SOPD Frequency Control 5 — Questions and Answers
Question 1: What is the primary difference between 'spinning reserve' and 'non-spinning reserve' in frequency control?
- Spinning reserve is on synchronous units already online; non-spinning reserve requires unit startup (Correct answer)
- Spinning reserve responds in 30 minutes; non-spinning reserve responds in 10 minutes
- Spinning reserve is used only for over-frequency events; non-spinning for under-frequency
- Spinning reserve is thermal generation only; non-spinning includes hydro and wind
Correct answer: Spinning reserve is on synchronous units already online; non-spinning reserve requires unit startup
Spinning reserve is unloaded capacity on already-synchronized online units; non-spinning (supplemental) reserve requires starting offline units, taking longer to deploy.
Question 2: How does increased penetration of inverter-based resources (IBR) such as solar PV affect system frequency dynamics?
- IBR improves frequency response by providing faster governor action than synchronous generators
- IBR reduces system inertia if it displaces synchronous generation, making frequency more sensitive to disturbances (Correct answer)
- IBR automatically provides frequency response through built-in under-frequency protection relays
- IBR has no effect on frequency dynamics because it operates at unity power factor
Correct answer: IBR reduces system inertia if it displaces synchronous generation, making frequency more sensitive to disturbances
Inverter-based resources do not inherently provide synchronous inertia, so high IBR penetration that displaces synchronous generators reduces total system inertia.
Question 3: What is 'Control Performance Standard 1' (CPS1) as defined by NERC?
- A limit on the maximum rate of frequency change (ROCOF) during contingency events
- A statistical measure of how well a balancing authority's ACE correlates with interconnection frequency error over time (Correct answer)
- A requirement to maintain frequency within ±0.5 Hz of 60 Hz at all times
- A standard for the minimum spinning reserve a balancing authority must carry
Correct answer: A statistical measure of how well a balancing authority's ACE correlates with interconnection frequency error over time
CPS1 measures the one-minute average of ACE × frequency error over a year; a score ≥100% indicates the area is helping (not hurting) interconnection frequency control.
Question 4: During a frequency emergency, a system operator issues an 'Energy Emergency Alert' (EEA). What level indicates the operator has shed firm load?
- EEA Level 1
- EEA Level 2
- EEA Level 3 (Correct answer)
- EEA Level 4
Correct answer: EEA Level 3
EEA Level 3 indicates the operator has exhausted all other resources and is implementing firm load shedding to maintain system reliability.
Question 5: What is the effect of a 'flat frequency response' characteristic (infinite droop or blocked governor) on interconnection frequency control?
- It improves frequency stability by preventing oscillations between generators
- It reduces the unit's contribution to primary response, increasing frequency deviation for all interconnected areas (Correct answer)
- It allows the unit to provide more reactive power during voltage events
- It speeds up AGC response by removing governor deadband interference
Correct answer: It reduces the unit's contribution to primary response, increasing frequency deviation for all interconnected areas
A unit with blocked governors or infinite droop provides no primary frequency response, meaning other units must compensate and frequency deviations will be larger.
Question 6: A frequency disturbance causes frequency to drop to 59.3 Hz in the Western Interconnection. Which action would MOST quickly arrest further frequency decline?
- Committing additional fast-start combustion turbines (20-minute startup)
- Dispatching demand response programs with 10-minute notification
- Governor response from already-online generators with headroom (Correct answer)
- Purchasing emergency energy from neighboring interconnections via DC ties
Correct answer: Governor response from already-online generators with headroom
Governor primary response from online generators acts within seconds, far faster than starting offline units, activating demand response, or arranging emergency interchange.
Question 7: What condition is described when two synchronous areas are interconnected and one experiences a sudden generation loss causing frequency to drop in both areas?
- Islanding — each area separates and responds independently
- Interconnection frequency response — all synchronous generators in both areas contribute proportionally to governor droop (Correct answer)
- Resonance — the two areas' natural frequencies interact destructively
- Voltage collapse — reactive power transfer limits prevent real power support
Correct answer: Interconnection frequency response — all synchronous generators in both areas contribute proportionally to governor droop
In a synchronous interconnection, a frequency disturbance in one area is shared across all connected areas, with every online governor contributing to primary response proportional to its droop setting.
What is the primary difference between 'spinning reserve' and 'non-spinning reserve' in frequency control?