NEC Overcurrent Protection & Controls 3 — Questions and Answers
Question 1: Where supplementary overcurrent protection is used, per NEC 240.10 it shall NOT be used as a substitute for what?
- Branch-circuit overcurrent protection (Correct answer)
- Surge protection
- Ground-fault protection of equipment
- Arc-fault protection
Correct answer: Branch-circuit overcurrent protection
NEC 240.10 states supplementary overcurrent protection is not a substitute for required branch-circuit overcurrent devices.
Question 2: Per NEC 240.24(A), overcurrent devices must generally be readily accessible and installed so the center of the operating handle is not more than what height above the floor?
- 1.8 m (6 ft)
- 2.0 m (6 ft 7 in.) (Correct answer)
- 2.5 m (8 ft)
- 3.0 m (10 ft)
Correct answer: 2.0 m (6 ft 7 in.)
NEC 240.24(A) limits the operating handle height to 2.0 m (6 ft 7 in.) above the floor or working platform.
Question 3: Per NEC 240.24(D), overcurrent devices shall not be located where exposed to what?
- Direct sunlight
- Physical damage (Correct answer)
- Cold temperatures
- Humidity below 30%
Correct answer: Physical damage
NEC 240.24(D) prohibits locating overcurrent devices where they would be exposed to physical damage.
Question 4: Per NEC 240.24(E), overcurrent devices shall not be located in what location in dwelling units?
- Bedroom closets
- Bathrooms (Correct answer)
- Hallways
- Basements
Correct answer: Bathrooms
NEC 240.24(E) prohibits overcurrent devices in bathrooms of dwelling units and guest rooms.
Question 5: Per NEC 240.24(F), overcurrent devices shall not be located over what?
- Steps of a stairway (Correct answer)
- A doorway
- A window
- An electric meter
Correct answer: Steps of a stairway
NEC 240.24(F) prohibits locating overcurrent devices over the steps of a stairway.
Question 6: Per NEC 240.32, enclosures for overcurrent devices in damp or wet locations shall comply with what requirement?
- Be painted with rust-inhibiting coating
- Prevent moisture or water from entering or accumulating (Correct answer)
- Be installed only indoors
- Use only plastic enclosures
Correct answer: Prevent moisture or water from entering or accumulating
NEC 240.32 requires damp/wet location enclosures to prevent moisture or water from entering and accumulating.
Question 7: Per NEC 240.33, enclosures for overcurrent devices shall generally be mounted in what position?
- Horizontal only
- In a vertical position unless that is impracticable (Correct answer)
- Face down
- At a 45-degree angle
Correct answer: In a vertical position unless that is impracticable
NEC 240.33 requires enclosures to be mounted vertically unless that orientation is shown to be impracticable.
Where supplementary overcurrent protection is used, per NEC 240.10 it shall NOT be used as a substitute for what?