CFM Fire Prevention & Code Enforcement — Questions and Answers
Question 1: Under NFPA 1730, how often should occupancies classified as high-risk generally be inspected?
- Monthly
- Annually (Correct answer)
- Every two years
- Every three years
Correct answer: Annually
NFPA 1730 recommends annual inspections for high-risk occupancies, biennial for moderate-risk, and triennial for low-risk.
Question 2: Which U.S. Supreme Court case established that a fire inspector generally needs an administrative warrant to inspect a commercial property without the owner's consent?
- Michigan v. Tyler
- Mapp v. Ohio
- See v. City of Seattle (Correct answer)
- Michigan v. Clifford
Correct answer: See v. City of Seattle
See v. City of Seattle (1967) extended the administrative warrant requirement of Camara to commercial premises.
Question 3: Under the IFC, when an automatic sprinkler system is out of service for more than how many hours in a 24-hour period, the fire code official must be notified and the building evacuated or a fire watch provided?
- 4 hours
- 8 hours
- 10 hours (Correct answer)
- 24 hours
Correct answer: 10 hours
IFC 901.7 sets 10 hours in a 24-hour period for sprinkler impairments and 4 hours for fire alarm impairments.
Question 4: An inspector finds combustible storage stacked directly beneath sprinkler deflectors in a warehouse. What minimum clearance is typically required below the deflectors?
- 6 inches
- 12 inches
- 18 inches (Correct answer)
- 36 inches
Correct answer: 18 inches
A minimum 18-inch clearance below sprinkler deflectors is required so the discharge pattern is not obstructed.
Question 5: Which IFC permit type is required to conduct an ongoing activity such as storing hazardous materials or operating a place of assembly?
- Construction permit
- Operational permit (Correct answer)
- Building permit
- Certificate of occupancy
Correct answer: Operational permit
The IFC distinguishes operational permits for ongoing activities from construction permits for installing or modifying systems.
Question 6: A notice of violation issued by a fire marshal should, at a minimum, include which of the following elements?
- The owner's insurance carrier and policy number
- A description of the violation, the code section, a correction deadline, and appeal rights (Correct answer)
- Only the fine amount owed
- A copy of the department's annual budget
Correct answer: A description of the violation, the code section, a correction deadline, and appeal rights
Due process requires the notice to identify the violation, cite the code, give time to correct, and explain the right to appeal.
Question 7: Under the IFC, what is the minimum unobstructed width of a fire apparatus access road?
- 12 feet
- 16 feet
- 20 feet (Correct answer)
- 26 feet
Correct answer: 20 feet
IFC requires fire apparatus access roads to have at least 20 feet of unobstructed width and 13 feet 6 inches of vertical clearance.
Question 8: Per NFPA 96, how often should exhaust systems serving solid-fuel cooking operations be inspected for grease buildup?
- Monthly (Correct answer)
- Quarterly
- Semiannually
- Annually
Correct answer: Monthly
NFPA 96 requires monthly inspection for systems serving solid-fuel cooking operations.
Question 9: Under the NFPA flammable liquid classification, a liquid with a flash point below 73°F and a boiling point below 100°F is classified as which class?
- Class IA (Correct answer)
- Class IB
- Class IC
- Class II
Correct answer: Class IA
Class IA liquids have a flash point below 73°F and a boiling point below 100°F, making them the most hazardous flammable liquids.
Question 10: During a hot work permit inspection under NFPA 51B, combustible materials generally must be relocated at least how far from the work area?
- 10 feet
- 20 feet
- 35 feet (Correct answer)
- 50 feet
Correct answer: 35 feet
NFPA 51B uses a 35-foot radius for relocating or protecting combustibles around hot work.
Question 11: An inspector observes a fire door held open with a wooden wedge in a hospital corridor. What is the correct code interpretation?
- Acceptable if the door is closed at night
- Acceptable if a sign states 'Keep Closed'
- A violation; fire doors may be held open only by approved devices that release on smoke detection or fire alarm activation (Correct answer)
- Acceptable if the door has a fusible link closer
Correct answer: A violation; fire doors may be held open only by approved devices that release on smoke detection or fire alarm activation
NFPA 80 and the IFC prohibit wedging fire doors open; only listed hold-open devices that release automatically are allowed.
Question 12: NFPA 80 requires fire door assemblies to be inspected and tested at what minimum frequency?
- Monthly
- Quarterly
- Annually (Correct answer)
- Every five years
Correct answer: Annually
NFPA 80 requires fire door assemblies to be inspected and tested at least annually, with written records kept.
Question 13: Under ASTM E84, interior finish materials with a flame spread index of 0-25 are classified as which class?
- Class A (Correct answer)
- Class B
- Class C
- Class D
Correct answer: Class A
Class A is 0-25, Class B is 26-75, and Class C is 76-200 flame spread index.
Question 14: Which of the five E's of community risk reduction involves using fines, citations, and code compliance actions?
- Education
- Engineering
- Enforcement (Correct answer)
- Emergency response
Correct answer: Enforcement
Enforcement uses legal and regulatory tools such as codes, citations, and penalties to reduce risk.
Question 15: Under the IFC, panic or fire exit hardware is required on swinging egress doors with locks or latches in Group A and Group E occupancies with an occupant load of at least:
- 10
- 50 (Correct answer)
- 100
- 300
Correct answer: 50
IFC/IBC require panic hardware in Group A and E occupancies when the occupant load is 50 or more.
Question 16: Using IBC/IFC occupant load factors, what is the factor for an unconcentrated assembly area with tables and chairs?
- 5 net sq ft per person
- 7 net sq ft per person
- 15 net sq ft per person (Correct answer)
- 150 gross sq ft per person
Correct answer: 15 net sq ft per person
Unconcentrated assembly (tables and chairs) uses 15 net square feet per occupant.
Question 17: Emergency lighting for means of egress must typically provide illumination for at least how long after loss of normal power?
- 30 minutes
- 60 minutes
- 90 minutes (Correct answer)
- 4 hours
Correct answer: 90 minutes
NFPA 101 and the IFC require emergency lighting to operate for a minimum of 90 minutes.
Question 18: In a fully sprinklered building, the minimum separation between two required exits is generally at least what fraction of the overall diagonal of the area served?
- One-quarter
- One-third (Correct answer)
- One-half
- Two-thirds
Correct answer: One-third
The exit separation rule is one-half the diagonal, reduced to one-third when the building is fully sprinklered.
Question 19: An inspector finds extension cords run through a wall to permanently power a vending machine. What is the correct action?
- Approve it if the cord is heavy duty
- Cite the violation, since extension cords may not substitute for permanent wiring (Correct answer)
- Approve it if it is plugged into a GFCI outlet
- Require only that the cord be taped down
Correct answer: Cite the violation, since extension cords may not substitute for permanent wiring
The IFC prohibits extension cords as a substitute for permanent wiring and prohibits running them through walls, ceilings, or floors.
Question 20: Under NFPA 72, smoke alarms in dwelling units must be replaced no later than how many years from their date of manufacture?
- 5 years
- 8 years
- 10 years (Correct answer)
- 15 years
Correct answer: 10 years
NFPA 72 requires smoke alarms to be replaced 10 years from the manufacture date or sooner if they fail testing.
Question 21: In an assembly occupancy, where must the approved occupant load sign be posted?
- Only in the building owner's office
- In a conspicuous place near the main exit or exit access doorway of the room (Correct answer)
- On the exterior of the roof
- Only on the fire department's inspection report
Correct answer: In a conspicuous place near the main exit or exit access doorway of the room
The IFC requires the maximum occupant load to be posted in a conspicuous place near the main exit or exit access doorway.
Question 22: Under NFPA 291, a fire hydrant with a rated capacity of 1,000-1,499 gpm should have its bonnet and caps painted which color?
- Light blue
- Green (Correct answer)
- Orange
- Red
Correct answer: Green
NFPA 291 uses light blue for 1,500+ gpm, green for 1,000-1,499 gpm, orange for 500-999 gpm, and red for under 500 gpm.
Question 23: In the NFPA 704 hazard diamond, what does the yellow quadrant indicate?
- Health hazard
- Flammability
- Instability/reactivity (Correct answer)
- Special hazards
Correct answer: Instability/reactivity
Yellow shows instability, blue shows health, red shows flammability, and white shows special hazards.
Question 24: Under NFPA 10, how often must portable fire extinguishers be visually inspected?
- Weekly
- Monthly (Correct answer)
- Annually
- Every six years
Correct answer: Monthly
NFPA 10 requires monthly inspection, annual maintenance, and periodic internal maintenance and hydrostatic testing.
Question 25: Under NFPA 25, standard-response sprinklers in service for how many years must be replaced or have representative samples tested?
- 10 years
- 20 years
- 25 years
- 50 years (Correct answer)
Correct answer: 50 years
NFPA 25 requires standard sprinklers to be replaced or sample-tested at 50 years and then every 10 years.
Question 26: A property owner disagrees with a fire marshal's interpretation of the fire code. Under the IFC, where should the owner's appeal normally go?
- The state attorney general
- The board of appeals established by the jurisdiction (Correct answer)
- The local police chief
- The insurance underwriter
Correct answer: The board of appeals established by the jurisdiction
IFC Section 109 provides for a board of appeals to hear challenges to the fire code official's decisions and interpretations.
Question 27: Which IFC fire apparatus access road condition requires an approved turnaround?
- Any road longer than 50 feet
- A dead-end access road longer than 150 feet (Correct answer)
- Any road wider than 20 feet
- Only roads serving high-rise buildings
Correct answer: A dead-end access road longer than 150 feet
The IFC requires an approved turnaround for dead-end fire apparatus access roads longer than 150 feet.
Question 28: Historically, which NFPA professional qualification standard addressed the job performance requirements of the fire marshal, and is now consolidated into NFPA 1030?
- NFPA 1031
- NFPA 1033
- NFPA 1035
- NFPA 1037 (Correct answer)
Correct answer: NFPA 1037
NFPA 1037 covered fire marshal qualifications before being consolidated with 1031, 1033, and 1035 into NFPA 1030.
Under NFPA 1730, how often should occupancies classified as high-risk generally be inspected?
What Practice Test Geeks adds beyond an AI chat for CFM
An AI chatbot can quiz you, but it can't reproduce the exam conditions or keep your record. Here you get:
- A timed, full-length CFM mock exam — 100 questions in 120 minutes with a 70% pass mark, modeled on the official exam's question count and time limit, followed by a score report broken down by exam domain.
- A fixed CFM question bank: the same test every attempt, so your score is comparable from one try to the next instead of changing with every regenerated quiz.
- Progress saved on your device: completed tests, scores and missed questions stay in My Progress, so you can retake only what you got wrong.
- A printable CFM cheat sheet you can print or save as a PDF.
- CFM flashcards built from the same question bank.
Practice questions written with AI assistance and published by Nathan Beja, founder of Practice Test Geeks. They are not real exam questions. Exam facts are checked against the official sources linked below. Editorial policy
Sources & references
Exam facts on this page (fees, format, dates, passing scores) are checked against these official sources; the date is our last check. Editorial policy
- iccsafe.org — Retake policy, exam format, time limit, registration, test delivery, eligibility, exam information · verified Nov 2026
- support.iccsafe.org — Renewal, score release, passing score · verified Nov 2026
- cdn-www-v2.iccsafe.org — Score validity · verified Nov 2026
- shop.iccsafe.org — Fees, registration deadline · verified Nov 2026