NEC Overcurrent Protection & Grounding 2 — Questions and Answers
Question 1: According to NEC 240.4(D), what is the maximum overcurrent protection permitted for 14 AWG copper conductors?
- 15 amperes (Correct answer)
- 20 amperes
- 25 amperes
- 30 amperes
Correct answer: 15 amperes
NEC 240.4(D) limits overcurrent protection for 14 AWG copper to 15 amperes regardless of the conductor's ampacity.
Question 2: What NEC article governs the use of ground-fault circuit-interrupter (GFCI) protection?
- Article 210 (Correct answer)
- Article 230
- Article 250
- Article 310
Correct answer: Article 210
Article 210 covers branch circuits, including the GFCI protection requirements for receptacles in wet and damp locations.
Question 3: What is the minimum size copper equipment grounding conductor (EGC) required for a circuit protected by a 60-ampere overcurrent device per NEC Table 250.122?
- 10 AWG (Correct answer)
- 8 AWG
- 6 AWG
- 4 AWG
Correct answer: 10 AWG
NEC Table 250.122 requires a minimum 10 AWG copper EGC for circuits protected at 60 amperes.
Question 4: Under NEC 250.24(A), a service-entrance grounded conductor (neutral) must be connected to the grounding electrode system at which location?
- At the service disconnecting means enclosure (Correct answer)
- At the first panelboard downstream
- At the meter base only
- At the transformer secondary
Correct answer: At the service disconnecting means enclosure
NEC 250.24(A) requires the grounded conductor to be bonded to the grounding electrode system at the service disconnecting means.
Question 5: A 20-ampere, 120-volt branch circuit breaker trips repeatedly under normal load. Per NEC principles, what is the FIRST corrective action?
- Evaluate the actual load versus the circuit's rated capacity (Correct answer)
- Replace the breaker with a 30-ampere device
- Install a larger wire on the circuit
- Add a second circuit breaker in parallel
Correct answer: Evaluate the actual load versus the circuit's rated capacity
NEC requires conductors and overcurrent devices to be properly sized for the load; the load must be evaluated before upsizing protection.
Question 6: What does NEC 250.119 require regarding identification of equipment grounding conductors?
- Continuous green color or green with yellow stripes, or bare (Correct answer)
- White or gray insulation only
- Orange insulation for high-voltage circuits
- Black insulation with green tape at terminations
Correct answer: Continuous green color or green with yellow stripes, or bare
NEC 250.119 requires EGCs to be identified by green insulation, green with yellow stripe, or bare copper.
Question 7: Per NEC 240.21(B)(1), a tap conductor from a feeder must not exceed what length when not otherwise protected at its point of supply?
- 10 feet (Correct answer)
- 25 feet
- 50 feet
- 100 feet
Correct answer: 10 feet
NEC 240.21(B)(1) allows tap conductors up to 10 feet without overcurrent protection at the tap point if specific conditions are met.
According to NEC 240.4(D), what is the maximum overcurrent protection permitted for 14 AWG copper conductors?