ISA CAP Control Systems & Instrumentation 2 — Questions and Answers
Question 1: In a cascade control system, the output of the primary (master) controller becomes the:
- Measured variable of the secondary loop
- Setpoint of the secondary (slave) controller (Correct answer)
- Manipulated variable of the primary loop
- Disturbance input to the process
Correct answer: Setpoint of the secondary (slave) controller
In cascade control, the primary controller's output sets the setpoint for the secondary controller, allowing faster disturbance rejection.
Question 2: A thermocouple produces an EMF based on the Seebeck effect. What is the purpose of cold junction compensation?
- To amplify the thermocouple output signal
- To correct for the reference junction temperature not being at 0°C (Correct answer)
- To linearize the thermocouple characteristic curve
- To protect the thermocouple from electrical noise
Correct answer: To correct for the reference junction temperature not being at 0°C
Cold junction compensation accounts for the actual reference junction temperature so the measured EMF accurately represents the process temperature.
Question 3: What does the term 'rangeability' refer to in a control valve?
- The maximum allowable pressure drop across the valve
- The ratio of maximum to minimum controllable flow (Correct answer)
- The travel distance between fully open and fully closed positions
- The operating temperature range of the valve body
Correct answer: The ratio of maximum to minimum controllable flow
Rangeability is the ratio of the maximum to minimum flow that the valve can control while maintaining its specified flow characteristic.
Question 4: In process control, what is 'offset' in the context of proportional-only control?
- The time delay before the controller begins responding
- A sustained steady-state error between setpoint and process variable (Correct answer)
- The derivative kick experienced on setpoint changes
- The integral windup accumulated during saturation
Correct answer: A sustained steady-state error between setpoint and process variable
Proportional-only controllers have inherent offset because a nonzero error is required to produce a nonzero control output.
Question 5: A 4-20 mA transmitter is configured for a 0-100 psi range. What process pressure corresponds to a signal of 12 mA?
- 50 psi (Correct answer)
- 60 psi
- 40 psi
- 75 psi
Correct answer: 50 psi
12 mA is the midpoint of the 4-20 mA span (16 mA range), representing 50% of the 0-100 psi range, which equals 50 psi.
Question 6: Which control valve characteristic provides approximately equal percentage changes in flow for equal increments of valve travel?
- Linear characteristic
- Quick-opening characteristic
- Equal-percentage characteristic (Correct answer)
- Parabolic characteristic
Correct answer: Equal-percentage characteristic
An equal-percentage characteristic means each increment of valve travel produces the same percentage change in flow relative to current flow.
Question 7: What is the primary advantage of using a Coriolis mass flow meter over a volumetric flow meter in custody transfer applications?
- Lower installation cost and simpler maintenance
- Direct mass measurement unaffected by fluid density changes (Correct answer)
- Higher accuracy only at very low flow rates
- Compatibility with all corrosive fluid types
Correct answer: Direct mass measurement unaffected by fluid density changes
Coriolis meters measure mass flow directly, eliminating errors caused by density variations due to temperature, pressure, or composition changes.
In a cascade control system, the output of the primary (master) controller becomes the: