Air Conditioning Repair Service — Questions and Answers
Question 1: When performing a refrigerant recovery, the technician should recover the refrigerant until the system pressure reaches:
- 0 psig or as low as possible (Correct answer)
- 10 psig
- 30 psig
- 50 psig
Correct answer: 0 psig or as low as possible
EPA regulations require recovering refrigerant to 0 psig or as low as the recovery machine can achieve to minimize emissions.
Question 2: A technician notices that the evaporator coil is icing up during operation. Which service step should be performed FIRST?
- Check airflow across the evaporator (Correct answer)
- Add refrigerant to the system
- Replace the TXV
- Clean the condenser coil
Correct answer: Check airflow across the evaporator
Restricted airflow is the most common cause of evaporator icing, and checking it first eliminates the simplest root cause before invasive repairs.
Question 3: What is the purpose of performing a standing pressure test on a system after repair?
- To verify no leaks exist before charging with refrigerant (Correct answer)
- To check compressor capacity
- To measure superheat
- To calibrate the thermostat
Correct answer: To verify no leaks exist before charging with refrigerant
A standing pressure test uses dry nitrogen to verify system integrity and confirm no leaks are present before introducing refrigerant.
Question 4: Which oil is required for use in systems containing R-410A refrigerant?
- POE (polyolester) oil (Correct answer)
- Mineral oil
- Alkylbenzene oil
- PAG oil
Correct answer: POE (polyolester) oil
R-410A systems require POE (polyolester) oil because it is miscible with HFC refrigerants, ensuring proper lubrication throughout the system.
Question 5: During a service call, a technician measures suction pressure lower than normal and discharge pressure lower than normal. This most likely indicates:
- Low refrigerant charge (Correct answer)
- High refrigerant charge
- Dirty condenser coil
- Faulty reversing valve
Correct answer: Low refrigerant charge
Both suction and discharge pressures below normal simultaneously is a classic indicator of an undercharged (low refrigerant) system.
Question 6: Before replacing a compressor, a technician should always:
- Perform a system flush to remove contaminants (Correct answer)
- Increase the refrigerant charge by 10%
- Replace only the run capacitor
- Bypass the high-pressure switch
Correct answer: Perform a system flush to remove contaminants
Flushing removes acid, moisture, and debris from a failed compressor before installing a new one, preventing premature failure of the replacement.
Question 7: A technician is checking subcooling on a fixed-orifice system. Where should subcooling be measured?
- At the liquid line service valve near the condenser outlet (Correct answer)
- At the suction line near the compressor
- At the discharge line near the compressor
- At the inlet of the evaporator
Correct answer: At the liquid line service valve near the condenser outlet
Subcooling is measured at the liquid line leaving the condenser, comparing the actual temperature to the saturation temperature at that pressure.
Question 8: When using an electronic leak detector on an air conditioning system, the probe should be moved:
- Slowly along the bottom of fittings and connections (Correct answer)
- Rapidly across the entire unit
- Only along the top of refrigerant lines
- Directly over the Schrader valves only
Correct answer: Slowly along the bottom of fittings and connections
Refrigerant vapor is heavier than air and settles downward, so moving the probe slowly along the bottom of fittings ensures detection of leaking vapors.
Question 9: A technician replaces a contactor on a condensing unit. After the repair, the compressor hums but does not start. What is the most likely cause?
- Failed run capacitor (Correct answer)
- Open high-pressure switch
- Defective thermostat
- Clogged filter drier
Correct answer: Failed run capacitor
A humming compressor that won't start typically indicates a failed run or start capacitor that is not providing the necessary starting torque.
Question 10: What is the correct procedure when adding refrigerant to a system equipped with a TXV metering device?
- Charge by weight or target superheat at the evaporator outlet (Correct answer)
- Charge by subcooling only at the condenser
- Add refrigerant until sight glass clears
- Charge to manufacturer's listed operating pressure only
Correct answer: Charge by weight or target superheat at the evaporator outlet
TXV systems are best charged by weight per manufacturer specs or by targeting correct superheat, as sight glass clearing is not a reliable method for TXV systems.
Question 11: Which component's failure would most likely cause high superheat AND high subcooling simultaneously?
- Restricted liquid line or filter drier (Correct answer)
- Overcharged refrigerant
- Failed condenser fan motor
- Open suction service valve
Correct answer: Restricted liquid line or filter drier
A restriction in the liquid line or a clogged filter drier causes refrigerant to back up (high subcooling) before the restriction and starve the evaporator (high superheat) after it.
Question 12: What does a nitrogen purge during brazing accomplish?
- Prevents oxidation and carbon scale from forming inside the copper tubing (Correct answer)
- Increases the melting temperature of the solder
- Removes moisture from the atmosphere
- Pressurizes the system to check for leaks
Correct answer: Prevents oxidation and carbon scale from forming inside the copper tubing
Flowing dry nitrogen through the tubing during brazing displaces oxygen, preventing the formation of copper oxides (scale) that can contaminate the system.
Question 13: A split-system air conditioner has a normal suction pressure but an abnormally high discharge pressure. The MOST likely cause is:
- Dirty or blocked condenser coil (Correct answer)
- Low refrigerant charge
- Restricted filter drier
- Faulty TXV
Correct answer: Dirty or blocked condenser coil
A dirty condenser coil reduces heat rejection, causing refrigerant to remain at a higher temperature and pressure on the high side.
Question 14: When is it acceptable to mix different types of refrigerant in a single system?
- Never — mixing refrigerants is not permitted (Correct answer)
- Only when both are HFCs
- When the pressures are within 5 psig of each other
- Only if approved by the EPA in writing
Correct answer: Never — mixing refrigerants is not permitted
Mixing different refrigerants creates an unidentified blend that cannot be safely recovered, recycled, or identified, and is prohibited by EPA regulations.