SPED Pressure Testing & Commissioning 3 — Questions and Answers
Question 1: What ASME B31.3 hydrostatic test pressure multiplier is applied to the design pressure for normal fluid service?
- 1.1×
- 1.25×
- 1.5× (Correct answer)
- 2.0×
Correct answer: 1.5×
ASME B31.3 requires a hydrostatic test pressure of at least 1.5 times the design pressure for normal fluid service piping.
Question 2: During commissioning of a utility water system, a valve is found to pass slightly when in the closed position. This deficiency is classified as which punch list category?
- Category A (blocks mechanical completion) (Correct answer)
- Category B (can be addressed after startup)
- Category C (cosmetic, no action needed)
- Category D (requires design change)
Correct answer: Category A (blocks mechanical completion)
Valve passing in the closed position is a Category A punch item because it can affect safe operation and must be resolved before mechanical completion sign-off.
Question 3: Which test method uses acoustic emission sensors placed on the pipe exterior to detect leak location during pressurization?
- Hydrostatic test
- Pneumatic soap-bubble test
- Acoustic emission testing (AET) (Correct answer)
- Radiographic testing
Correct answer: Acoustic emission testing (AET)
Acoustic emission testing detects and locates leaks by analyzing high-frequency stress waves emitted from crack growth or fluid escaping through defects.
Question 4: When pressure testing a piping system with multiple pressure ratings, the test pressure is governed by which component?
- The highest-rated component in the system
- The lowest-rated component in the system (Correct answer)
- The average of all component ratings
- The pipeline designer's recommendation
Correct answer: The lowest-rated component in the system
The test pressure must not exceed the capability of the weakest (lowest-rated) component in the system to prevent damage during testing.
Question 5: Which commissioning activity verifies that instrument transmitters are reading correctly at known process conditions before startup?
- Loop checking (Correct answer)
- Hydrostatic testing
- HAZOP review
- Functional safety assessment
Correct answer: Loop checking
Loop checking involves applying a known signal or process condition and verifying the entire measurement loop reads correctly at the control system.
Question 6: A piping system is returned to service after a repair weld without re-testing. Under ASME B31.3, what minimum post-weld examination is required?
- Visual examination only
- 100% radiographic examination
- Pressure test at original test pressure
- Examination per the original construction code and Owner approval (Correct answer)
Correct answer: Examination per the original construction code and Owner approval
ASME B31.3 requires repairs to be examined and tested in accordance with the original construction requirements, subject to Owner-authorized alternatives.
Question 7: What is the purpose of a 'golden weld' or 'tie-in weld' lock-out procedure during pressure testing?
- To identify welds exempt from PWHT
- To prevent test pressure from entering sections not yet ready for testing (Correct answer)
- To mark welds requiring radiographic examination
- To denote welds made by certified welders
Correct answer: To prevent test pressure from entering sections not yet ready for testing
Tie-in weld isolation procedures ensure that pressurized test sections are physically separated from adjacent piping not yet constructed or cleared for testing.
What ASME B31.3 hydrostatic test pressure multiplier is applied to the design pressure for normal fluid service?