EETC Power Distribution 4 — Questions and Answers
Question 1: In power distribution, 'load factor' is defined as:
- Peak demand divided by total connected load
- Average load divided by peak demand over a given period (Correct answer)
- Energy consumed divided by system capacity
- Installed capacity divided by actual demand
Correct answer: Average load divided by peak demand over a given period
Load factor = average load / peak load over a period, indicating how efficiently the system capacity is utilized; a higher load factor means more uniform loading.
Question 2: What is the typical voltage range for 'primary distribution' circuits in the United States?
- 120 V to 240 V
- 480 V to 600 V
- 2.4 kV to 35 kV (Correct answer)
- 69 kV to 345 kV
Correct answer: 2.4 kV to 35 kV
Primary distribution operates at medium voltages, typically 2.4 kV to 35 kV (most commonly 4, 13.2, 13.8, or 25 kV), between the substation and distribution transformers.
Question 3: Which type of fault produces the highest fault current on a three-phase power system?
- Single-line-to-ground fault
- Line-to-line fault
- Double-line-to-ground fault
- Bolted three-phase fault (Correct answer)
Correct answer: Bolted three-phase fault
A bolted (zero impedance) three-phase symmetrical fault produces the highest fault current because all three phases are involved symmetrically with no fault impedance.
Question 4: A distribution recloser is set for a '2 fast, 2 delayed' sequence. What does this mean?
- It opens twice quickly, then twice after a time delay, and locks out after the 4th operation (Correct answer)
- It closes twice quickly, waits, then closes twice more before alarming
- It uses fast curves for phase faults and delayed curves for ground faults only
- It automatically resets after 2 fast operations if the fault clears
Correct answer: It opens twice quickly, then twice after a time delay, and locks out after the 4th operation
The '2 fast, 2 delayed' sequence means the recloser trips twice on a fast (instantaneous) curve, then twice on a slower time-delay curve before locking out after the fourth operation if the fault persists.
Question 5: Underground residential distribution (URD) cables most commonly use which insulation material?
- Paper-lead (PILC)
- Cross-linked polyethylene (XLPE) or EPR (Correct answer)
- Polyvinyl chloride (PVC)
- Rubber with cotton braid
Correct answer: Cross-linked polyethylene (XLPE) or EPR
Modern URD cables use XLPE or EPR insulation for their superior electrical properties, moisture resistance, and long service life compared to older materials.
Question 6: What is the primary cause of 'ferroresonance' in distribution systems?
- Excessive harmonic distortion from nonlinear loads
- Interaction between transformer magnetizing inductance and system capacitance under light or no-load conditions (Correct answer)
- Loose connections causing series impedance resonance
- Overcorrection of power factor by capacitor banks
Correct answer: Interaction between transformer magnetizing inductance and system capacitance under light or no-load conditions
Ferroresonance occurs when the nonlinear magnetizing inductance of an unloaded or lightly loaded transformer resonates with cable or capacitor charging capacitance, producing overvoltages.
Question 7: According to the NESC, what minimum vertical clearance above ground is required for a 13.8 kV overhead distribution conductor crossing a public roadway (open country)?
- 15.5 feet
- 18 feet (Correct answer)
- 22 feet
- 25 feet
Correct answer: 18 feet
The NESC requires 18 feet of vertical clearance for conductors operating at 15 kV or less crossing roads accessible to truck traffic in open country.
In power distribution, 'load factor' is defined as: