NETA Electrical Testing Procedures & Equipment Operation 3 — Questions and Answers
Question 1: The polarization index (PI) is calculated by dividing the insulation resistance measured at 10 minutes by the reading at:
- 30 seconds
- 1 minute (Correct answer)
- 5 minutes
- 15 minutes
Correct answer: 1 minute
PI = IR at 10 minutes divided by IR at 1 minute; a value of 2.0 or above generally indicates acceptable insulation condition.
Question 2: Which safety precaution is mandatory before connecting a megohmmeter to a large capacitive load such as a cable run?
- Short the leads together to zero the instrument
- Verify the load is de-energized and fully discharged (Correct answer)
- Set the instrument to AC mode
- Connect the guard terminal to ground
Correct answer: Verify the load is de-energized and fully discharged
Capacitive equipment stores dangerous charge; the equipment must be de-energized and discharged (verified with a voltmeter) before connecting the megohmmeter.
Question 3: In a transformer turns ratio (TTR) test, a ratio error exceeding what percentage typically triggers further investigation per NETA MTS?
- 0.1%
- 0.5% (Correct answer)
- 1.0%
- 5.0%
Correct answer: 0.5%
NETA MTS flags a turns ratio deviation greater than 0.5% from the nameplate ratio as requiring further evaluation for possible winding faults.
Question 4: When performing an AC high-potential (hipot) test on cable insulation, the test voltage is typically applied for:
- 10 seconds
- 1 minute (Correct answer)
- 5 minutes
- 15 minutes
Correct answer: 1 minute
The standard AC hipot withstand duration for cable insulation per NETA MTS is 1 minute at the specified test voltage.
Question 5: A very low frequency (VLF) test on medium-voltage cable uses a test frequency of:
- 60 Hz
- 50 Hz
- 0.1 Hz (Correct answer)
- 400 Hz
Correct answer: 0.1 Hz
VLF testing uses 0.1 Hz (or 0.01–0.1 Hz range) to stress cable insulation at a fraction of the normal power frequency, reducing the required kVA from the test set.
Question 6: During a sweep frequency response analysis (SFRA) test on a power transformer, the primary purpose is to detect:
- Insulation moisture content
- Winding deformation or displacement due to mechanical stress (Correct answer)
- Core loss and exciting current
- Bushing capacitance imbalance
Correct answer: Winding deformation or displacement due to mechanical stress
SFRA compares frequency response signatures to detect physical winding movement, deformation, or damage caused by through-faults or transportation.
Question 7: What test is performed to verify that a protective relay correctly operates at the designed current pickup level?
- Contact resistance test
- Insulation resistance test
- Secondary current injection test (Correct answer)
- Dielectric absorption test
Correct answer: Secondary current injection test
Secondary injection testing applies a calibrated current directly to the relay's current input terminals to verify pickup, timing, and trip function without energizing primary equipment.
The polarization index (PI) is calculated by dividing the insulation resistance measured at 10 minutes by the reading at: