InterNACHI Electrical Systems and Safety 4 — Questions and Answers
Question 1: What is the maximum height above the floor at which a standard wall-mounted electrical outlet may be installed per general accessibility guidelines?
- 18 inches
- 36 inches
- 48 inches
- No maximum is specified in the NEC (Correct answer)
Correct answer: No maximum is specified in the NEC
The NEC does not specify a maximum height for receptacle installation, though accessibility guidelines (ADA) recommend no higher than 48 inches.
Question 2: An inspector observes a service entrance cable with damaged outer insulation at the weatherhead. What is the primary concern?
- Water intrusion causing corrosion inside the meter base (Correct answer)
- Reduced amperage capacity of the service
- The utility company will disconnect service automatically
- Damaged insulation affects only aesthetics
Correct answer: Water intrusion causing corrosion inside the meter base
Damaged service entrance cable insulation allows moisture to enter the cable and meter base, causing corrosion and potential arcing failures.
Question 3: Which of the following is the correct InterNACHI-recommended finding when a home inspector observes a 60-amp main disconnect in a home with central air conditioning and electric range?
- 60-amp service is adequate for any modern home
- The service capacity appears insufficient for the electrical loads present and evaluation by an electrician is recommended (Correct answer)
- This only needs reporting if the panel is over 40 years old
- 60-amp service is acceptable if no additions have been made
Correct answer: The service capacity appears insufficient for the electrical loads present and evaluation by an electrician is recommended
Modern homes with central AC and electric cooking typically require 150–200 amp service; 60-amp service is likely undersized and warrants an electrician's evaluation.
Question 4: A home inspector finds Federal Pacific Electric (FPE) Stab-Lok panel in a home. What should the report state?
- FPE panels are recalled and must be replaced immediately
- FPE Stab-Lok panels have documented reliability concerns and evaluation by a licensed electrician is recommended (Correct answer)
- FPE panels are acceptable if breakers do not trip during inspection
- No action needed if the panel is less than 30 years old
Correct answer: FPE Stab-Lok panels have documented reliability concerns and evaluation by a licensed electrician is recommended
FPE Stab-Lok panels have a documented history of breaker failures and fire risk; inspectors should recommend evaluation but cannot require replacement.
Question 5: What does it mean when an electrical panel has its neutral and ground buses bonded together in a sub-panel?
- This is a code-compliant practice in all panels
- This is a defect that creates a parallel neutral path and shock hazard (Correct answer)
- Bonding is only required in the main panel and permitted in sub-panels
- This indicates the sub-panel has an improper main breaker
Correct answer: This is a defect that creates a parallel neutral path and shock hazard
In sub-panels, the neutral and ground buses must be separated because bonding them creates a parallel return path that can energize ground wires.
Question 6: What type of electrical hazard is indicated by scorch marks or discoloration around an outlet or switch cover plate?
- Overloaded neutral conductor
- Evidence of arcing or overheating at that device (Correct answer)
- Normal aging of plastic outlet covers
- Indication of reversed polarity only
Correct answer: Evidence of arcing or overheating at that device
Scorch marks or discoloration around electrical devices indicate past or ongoing arcing or heat buildup, which is a serious fire hazard.
Question 7: According to InterNACHI standards, what is an inspector's responsibility when they cannot access an electrical panel due to stored items blocking it?
- Move the items and inspect the panel
- Skip the panel and note no deficiencies were observed
- Report the panel as inaccessible and recommend evaluation (Correct answer)
- Assume the panel is code-compliant if the home passed prior inspections
Correct answer: Report the panel as inaccessible and recommend evaluation
When a panel cannot be accessed, the inspector must report it as inaccessible and recommend that it be evaluated when access is available.
What is the maximum height above the floor at which a standard wall-mounted electrical outlet may be installed per general accessibility guidelines?