E2 Overcurrent Protection Devices — Questions and Answers
Question 1: Per NEC 240.4(D), what is the maximum overcurrent protection permitted for 14 AWG copper conductors in a commercial installation?
- 20 amperes
- 25 amperes
- 15 amperes (Correct answer)
- 30 amperes
Correct answer: 15 amperes
NEC 240.4(D) limits overcurrent protection for 14 AWG copper conductors to a maximum of 15 amperes to prevent conductor damage from overheating.
Question 2: According to NEC 240.4(D), what is the maximum overcurrent protection allowed for 12 AWG copper conductors?
- 15 amperes
- 20 amperes (Correct answer)
- 25 amperes
- 30 amperes
Correct answer: 20 amperes
NEC 240.4(D) specifies that 12 AWG copper conductors shall not be protected by overcurrent devices rated more than 20 amperes.
Question 3: Under NEC 240.4(D), what is the maximum overcurrent protection for 10 AWG copper conductors?
- 20 amperes
- 25 amperes
- 35 amperes
- 30 amperes (Correct answer)
Correct answer: 30 amperes
NEC 240.4(D) limits overcurrent protection for 10 AWG copper conductors to a maximum of 30 amperes.
Question 4: Which of the following is a standard ampere rating for overcurrent devices per NEC 240.6(A)?
- 55 amperes
- 65 amperes
- 45 amperes (Correct answer)
- 85 amperes
Correct answer: 45 amperes
NEC 240.6(A) lists 45 amperes as a standard overcurrent device rating; 55, 65, and 85 amperes do not appear in the standard rating sequence.
Question 5: Per NEC 240.21, overcurrent protection for conductors shall generally be provided at:
- The load end of the conductor run
- The point where the conductor receives its supply (Correct answer)
- The midpoint of long conductor runs
- The main service disconnect only
Correct answer: The point where the conductor receives its supply
NEC 240.21 requires overcurrent protection at the point where the conductor receives its supply from the feeder or service, protecting the entire conductor run.
Question 6: Under NEC 240.21(B)(1), what is the maximum length of a feeder tap conductor that does not require overcurrent protection at the tap point, provided it is enclosed in a raceway and meets all other conditions?
- 10 feet (Correct answer)
- 15 feet
- 25 feet
- 50 feet
Correct answer: 10 feet
NEC 240.21(B)(1) permits unprotected tap conductors up to 10 feet when all specified conditions are met, including enclosure in a raceway and termination in a single circuit breaker or set of fuses.
Question 7: Per NEC 240.21(B)(2), what is the maximum length for a feeder tap conductor whose ampacity is not less than 1/3 the rating of the overcurrent device protecting the feeder?
- 10 feet
- 15 feet
- 25 feet (Correct answer)
- 50 feet
Correct answer: 25 feet
NEC 240.21(B)(2) allows tap conductors up to 25 feet when their ampacity is at least 1/3 the feeder's OCPD rating and conditions including physical protection are satisfied.
Question 8: Per NEC 240.4(B), using the next higher standard overcurrent device rating above the conductor's calculated ampacity is NOT permitted when the conductor ampacity exceeds:
- 200 amperes
- 400 amperes
- 600 amperes
- 800 amperes (Correct answer)
Correct answer: 800 amperes
NEC 240.4(B) prohibits rounding up to the next higher standard overcurrent device rating when the conductor ampacity exceeds 800 amperes; the OCPD must not exceed the conductor's ampacity.
Question 9: According to NEC 240.85, a circuit breaker with a straight voltage rating (e.g., 480V) is suitable for use in:
- Solidly grounded systems only
- Ungrounded systems only
- Either solidly grounded or ungrounded systems at that voltage (Correct answer)
- Resistance-grounded systems only
Correct answer: Either solidly grounded or ungrounded systems at that voltage
NEC 240.85 states that a straight voltage-rated circuit breaker may be applied in either solidly grounded or ungrounded systems at that voltage level.
Question 10: Per NEC Article 100, a current-limiting overcurrent protective device is defined as one that:
- Limits current to the conductor's rated ampacity under all fault conditions
- Reduces the let-through current to a value less than the available fault current (Correct answer)
- Prevents any fault current from reaching the load side
- Limits the duration of any overcurrent to exactly one half-cycle
Correct answer: Reduces the let-through current to a value less than the available fault current
A current-limiting OCPD reduces the peak let-through current to a magnitude less than the maximum available fault current, reducing thermal and magnetic stress on protected equipment.
Question 11: Per NEC 240.24(E), in a multifamily dwelling, overcurrent devices protecting a specific dwelling unit shall be accessible to:
- The building owner or property manager only
- All tenants in the building equally
- The occupant of the dwelling unit that is protected (Correct answer)
- Only qualified electrical personnel
Correct answer: The occupant of the dwelling unit that is protected
NEC 240.24(E) requires that overcurrent devices protecting a dwelling unit be accessible to the occupant of that specific unit, allowing them to reset breakers without entering another tenant's space.
Question 12: Under NEC 110.9, equipment intended to interrupt current at fault levels must have an interrupting rating:
- Of at least 10,000 amperes symmetrical RMS
- Of at least 22,000 amperes symmetrical RMS
- Sufficient for the nominal circuit voltage and the current available at its line terminals (Correct answer)
- Marked on the nameplate with a minimum of 5,000 AIC
Correct answer: Sufficient for the nominal circuit voltage and the current available at its line terminals
NEC 110.9 requires that equipment intended to interrupt fault current have an interrupting rating sufficient for the nominal circuit voltage and the available fault current at its terminals.
Question 13: Per NEC 230.95(A), what is the maximum ground-fault trip current setting permitted for ground-fault protection of equipment (GFPE) on service equipment?
- 400 amperes
- 800 amperes
- 1200 amperes (Correct answer)
- 1600 amperes
Correct answer: 1200 amperes
NEC 230.95(A) limits the maximum GFPE trip setting to 1200 amperes to ensure the device will operate before a destructive arcing ground fault causes catastrophic damage to switchgear or switchboards.
Question 14: Per NEC 110.15 and 230.56, the high-leg conductor of a 4-wire, 3-phase delta system shall be identified by the color:
- Red
- Blue
- Yellow
- Orange (Correct answer)
Correct answer: Orange
NEC 110.15 and 230.56 require the high-leg conductor (the phase with the highest voltage to ground, approximately 208V) in a 4-wire delta system to be identified with orange color.