E2 Wiring Methods and Materials 3 — Questions and Answers
Question 1: Intermediate Metal Conduit (IMC) is permitted to be used as an equipment grounding conductor under which condition?
- Never — a separate EGC is always required
- Only with listed fittings installed per manufacturer instructions (Correct answer)
- Only indoors
- Only when bonded at both ends with locknuts
Correct answer: Only with listed fittings installed per manufacturer instructions
NEC 250.118(4) permits IMC to serve as an EGC when installed with listed fittings according to the manufacturer's instructions.
Question 2: What is the maximum trade size of Flexible Metal Conduit (FMC) that may be installed in lengths up to 6 feet without a separate equipment grounding conductor?
- 1/2 inch
- 3/4 inch (Correct answer)
- 1 inch
- 1-1/4 inch
Correct answer: 3/4 inch
Per NEC 250.118(5), FMC up to 3/4-inch trade size in lengths of 6 feet or less can serve as the EGC when listed fittings are used.
Question 3: In a commercial occupancy, Type AC cable (Armored Cable) must be secured within how many inches of every box or fitting?
- 6 inches
- 12 inches (Correct answer)
- 18 inches
- 24 inches
Correct answer: 12 inches
NEC 320.30(C) requires AC cable to be secured within 12 inches of every outlet box, junction box, or fitting.
Question 4: Which of the following conduit types is NOT permitted for use in cinder fill locations due to corrosion concerns?
- RMC with corrosion protection
- PVC Schedule 40
- EMT without corrosion protection (Correct answer)
- RTRC (fiberglass)
Correct answer: EMT without corrosion protection
NEC 358.10(B) prohibits EMT in cinder fill unless protected from the corrosive environment, as the thin wall is susceptible to attack.
Question 5: A run of rigid PVC conduit passes through a building expansion joint. The inspector should verify the presence of:
- A bonding jumper only
- An expansion coupling listed for the purpose (Correct answer)
- A flexible metallic coupling
- A union fitting with thread sealant
Correct answer: An expansion coupling listed for the purpose
NEC 352.44 requires an expansion fitting listed for PVC where the conduit crosses a structural expansion joint.
Question 6: What is the minimum bend radius for a 1-inch EMT conduit field bend to the inside of the bend?
- 2.5 inches
- 4 inches (Correct answer)
- 5 inches
- 8 inches
Correct answer: 4 inches
NEC Table 344.24 (referenced by 358.24) specifies a minimum 4-inch inside bend radius for 1-inch trade size conduit.
Question 7: Under the NEC, where must a conduit body (e.g., LB, LL, LR) be accessible?
- Only when containing splices
- Always, unless encased in concrete (Correct answer)
- It need not be accessible
- Only when installed outdoors
Correct answer: Always, unless encased in concrete
NEC 314.29 requires all junction and pull boxes, including conduit bodies, to remain accessible unless encased in concrete.
Intermediate Metal Conduit (IMC) is permitted to be used as an equipment grounding conductor under which condition?