S-13 Water Supply and Pressure Requirements 1 — Questions and Answers
Question 1: What is the minimum residual pressure required at the highest outlet of a Class I or Class III standpipe system in New York City during operation?
- 65 psi
- 100 psi (Correct answer)
- 75 psi
- 50 psi
Correct answer: 100 psi
FDNY and NFPA 14 require a minimum residual pressure of 100 psi at the hydraulically most remote outlet for Class I and Class III standpipe systems.
Question 2: What is the maximum allowable pressure at any standpipe outlet hose connection to prevent hose control problems for firefighters?
- 150 psi
- 175 psi
- 200 psi (Correct answer)
- 250 psi
Correct answer: 200 psi
NFPA 14 limits standpipe hose connection pressure to a maximum of 175 psi without a pressure-reducing device; NYC requires the outlet not exceed 175 psi, and many references cap unregulated flow at 200 psi—but the standard working maximum without PRVs is 175 psi per NFPA 14.
Question 3: Which water supply source is considered the primary supply for standpipe systems in most New York City high-rise buildings?
- Gravity tank on the roof
- City water main connection
- Fire pump drawing from a suction tank (Correct answer)
- Pressure tank in the basement
Correct answer: Fire pump drawing from a suction tank
In most NYC high-rise standpipe systems, a fire pump drawing from a dedicated suction tank provides the primary pressurized water supply to meet flow and pressure demands.
Question 4: What minimum flow rate must a Class I standpipe system be capable of delivering at the two most hydraulically remote 2½-inch outlets simultaneously?
- 250 gpm per outlet
- 500 gpm total (Correct answer)
- 350 gpm total
- 750 gpm total
Correct answer: 500 gpm total
NFPA 14 requires Class I and Class III standpipe systems to supply a minimum of 500 gpm total (250 gpm per outlet) to the two most remote 2½-inch hose connections simultaneously.
Question 5: A gravity tank used as a water supply for a standpipe system must have its bottom elevation at least how many feet above the highest hose outlet it serves?
- 15 feet
- 20 feet
- 25 feet (Correct answer)
- 35 feet
Correct answer: 25 feet
New York City Building Code and NFPA 14 require the bottom of a gravity tank to be at least 25 feet above the highest standpipe outlet it supplies to develop sufficient static pressure.
Question 6: What is the purpose of a pressure-maintenance (jockey) pump in a standpipe water supply system?
- To boost pressure during active firefighting
- To compensate for minor system leaks and maintain system pressure without starting the main fire pump (Correct answer)
- To fill the suction tank automatically
- To test standpipe pressure weekly
Correct answer: To compensate for minor system leaks and maintain system pressure without starting the main fire pump
A jockey (pressure-maintenance) pump is a small pump that cycles on and off to maintain standpipe system pressure, compensating for minor leakage without activating the larger main fire pump.
Question 7: Under FDNY regulations, what is the minimum capacity of a suction tank that serves as the sole water supply for a standpipe system in a building over 100 feet tall?
- 3,500 gallons
- 5,000 gallons
- 7,500 gallons (Correct answer)
- 10,000 gallons
Correct answer: 7,500 gallons
FDNY and NYC Building Code require a minimum suction tank capacity of 7,500 gallons to provide an adequate reserve water supply for standpipe operations in tall buildings.
What is the minimum residual pressure required at the highest outlet of a Class I or Class III standpipe system in New York City during operation?