DCI Cable Installation Techniques 3 — Questions and Answers
Question 1: What is the primary purpose of leaving a service loop when terminating cable in a telecommunications room?
- To act as extra shielding
- To allow re-termination if a connection fails (Correct answer)
- To reduce crosstalk between cables
- To satisfy NEC bonding requirements
Correct answer: To allow re-termination if a connection fails
A service loop (typically 3–10 feet) provides enough extra cable length to re-terminate the end if a punch-down is damaged or needs to be moved.
Question 2: When installing horizontal cable, what is the maximum distance allowed from the work area outlet to the telecommunications room under TIA-568?
- 50 meters (164 ft)
- 90 meters (295 ft) (Correct answer)
- 100 meters (328 ft)
- 150 meters (492 ft)
Correct answer: 90 meters (295 ft)
TIA-568 limits horizontal cable (permanent link) to 90 meters to leave 10 meters for equipment and patch cords in the total 100-meter channel.
Question 3: Which wiring standard pinout is most commonly required for new commercial structured cabling installations in the US?
- T568A
- T568B (Correct answer)
- USOC
- EIA-310
Correct answer: T568B
T568B is the most commonly used pinout for commercial installations in the US, though T568A is specified for government and some enterprise environments.
Question 4: A cable installer notices the cable jacket is slightly crushed after installation through a conduit. What is the best course of action?
- Test the cable and replace only if it fails
- Remove and replace the cable regardless of test results (Correct answer)
- Apply electrical tape over the crush point
- Increase transmit power to compensate
Correct answer: Remove and replace the cable regardless of test results
A crushed jacket can deform internal pairs and cause latent failures; the cable should be replaced to ensure long-term reliability even if it initially passes testing.
Question 5: Which type of conduit fill table should be referenced when determining how many cables can be pulled through a 1-inch EMT conduit?
- NEC Article 300 fill tables
- NEC Chapter 9 conduit fill tables (Correct answer)
- TIA-569 pathway fill guidelines
- ANSI/NEMA VE 2 tables
Correct answer: NEC Chapter 9 conduit fill tables
NEC Chapter 9 tables provide conduit fill calculations for conductors and cables, specifying maximum fill percentages for different conduit types and sizes.
Question 6: What installation practice minimizes alien crosstalk (AXT) when running multiple Cat 6A cables in close proximity?
- Tightly bundling cables together
- Maintaining random, loose cable spacing without bundling (Correct answer)
- Using solid-conductor cable only
- Installing all cables in the same orientation
Correct answer: Maintaining random, loose cable spacing without bundling
Loose, random spacing without tight bundling prevents the consistent parallel alignment that maximizes alien crosstalk coupling between adjacent cables.
Question 7: When installing a cable through a suspended ceiling, which pathway guideline must the installer follow regarding cable support?
- Cables may rest freely on ceiling tiles
- Cables must be supported every 4–5 feet and not laid on ceiling tiles (Correct answer)
- Cables must be enclosed in metallic conduit at all times
- Only plenum-rated cable can run above suspended ceilings
Correct answer: Cables must be supported every 4–5 feet and not laid on ceiling tiles
TIA-569 and NEC require cables above suspended ceilings to be supported at intervals not exceeding 4–5 feet and must not rest on the ceiling tiles.
What is the primary purpose of leaving a service loop when terminating cable in a telecommunications room?