HVAC Ventilation Design 2 — Questions and Answers
Question 1: According to ASHRAE 62.1, what is the minimum outdoor air ventilation rate for an office space occupied at 5 people per 1,000 sq ft?
- 5 cfm per person
- 10 cfm per person (Correct answer)
- 15 cfm per person
- 20 cfm per person
Correct answer: 10 cfm per person
ASHRAE 62.1 specifies 10 cfm per person as the minimum outdoor air rate for office occupancies under standard conditions.
Question 2: What does the term 'ventilation effectiveness' describe in HVAC design?
- The ratio of supply air to return air
- How efficiently outdoor air reaches the breathing zone (Correct answer)
- The efficiency of the air handler fan
- The percentage of recirculated air in the system
Correct answer: How efficiently outdoor air reaches the breathing zone
Ventilation effectiveness (Ev) measures how well the outdoor air delivered to a space actually reaches the occupants' breathing zone.
Question 3: A demand-controlled ventilation (DCV) system uses which sensor to modulate outdoor air intake?
- Humidity sensor
- CO2 sensor (Correct answer)
- VOC sensor
- Temperature sensor
Correct answer: CO2 sensor
DCV systems use CO2 sensors as a proxy for occupancy level to dynamically adjust outdoor air supply and reduce energy waste.
Question 4: What is the primary purpose of an energy recovery ventilator (ERV) compared to a heat recovery ventilator (HRV)?
- ERV recovers heat only; HRV recovers both heat and moisture
- ERV recovers both heat and moisture; HRV recovers heat only (Correct answer)
- ERV filters air; HRV recovers heat
- ERV is for cooling climates; HRV is for heating climates
Correct answer: ERV recovers both heat and moisture; HRV recovers heat only
An ERV transfers both sensible heat and latent moisture between exhaust and supply airstreams, while an HRV transfers sensible heat only.
Question 5: Which ventilation strategy introduces 100% outdoor air and exhausts 100% of return air, with no recirculation?
- Mixed-air system
- Once-through system (Correct answer)
- Recirculating system
- VAV system
Correct answer: Once-through system
A once-through (100% OA) system uses no return air recirculation, making it ideal for spaces like laboratories and hospitals with contamination concerns.
Question 6: In a multi-zone VAV system, the 'critical zone' is defined as the zone that:
- Has the highest cooling load
- Requires the highest fraction of outdoor air relative to supply air (Correct answer)
- Is farthest from the air handler
- Has the lowest thermostat setpoint
Correct answer: Requires the highest fraction of outdoor air relative to supply air
The critical zone is the zone with the highest outdoor air fraction (Zp), which drives the system-level outdoor air correction calculation.
Question 7: What ventilation design approach is most appropriate for a commercial kitchen exhaust hood?
- Dilution ventilation
- Local exhaust ventilation (Correct answer)
- Displacement ventilation
- Natural ventilation
Correct answer: Local exhaust ventilation
Local exhaust ventilation captures contaminants (grease, heat, combustion gases) at the source before they can disperse into the occupied space.
According to ASHRAE 62.1, what is the minimum outdoor air ventilation rate for an office space occupied at 5 people per 1,000 sq ft?