A plant has a measured power factor of 0.72 lagging at 480V, 3-phase, drawing 800 kW. How much reactive power (kVAR) must be added to correct the power factor to 0.95 lagging?
-
A
Approximately 233 kVAR
-
B
Approximately 421 kVAR
-
C
Approximately 577 kVAR
-
D
Approximately 800 kVAR