide treatment are essential for indoor air quality.
Question 30: What is 'face split' coil configuration in air handling units?
- A coil divided horizontally into separate circuits for pre-cooling and main cooling
- A coil divided vertically with each half connected to a separate refrigerant circuit for capacity staging (Correct answer)
- A coil with alternating hot water and chilled water circuits
- A coil where alternate fins are removed to reduce pressure drop
Correct answer: A coil divided vertically with each half connected to a separate refrigerant circuit for capacity staging
A face-split coil divides the coil vertically, with each half connected to a separate circuit. This allows staging of capacity — one circuit can be active while the other is off, providing better part-load performance and humidity control.
Question 31: How does a dirty air filter affect evaporator coil performance?
- Increases airflow velocity across the coil, improving heat transfer
- Reduces airflow, lowering suction pressure and potentially causing coil freeze-up (Correct answer)
- Has no effect on coil performance — only on air quality
- Increases the sensible heat ratio of the coil
Correct answer: Reduces airflow, lowering suction pressure and potentially causing coil freeze-up
A dirty filter restricts airflow, reducing the amount of air passing over the evaporator coil. Less airflow means the coil absorbs less heat, suction pressure drops, and coil temperature can fall below 32°F causing freeze-up.
Question 32: What is the purpose of a UV germicidal lamp installed in an air handler?
- To pre-heat the evaporator coil before startup
- To kill biological growth (mold, bacteria) on the coil surface and in the drain pan area (Correct answer)
- To ionize the airstream for static reduction
- To detect refrigerant leaks using UV-reactive dye
Correct answer: To kill biological growth (mold, bacteria) on the coil surface and in the drain pan area
UV germicidal lamps (UVC type, 254nm wavelength) installed in air handlers irradiate the coil and drain pan surfaces to inhibit biological growth. They are effective at preventing dirty sock syndrome and improving indoor air quality.
Question 33: What is the effect of 'air stratification' on coil performance in a large duct?
- It improves coil efficiency by creating turbulent flow
- Uneven air temperature and humidity distribution across the coil face reduces efficiency and may cause condensation problems (Correct answer)
- It has no effect if the coil is properly sized
- It only affects filter performance, not coil performance
Correct answer: Uneven air temperature and humidity distribution across the coil face reduces efficiency and may cause condensation problems
Air stratification (temperature/humidity layers in the airstream) causes uneven conditions across the coil face. Some portions may be oversaturated (causing moisture carryover) while others are underloaded, reducing overall efficiency and creating IAQ issues.
Question 34: What MERV rating is recommended for air handler filters in standard commercial comfort cooling to balance filtration with acceptable pressure drop?
- MERV 1-4
- MERV 8-13 (Correct answer)
- MERV 14-16
- MERV 17-20 (HEPA)
Correct answer: MERV 8-13
MERV 8-13 filters provide good particle removal efficiency (capturing fine dust, pollen, mold spores, some bacteria) while maintaining acceptable static pressure drop for most commercial air handlers. HEPA (MERV 17+) requires specialized equipment due to very high pressure drop.
Question 35: What is 'coil circuiting imbalance' and what symptoms does it cause?
- Electrical imbalance in coil heating elements causing hot spots
- Uneven refrigerant distribution through coil circuits causing uneven superheat and reduced capacity (Correct answer)
- Uneven airflow distribution across the coil face
- Pressure imbalance between supply and return connections
Correct answer: Uneven refrigerant distribution through coil circuits causing uneven superheat and reduced capacity
Coil circuiting imbalance occurs when refrigerant is not evenly distributed among the coil's parallel circuits. Some circuits may be starved (high superheat) while others are flooded (low superheat), reducing overall capacity and efficiency.
Question 36: What is the purpose of a 'mixing box' or 'blend box' in a commercial air handling unit?
- To mix refrigerant types for blended system operation
- To blend return air with outdoor air in controlled proportions for ventilation and economizer operation (Correct answer)
- To mix hot and cold airstreams for precise temperature control
- To equalize static pressure between supply and return ducts
Correct answer: To blend return air with outdoor air in controlled proportions for ventilation and economizer operation
A mixing box blends return air and outdoor air in controlled proportions. Dampers modulate the mix ratio to meet ventilation requirements (minimum OA), support economizer free cooling (maximum OA), and provide precise entering air conditions to the coil.
What is the primary function of an air handler unit (AHU) in an HVAC system?
What Practice Test Geeks adds beyond an AI chat for HVAC
An AI chatbot can quiz you, but it can't reproduce the exam conditions or keep your record. Here you get:
- A timed, full-length HVAC mock exam — 100 questions in 120 minutes with a 70% pass mark, modeled on the official exam's question count and time limit, followed by a score report broken down by exam domain.
- A fixed HVAC question bank: the same test every attempt, so your score is comparable from one try to the next instead of changing with every regenerated quiz.
- Progress saved on your device: completed tests, scores and missed questions stay in My Progress, so you can retake only what you got wrong.
- A printable HVAC cheat sheet you can print or save as a PDF.
- HVAC flashcards built from the same question bank.
These practice questions were written with AI tools. They are not real exam questions. Exam facts are checked against the official sources listed below. Not reviewed by a subject-matter expert. Editorial policy
Sources & references
Exam facts on this page (fees, format, dates, passing scores) are checked against these official sources; the date is our last check. Editorial policy