NABCEP Commissioning 3 — Questions and Answers
Question 1: Which NEC article governs the labeling requirements that must be verified during PV system commissioning?
- Article 690 (Correct answer)
- Article 705
- Article 480
- Article 310
Correct answer: Article 690
NEC Article 690 contains all PV-specific installation and labeling requirements, including mandatory warning labels at disconnects and combiner boxes.
Question 2: During commissioning, an insulation resistance test on a PV source circuit reads 0.5 MΩ at 500 V. How should the installer interpret this result?
- Acceptable — above 1 kΩ per volt is sufficient
- Borderline — monitor but proceed
- Unacceptable — investigate for ground fault or damaged insulation (Correct answer)
- Normal for wet conditions — retest when dry
Correct answer: Unacceptable — investigate for ground fault or damaged insulation
Industry practice requires insulation resistance values well above 1 MΩ; 0.5 MΩ suggests damaged insulation or a ground fault that must be corrected.
Question 3: What is the purpose of recording I-V curve data during PV system commissioning?
- To set the inverter's MPPT frequency
- To establish a performance baseline for future degradation comparison (Correct answer)
- To satisfy utility net metering billing requirements
- To calibrate the ground fault detection circuit
Correct answer: To establish a performance baseline for future degradation comparison
I-V curve measurements at commissioning serve as the baseline against which future measurements are compared to detect degradation or faults.
Question 4: A commissioning technician finds that PV module frames are not bonded to the racking system. Which code section is violated?
- NEC 690.43 — Equipment Grounding (Correct answer)
- NEC 690.35 — Ungrounded Systems
- NEC 705.12 — Load-Side Connections
- NEC 690.13 — Disconnecting Means
Correct answer: NEC 690.43 — Equipment Grounding
NEC 690.43 requires that non-current-carrying metal parts of PV modules and equipment be bonded to the equipment grounding system.
Question 5: When performing a functional test of a DC arc fault circuit interrupter (AFCI) during commissioning, what is the expected outcome?
- The inverter output power increases by 10%
- The AFCI trips and must be manually reset after the test (Correct answer)
- The array voltage drops to zero automatically
- The ground fault LED illuminates on the combiner
Correct answer: The AFCI trips and must be manually reset after the test
A successful AFCI self-test or trip test causes the device to open the circuit and require a manual reset, confirming protective function.
Question 6: During commissioning of a roof-mounted residential system, the installer cannot locate the required rapid shutdown initiation device. What should happen?
- Proceed — rapid shutdown only applies to commercial systems
- Document the omission and commission the system provisionally
- Do not commission the system until the RSD device is installed and labeled (Correct answer)
- Bypass the RSD and note it for a future service call
Correct answer: Do not commission the system until the RSD device is installed and labeled
NEC 690.12 requires rapid shutdown systems on all rooftop PV systems; the system must not be commissioned without this required safety equipment in place.
Question 7: What reading should a clamp-on DC ammeter show on a shaded string during peak sun hours compared to an unshaded string of identical modules?
- Higher current due to voltage redistribution
- Lower current proportional to the degree of shading (Correct answer)
- Identical current because bypass diodes compensate fully
- Zero current because shading triggers string protection
Correct answer: Lower current proportional to the degree of shading
Shading reduces short-circuit current (Isc) in the affected cells, so the entire shaded string produces less current than an unshaded string.
Which NEC article governs the labeling requirements that must be verified during PV system commissioning?