NJATC Load Calculations — Questions and Answers
Question 1: According to NEC Table 220.12, what is the general lighting load in volt-amperes per square foot for a dwelling unit?
- 1 VA/sq ft
- 2 VA/sq ft
- 3 VA/sq ft (Correct answer)
- 4 VA/sq ft
Correct answer: 3 VA/sq ft
NEC Table 220.12 specifies 3 VA per square foot as the general lighting load for dwelling units.
Question 2: How many 20-ampere small appliance branch circuits are required by the NEC in the kitchen, pantry, breakfast room, and dining room of a dwelling unit?
- One
- Two (Correct answer)
- Three
- Four
Correct answer: Two
NEC 210.11(C)(1) requires at least two 20-ampere small appliance branch circuits for these areas of a dwelling.
Question 3: What demand factor is applied to the first 3,000 VA of general lighting load in a dwelling unit per NEC Table 220.42?
- 100% (Correct answer)
- 75%
- 50%
- 35%
Correct answer: 100%
NEC Table 220.42 specifies a 100% demand factor for the first 3,000 VA of general lighting and receptacle loads in a dwelling unit.
Question 4: Per NEC Table 220.55 Column C, what is the permitted demand load for a single household electric range rated at 12 kW or less?
- 6 kW
- 8 kW (Correct answer)
- 10 kW
- 12 kW
Correct answer: 8 kW
NEC Table 220.55 Column C permits an 8 kW demand load for a single household range rated at 12 kW or less.
Question 5: What minimum load in volt-amperes must be included per NEC 220.52(A) for each laundry branch circuit in a dwelling unit?
- 1,000 VA
- 1,500 VA (Correct answer)
- 2,000 VA
- 2,500 VA
Correct answer: 1,500 VA
NEC 220.52(A) requires a minimum 1,500 VA load for each laundry branch circuit included in a dwelling unit calculation.
Question 6: Per NEC 220.60, when can the smaller of two non-coincident loads (such as heating and cooling) be omitted from a dwelling service calculation?
- When the heating load exceeds 5 kW
- When both systems will not operate simultaneously (Correct answer)
- When the AC load is greater than heating
- When heating exceeds AC load by more than 50%
Correct answer: When both systems will not operate simultaneously
NEC 220.60 permits omitting the smaller non-coincident load when it is unlikely the two systems will operate at the same time.
Question 7: For a 240-volt, single-phase circuit supplying a 30-ampere load, what is the calculated apparent power?
- 3,600 VA
- 4,800 VA
- 6,000 VA
- 7,200 VA (Correct answer)
Correct answer: 7,200 VA
Apparent power = Voltage × Current = 240V × 30A = 7,200 VA for a single-phase circuit.
Question 8: Per NEC 220.44, what demand factor may be applied to receptacle loads in office buildings that exceed 10,000 VA?
- 100%
- 75%
- 50% (Correct answer)
- 25%
Correct answer: 50%
NEC 220.44 permits a 50% demand factor for receptacle loads in excess of 10,000 VA in commercial occupancies such as office buildings.
Question 9: What is the required calculated load per linear foot of show window lighting per NEC 220.14(G)?
- 100 VA
- 150 VA
- 200 VA (Correct answer)
- 250 VA
Correct answer: 200 VA
NEC 220.14(G) requires 200 VA per linear foot of show window when calculating lighting loads for retail display windows.
Question 10: At what percentage of the continuous load must branch circuit conductors and overcurrent devices be rated per NEC 210.20(A)?
- 100%
- 110%
- 125% (Correct answer)
- 150%
Correct answer: 125%
NEC 210.20(A) requires branch circuit conductors and OCPDs to be rated at not less than 125% of the continuous load.
Question 11: Which formula correctly calculates true power (watts) in a three-phase circuit?
- P = V × I
- P = V × I × 1.732
- P = V × I × 1.732 × PF (Correct answer)
- P = V² / R
Correct answer: P = V × I × 1.732 × PF
Three-phase true power equals line voltage × line current × √3 (1.732) × power factor.
Question 12: What simplified NEC calculation method can be used for dwelling unit service sizing as an alternative to the standard method?
- Abbreviated Load Method
- Optional Calculation per NEC 220.82 (Correct answer)
- Simplified Feeder Method
- Reduced Demand Method
Correct answer: Optional Calculation per NEC 220.82
NEC 220.82 provides an Optional Calculation that simplifies residential service sizing using a general load per square foot plus specific appliance loads.
Question 13: Per NEC 220.61(B)(1), at what percentage of the ungrounded conductor load may the neutral load for household ranges be calculated?
- 100%
- 85%
- 75%
- 70% (Correct answer)
Correct answer: 70%
NEC 220.61(B)(1) allows the neutral load for household ranges, wall ovens, and cooktops to be calculated at 70% of the ungrounded conductor load.
Question 14: What is the minimum volt-ampere load that must be calculated per NEC 220.14(I) for each general-purpose receptacle outlet in a dwelling unit?
- 90 VA
- 120 VA
- 150 VA
- 180 VA (Correct answer)
Correct answer: 180 VA
NEC 220.14(I) requires 180 VA per receptacle outlet when calculating general-purpose receptacle loads in a dwelling unit.
Question 15: Per NEC 430.22, at what percentage of the motor's full-load current rating must branch circuit conductors for a single motor be sized?
- 100%
- 115%
- 125% (Correct answer)
- 150%
Correct answer: 125%
NEC 430.22 requires branch circuit conductors supplying a single motor to be sized at not less than 125% of the motor's full-load current rating.
Question 16: When sizing feeder conductors for multiple motors per NEC 430.24, how is the largest motor's current contribution calculated?
- At 100% of FLC
- At 115% of FLC
- At 125% of FLC (Correct answer)
- At 150% of FLC
Correct answer: At 125% of FLC
NEC 430.24 requires the largest motor's full-load current to be multiplied by 125% when sizing feeder conductors for multiple motors.
Question 17: What is the power factor of a purely resistive circuit, such as one supplying only electric heating elements?
- 0.80
- 0.85
- 0.90
- 1.0 (Correct answer)
Correct answer: 1.0
A purely resistive circuit has a power factor of 1.0 (unity) because voltage and current are perfectly in phase.
Question 18: What is the maximum calculated load capacity in kilowatts of a 100-ampere, 240-volt, single-phase service entrance?
- 12 kW
- 18 kW
- 24 kW (Correct answer)
- 30 kW
Correct answer: 24 kW
Maximum load = 240V × 100A = 24,000W = 24 kW for a 100-ampere, 240-volt single-phase service.
Question 19: Per NEC 220.53, what demand factor may be applied when four or more fastened-in-place appliances (other than ranges, dryers, or HVAC) are served by the same feeder?
- 100%
- 90%
- 75% (Correct answer)
- 50%
Correct answer: 75%
NEC 220.53 permits a 75% demand factor when four or more fastened-in-place appliances (excluding ranges, dryers, and HVAC) are on the same feeder.
Question 20: Per NEC Table 220.42, what demand factor applies to general lighting loads above 12,500 VA in a commercial (non-dwelling) occupancy?
- 100%
- 75%
- 50% (Correct answer)
- 35%
Correct answer: 50%
NEC Table 220.42 specifies a 50% demand factor for commercial occupancy lighting loads that exceed the initial 12,500 VA threshold.
Question 21: When both electric heating and air conditioning are installed in a dwelling, which load is included in the service calculation per NEC 220.60?
- The sum of both loads
- The larger of the two non-coincident loads (Correct answer)
- The smaller of the two non-coincident loads
- The average of both loads
Correct answer: The larger of the two non-coincident loads
NEC 220.60 requires using the larger of the two non-coincident loads since heating and cooling systems are unlikely to operate simultaneously.