Journeyman Plumbers Exam Gas Piping Systems 3 β Questions and Answers
Question 1: What is the required pressure test for new gas piping before placing it in service under the International Fuel Gas Code?
- 10 psi for 15 minutes
- 3 psi for 10 minutes (Correct answer)
- 1.5 times the operating pressure for 10 minutes
- 50 psi for 1 hour
Correct answer: 3 psi for 10 minutes
New gas piping systems must be pressure tested at no less than 3 psi gauge for a minimum of 10 minutes to verify there are no leaks before the gas is turned on.
Question 2: A gas appliance connector flexible hose may NOT be used to connect which type of appliance?
- Gas range
- Water heater
- Built-in oven (Correct answer)
- Gas dryer
Correct answer: Built-in oven
Built-in ovens are considered permanently installed appliances and must be connected with rigid piping, not flexible appliance connectors.
Question 3: When gas piping passes through a wall, floor, or ceiling, it must be protected by:
- A rubber grommet
- A sleeve or protective coating (Correct answer)
- A metal conduit pipe
- No protection is required
Correct answer: A sleeve or protective coating
Gas piping penetrating walls, floors, or ceilings must be protected with a sleeve or protective coating to prevent abrasion damage to the pipe.
Question 4: What is the specific gravity of propane compared to air?
- 0.55 (lighter than air)
- 1.0 (same as air)
- 1.5 (heavier than air) (Correct answer)
- 2.5 (much heavier than air)
Correct answer: 1.5 (heavier than air)
Propane has a specific gravity of approximately 1.5, making it heavier than air, which causes it to settle in low areas such as basements and pits.
Question 5: The BTU content of one cubic foot of natural gas is approximately:
- 500 BTU
- 1,000 BTU (Correct answer)
- 2,500 BTU
- 5,000 BTU
Correct answer: 1,000 BTU
Natural gas contains approximately 1,000 BTU per cubic foot, a value used in load calculations when sizing gas piping and meters.
Question 6: Which of the following joints is NOT acceptable for use in gas piping systems?
- Threaded joints with approved sealant
- Welded joints
- Solvent-cemented plastic pipe joints (Correct answer)
- Flared joints on copper tubing
Correct answer: Solvent-cemented plastic pipe joints
Solvent-cemented joints on plastic pipe are not acceptable for gas distribution inside buildings, as they are not rated for gas service in above-ground applications.
Question 7: A manual shutoff valve must be installed within what distance of each gas appliance?
- 3 feet
- 5 feet
- 6 feet (Correct answer)
- 10 feet
Correct answer: 6 feet
The IFGC requires a manual shutoff valve to be installed within 6 feet of each gas appliance to allow for quick isolation in an emergency.
What is the required pressure test for new gas piping before placing it in service under the International Fuel Gas Code?