CME Electrical Codes & Standards 2 — Questions and Answers
Question 1: Under NEC Article 230, what is the maximum number of service disconnects permitted for a single-occupancy building?
- Two
- Four
- Six (Correct answer)
- Eight
Correct answer: Six
NEC 230.71 allows a maximum of six disconnecting means for a single set of service-entrance conductors.
Question 2: Which NEC article governs the installation of transformers with a primary voltage over 600V?
- Article 408
- Article 450 (Correct answer)
- Article 480
- Article 490
Correct answer: Article 450
NEC Article 450 covers transformers and transformer vaults, including those rated over 600V.
Question 3: What does the NEC require for overcurrent protection of a 480V, 3-phase, 100 kVA transformer with a secondary of 208Y/120V?
- Primary protection only is always sufficient
- Secondary overcurrent protection must be within 25 feet of the transformer
- Primary protection set at 125% of rated current satisfies the NEC for most cases (Correct answer)
- No overcurrent protection is required for transformers under 112.5 kVA
Correct answer: Primary protection set at 125% of rated current satisfies the NEC for most cases
Per NEC 450.3, primary overcurrent protection set no more than 125% of rated primary current is the standard requirement for most transformers.
Question 4: NEC 310.15 ampacity tables are based on an ambient temperature of how many degrees Celsius?
- 25°C
- 30°C (Correct answer)
- 40°C
- 60°C
Correct answer: 30°C
NEC ampacity tables in 310.15 are based on a 30°C (86°F) ambient temperature unless otherwise noted.
Question 5: According to NEC 250.122, if a feeder circuit's overcurrent device is increased in size to handle a larger load, what must also be increased?
- The neutral conductor
- The equipment grounding conductor (Correct answer)
- The service entrance cable
- The conduit fill percentage
Correct answer: The equipment grounding conductor
NEC 250.122(B) requires the equipment grounding conductor to be proportionally increased when the OCPD is upsized.
Question 6: Under NFPA 70E, what arc flash PPE category requires a minimum arc rating of 40 cal/cm²?
- Category 1
- Category 2
- Category 3
- Category 4 (Correct answer)
Correct answer: Category 4
NFPA 70E Table 130.5(G) assigns PPE Category 4 a minimum arc rating of 40 cal/cm².
Question 7: Which NEC section defines the requirements for working clearances in front of electrical equipment operating at 600V or less?
- NEC 110.26 (Correct answer)
- NEC 230.70
- NEC 408.18
- NEC 240.24
Correct answer: NEC 110.26
NEC 110.26 specifies minimum working clearances, dedicated space, and headroom requirements for equipment up to 1000V.
Under NEC Article 230, what is the maximum number of service disconnects permitted for a single-occupancy building?