NABCEP NEC Article 690 Applications 4 — Questions and Answers
Question 1: NEC 690.71(A) covers storage batteries used with PV systems. What minimum voltage requirement applies to battery installations in dwelling units?
- Battery systems must not exceed 50 V dc nominal (Correct answer)
- Battery systems in dwellings must use only sealed, valve-regulated batteries
- Battery nominal voltage must not exceed the system voltage limits of Article 690
- There is no voltage restriction for dwelling battery systems
Correct answer: Battery systems must not exceed 50 V dc nominal
NEC 690.71(A) limits battery systems in dwelling units to 50 V dc nominal or less to reduce shock hazard in residential applications.
Question 2: Per NEC 690.74, battery interconnect conductors must be sized for at least what percentage of the rated ampacity required for the circuit?
- 100%
- 125% (Correct answer)
- 156%
- 80%
Correct answer: 125%
NEC 690.74 requires battery interconnect conductors to be sized at 125% of the maximum current for which the circuit is rated.
Question 3: According to NEC 690.72, what device is required to prevent overcharging of batteries in a PV system?
- A manual disconnect switch at the battery terminals
- A charge controller or other approved current-limiting means (Correct answer)
- An overcurrent protective device rated at 80% of battery capacity
- A bidirectional inverter only
Correct answer: A charge controller or other approved current-limiting means
NEC 690.72 requires a listed charge controller or other approved means to prevent overcharging and potential battery damage or fire.
Question 4: NEC 690.10 sets maximum voltage limits for PV systems on one- and two-family dwellings. What is the maximum system voltage for these residential installations?
- 300 V dc
- 600 V dc (Correct answer)
- 1000 V dc
- 1500 V dc
Correct answer: 600 V dc
NEC 690.10 limits PV systems on one- and two-family dwellings to a maximum system voltage of 600 V dc.
Question 5: When an inverter is used in a PV system, NEC 690.60 requires that inverters listed for interactive operation must be listed and identified for use with which type of system?
- Stand-alone systems only
- Interactive (utility-interactive or grid-tied) systems (Correct answer)
- Both stand-alone and interactive systems simultaneously
- Battery backup systems only
Correct answer: Interactive (utility-interactive or grid-tied) systems
NEC 690.60 requires inverters for grid-tied applications to be listed and identified for utility-interactive operation to ensure safety and compatibility.
Question 6: NEC 690.64 addresses the point of connection for PV systems to a distribution system. What limitation applies to the sum of all power sources connected to a busbar?
- The combined current ratings must not exceed 150% of the busbar rating
- The combined current ratings must not exceed 120% of the busbar rating (Correct answer)
- The power sources must not exceed 50% of the busbar rating
- No limitation applies as long as overcurrent protection is provided
Correct answer: The combined current ratings must not exceed 120% of the busbar rating
Per NEC 690.64, the sum of the ampere ratings of all overcurrent devices on a busbar must not exceed 120% of the busbar's ampere rating.
Question 7: For a stand-alone PV system powering a dwelling, NEC 690.10(C) requires the system to meet which additional code requirement?
- It must have a utility interconnection as a backup
- It must supply the loads in compliance with NEC Article 230 requirements (Correct answer)
- It must include a generator transfer switch
- All wiring must be in metal conduit
Correct answer: It must supply the loads in compliance with NEC Article 230 requirements
NEC 690.10(C) requires stand-alone systems to supply loads at voltages complying with NEC Article 230, maintaining safe voltage levels for premises wiring.
NEC 690.71(A) covers storage batteries used with PV systems.
What minimum voltage requirement applies to battery installations in dwelling units?