NABCEP Installation & Safety 5 β Questions and Answers
Question 1: When torquing module mounting hardware, why is it important to follow the manufacturer's specified torque values?
- To comply with aesthetic requirements of the rail manufacturer
- To ensure structural integrity without stripping threads or cracking frames, while maintaining warranty (Correct answer)
- To satisfy NEC electrical code requirements for conductors
- To meet the minimum wind-uplift calculation only
Correct answer: To ensure structural integrity without stripping threads or cracking frames, while maintaining warranty
Proper torque prevents under-tightening (which allows loosening) and over-tightening (which strips threads or cracks aluminum frames), and manufacturer specs are required to maintain equipment warranties.
Question 2: A worker is about to connect a second PV string to a combiner box that already has one string energized. What hazard must they address first?
- Voltage drop from the first string
- Backfeed current from the existing string through the new fuse position during connection (Correct answer)
- Grounding of the new string's racking
- The need to re-label the junction box
Correct answer: Backfeed current from the existing string through the new fuse position during connection
When one string is energized in the combiner, connecting a second string can create backfeed current through the new fuse position, risking arcing and injury during connection.
Question 3: What is the primary reason PV wire (USE-2/PV Wire) is used instead of standard THWN-2 wire for module-level wiring?
- PV wire is less expensive than THWN-2
- PV wire is rated for direct sunlight exposure and wet locations at elevated temperatures (Correct answer)
- THWN-2 cannot be used in conduit
- PV wire has lower resistance than THWN-2
Correct answer: PV wire is rated for direct sunlight exposure and wet locations at elevated temperatures
PV wire and USE-2 are specifically rated for prolonged sunlight exposure, wet locations, and higher temperature ratings, making them suitable for outdoor array wiring.
Question 4: Which of the following is an example of an engineering control to reduce fall hazards during rooftop PV installation?
- Providing workers with fall-arrest harnesses
- Installing temporary guardrails along roof edges before workers begin installation (Correct answer)
- Conducting a safety briefing before work begins
- Posting warning signs on the ground below the work area
Correct answer: Installing temporary guardrails along roof edges before workers begin installation
Engineering controls such as temporary guardrails physically prevent falls by creating a barrier, and are preferred over administrative controls or PPE in the hierarchy of controls.
Question 5: What is the function of a ground fault protection device (GFPD) in a PV system?
- It limits the maximum current output of the array
- It detects unintended current flow to ground and disconnects the faulted circuit to prevent fire (Correct answer)
- It protects the inverter from over-voltage surges
- It monitors the system's grounding electrode resistance
Correct answer: It detects unintended current flow to ground and disconnects the faulted circuit to prevent fire
A GFPD monitors for current flowing outside its intended path to ground, and when detected, disconnects the circuit to prevent fires caused by arcing at the fault point.
Question 6: According to OSHA, what is the required minimum illumination level for general construction work areas?
- 3 foot-candles
- 5 foot-candles (Correct answer)
- 10 foot-candles
- 30 foot-candles
Correct answer: 5 foot-candles
OSHA 1926.56 requires a minimum of 5 foot-candles of illumination for general construction areas, warehouses, corridors, hallways, and exitways.
Question 7: What is the primary purpose of bonding all metal parts of a PV array racking system together?
- To improve the efficiency of the modules by reducing stray currents
- To establish a low-impedance fault path so overcurrent devices operate quickly during a ground fault (Correct answer)
- To prevent corrosion between dissimilar metals
- To meet aesthetic requirements for grounding conductor visibility
Correct answer: To establish a low-impedance fault path so overcurrent devices operate quickly during a ground fault
Equipment bonding creates a low-impedance path back to the source so that a ground fault produces enough current to trip the overcurrent protective device and clear the fault safely.
When torquing module mounting hardware, why is it important to follow the manufacturer's specified torque values?