CFM Hazardous Materials & Building Safety — Questions and Answers
Question 1: Under NFPA 30, a liquid with a flash point of 85°F is classified as which class?
- Class IB
- Class IC (Correct answer)
- Class II
- Class IIIA
Correct answer: Class IC
Class IC liquids have flash points at or above 73°F and below 100°F.
Question 2: On an NFPA 704 diamond, what does the yellow quadrant indicate?
- Health hazard
- Flammability
- Instability (reactivity) (Correct answer)
- Special hazards
Correct answer: Instability (reactivity)
The yellow quadrant rates instability, from 0 (stable) to 4 (may detonate at normal conditions).
Question 3: Which IBC occupancy group applies to a building storing materials that pose a detonation hazard, such as Division 1.1 explosives above the maximum allowable quantity?
- H-1 (Correct answer)
- H-2
- H-3
- H-4
Correct answer: H-1
Group H-1 covers materials that present a detonation hazard.
Question 4: In the Emergency Response Guidebook (ERG), which colored section lists initial isolation and protective action distances?
- Yellow pages
- Blue pages
- Orange pages
- Green pages (Correct answer)
Correct answer: Green pages
Green pages give isolation and protective action distances for TIH and water-reactive materials.
Question 5: What is the maximum capacity of an approved safety can for flammable liquids under NFPA 30?
- 1 gallon
- 2.5 gallons
- 5 gallons (Correct answer)
- 10 gallons
Correct answer: 5 gallons
Safety cans are limited to 5 gallons (19 L) and have a spring-closing lid and flame arrester.
Question 6: Per the IBC, an interior exit stairway connecting four or more stories must be enclosed with construction having what minimum fire-resistance rating?
- 1 hour
- 1.5 hours
- 2 hours (Correct answer)
- 3 hours
Correct answer: 2 hours
Exit enclosures connecting four or more stories need 2-hour fire-resistance-rated construction.
Question 7: Which SDS section gives exposure limits and required personal protective equipment?
- Section 2
- Section 5
- Section 7
- Section 8 (Correct answer)
Correct answer: Section 8
Section 8 (Exposure Controls/Personal Protection) lists PELs, TLVs, engineering controls, and PPE.
Question 8: Under the IFC, how many control areas are permitted on the first story above grade plane, and at what percentage of the maximum allowable quantity?
- 2 control areas at 50%
- 3 control areas at 75%
- 4 control areas at 100% (Correct answer)
- 1 control area at 100%
Correct answer: 4 control areas at 100%
IFC Table 5003.8.3.1 allows 4 control areas at 100% MAQ on the first floor.
Question 9: What is the main feature that sets a fire wall apart from a fire barrier under the IBC?
- A fire wall must have a 4-hour rating in all cases
- A fire wall must stay structurally stable under fire conditions so that collapse on either side does not bring it down (Correct answer)
- A fire wall may contain unprotected openings
- A fire wall extends only from floor to ceiling
Correct answer: A fire wall must stay structurally stable under fire conditions so that collapse on either side does not bring it down
Fire walls create separate buildings and must stay standing if construction on either side collapses.
Question 10: Which DOT hazard class covers oxidizers and organic peroxides?
- Class 4
- Class 5 (Correct answer)
- Class 6
- Class 8
Correct answer: Class 5
DOT Class 5 covers oxidizers (5.1) and organic peroxides (5.2).
Question 11: Under the IFC, secondary containment for indoor hazardous liquid storage must hold the volume of the largest vessel plus the sprinkler discharge for how long?
- 10 minutes
- 20 minutes (Correct answer)
- 30 minutes
- 60 minutes
Correct answer: 20 minutes
The IFC requires the largest container's volume plus 20 minutes of fire-extinguishing system discharge over the area.
Question 12: A material that ignites spontaneously in air at or below 130°F (54.4°C) is classified as:
- Unstable reactive
- Water-reactive
- Pyrophoric (Correct answer)
- Oxidizer
Correct answer: Pyrophoric
The IFC and NFPA 400 define pyrophoric materials as those that ignite spontaneously in air at or below 130°F.
Question 13: How must stored oxygen cylinders be separated from flammable gas cylinders when no barrier is present?
- 5 feet
- 10 feet
- 20 feet (Correct answer)
- 50 feet
Correct answer: 20 feet
Oxygen must be 20 feet from fuel gas cylinders, or separated by a noncombustible barrier at least 5 feet high with a 1/2-hour rating.
Question 14: Which EPCRA section requires facilities to submit annual Tier II hazardous chemical inventory reports to the SERC, LEPC, and local fire department?
- Section 304
- Section 311
- Section 312 (Correct answer)
- Section 313
Correct answer: Section 312
EPCRA Section 312 requires annual Tier II inventory reporting.
Question 15: Which IBC occupancy classification applies to semiconductor fabrication facilities that use hazardous production materials (HPM)?
- H-2
- H-3
- H-4
- H-5 (Correct answer)
Correct answer: H-5
Group H-5 covers semiconductor fabrication and comparable R&D facilities that use HPM.
Question 16: Under NFPA 30, what is the maximum amount of Class I and Class II liquids allowed in a single approved flammable liquid storage cabinet?
- 30 gallons
- 60 gallons (Correct answer)
- 120 gallons
- 240 gallons
Correct answer: 60 gallons
A cabinet may hold up to 60 gallons of Class I and II liquids, or 120 gallons of Class I, II, and IIIA combined.
Question 17: A gas with a vapor density of 1.5, such as propane, released inside a building will most likely:
- Rise and gather at the ceiling
- Spread evenly throughout the room
- Collect in low areas such as basements and pits (Correct answer)
- Break down quickly on contact with air
Correct answer: Collect in low areas such as basements and pits
Gases with a vapor density greater than 1 are heavier than air and settle in low spots.
Question 18: Which GHS pictogram identifies an oxidizer?
- Flame
- Flame over circle (Correct answer)
- Exploding bomb
- Exclamation mark
Correct answer: Flame over circle
The flame-over-circle pictogram marks oxidizing gases, liquids, and solids.
Question 19: What does a fire marshal require during transfer of Class I liquids between metal containers to prevent static ignition?
- Ventilation only
- Bonding and grounding (Correct answer)
- An inert gas blanket on all containers
- A water spray curtain
Correct answer: Bonding and grounding
Bonding equalizes potential between the containers and grounding drains static to earth, preventing sparks.
Question 20: Under the IFC, how wide must an unobstructed fire apparatus access road be, at minimum?
- 12 feet
- 16 feet
- 20 feet (Correct answer)
- 26 feet
Correct answer: 20 feet
IFC 503.2.1 requires at least 20 feet of unobstructed width and 13 ft 6 in of vertical clearance.
Question 21: Under NFPA 51B, how far must combustibles be kept from hot work operations unless they are shielded or moved?
- 10 feet
- 20 feet
- 35 feet (Correct answer)
- 50 feet
Correct answer: 35 feet
NFPA 51B uses the 35-foot (11 m) rule for combustibles near hot work.
Question 22: Which IBC construction type has noncombustible exterior walls but allows interior elements of any material permitted by the code?
- Type II
- Type III (Correct answer)
- Type IV
- Type V
Correct answer: Type III
Type III construction requires noncombustible exterior walls; interior elements may be any approved material.
Question 23: On an NFPA 704 placard, what does a 'W' with a line through it in the white quadrant mean?
- Wear respiratory protection
- Use water as the primary extinguishing agent
- The material reacts with water; do not use water (Correct answer)
- The material is a weak acid
Correct answer: The material reacts with water; do not use water
A crossed-out W means the material reacts unusually or dangerously with water.
Question 24: Under the IBC, a high-rise building has an occupied floor more than how many feet above the lowest level of fire department vehicle access?
- 55 feet
- 75 feet (Correct answer)
- 100 feet
- 120 feet
Correct answer: 75 feet
The IBC defines a high-rise as having an occupied floor more than 75 feet above the lowest level of fire department vehicle access.
Question 25: Which standpipe class provides 2.5-inch hose connections intended only for fire department use?
- Class I (Correct answer)
- Class II
- Class III
- Class IV
Correct answer: Class I
Class I standpipes have 2.5-inch connections for fire department and trained personnel use.
Question 26: Under NFPA 101 and the IBC, what is the minimum duration emergency lighting must operate after normal power fails?
- 30 minutes
- 60 minutes
- 90 minutes (Correct answer)
- 120 minutes
Correct answer: 90 minutes
Emergency lighting must provide illumination for at least 90 minutes.
Question 27: What is a BLEVE?
- A slow leak of liquefied gas from a valve packing
- A rupture of a pressure vessel holding liquid above its boiling point, often followed by a fireball (Correct answer)
- A dust explosion inside a silo
- A spontaneous polymerization reaction
Correct answer: A rupture of a pressure vessel holding liquid above its boiling point, often followed by a fireball
A Boiling Liquid Expanding Vapor Explosion happens when a heated vessel fails and the superheated liquid flashes to vapor all at once.
Question 28: Under the IFC, the required fire-resistance rating of fire barriers between control areas on the fourth floor and higher is:
- 1 hour
- 1.5 hours
- 2 hours (Correct answer)
- 3 hours
Correct answer: 2 hours
Control-area fire barriers need a 2-hour rating on the fourth floor and above, and 1 hour on floors three and below.