E2 Systems and Equipment 2 — Questions and Answers
Question 1: According to the NEC, what is the minimum clearance required above a switchboard in a commercial installation?
- 3 feet
- 6 feet (Correct answer)
- 6.5 feet
- 8 feet
Correct answer: 6 feet
NEC 110.26(A)(1) requires a minimum of 6 feet of headroom above electrical equipment such as switchboards.
Question 2: A commercial building's emergency lighting system is required to provide illumination for at least how long upon loss of normal power?
- 30 minutes
- 60 minutes
- 90 minutes (Correct answer)
- 120 minutes
Correct answer: 90 minutes
NEC 700.12 requires emergency lighting systems to provide at least 90 minutes of operation upon normal power failure.
Question 3: When inspecting a variable frequency drive (VFD) installation, which conductor issue is most critical to verify?
- Wire insulation color
- Conductor ampacity derating for harmonic heating (Correct answer)
- Use of aluminum conductors only
- Minimum 10 AWG branch circuit
Correct answer: Conductor ampacity derating for harmonic heating
VFDs produce harmonics that cause additional heating in conductors, requiring ampacity derating per NEC 310.15(A)(2).
Question 4: Under the NEC, a motor controller must be capable of interrupting the stalled-rotor current of the motor it controls. This rating is known as the:
- Full load current (FLC)
- Locked rotor current (LRC) (Correct answer)
- Service factor amperage
- Running overload rating
Correct answer: Locked rotor current (LRC)
Motor controllers must be rated for locked rotor current (LRC), which is the maximum current drawn when the motor shaft is stalled.
Question 5: In a commercial kitchen, a dishwasher is hardwired to a 20-ampere, 120-volt circuit. The NEC requires this circuit to be protected by a:
- Standard GFCI breaker (Correct answer)
- AFCI breaker
- GFCI with 4mA trip threshold
- Standard overcurrent device only
Correct answer: Standard GFCI breaker
NEC 210.8(B) requires GFCI protection for commercial kitchen equipment in areas where water is present.
Question 6: What does the NEC require for grounding electrode conductors at a commercial service entrance that uses a metal water pipe as a grounding electrode?
- The conductor must be at least 4 AWG copper
- A supplemental electrode must also be installed (Correct answer)
- The pipe must be bonded with a 6 AWG conductor only
- No supplemental electrode is needed if the pipe is 3/4 inch or larger
Correct answer: A supplemental electrode must also be installed
NEC 250.53(D)(2) requires a supplemental grounding electrode when a metal water pipe is used as a grounding electrode.
Question 7: A rooftop HVAC unit on a commercial building is served by a disconnect switch mounted on the unit. The NEC requires this disconnect to be:
- Lockable in the open position (Correct answer)
- Rated at 200% of the motor FLA
- Located inside the unit's electrical compartment
- A fused safety switch only
Correct answer: Lockable in the open position
NEC 430.102(B) and 440.14 require the disconnecting means for HVAC equipment to be lockable in the open (off) position.
According to the NEC, what is the minimum clearance required above a switchboard in a commercial installation?