CLD Electrical Systems & Lighting Control 5 — Questions and Answers
Question 1: A lighting designer is coordinating with an electrical engineer on harmonic distortion. Which type of luminaire driver is most likely to introduce significant harmonics into the distribution system?
- Magnetic ballast with power factor correction capacitor
- High-quality LED driver with active power factor correction (PFC)
- LED driver with no PFC and high total harmonic distortion (THD) (Correct answer)
- Incandescent lamp on a resistive circuit
Correct answer: LED driver with no PFC and high total harmonic distortion (THD)
LED drivers without active PFC can exhibit high THD (>20%), injecting harmonic currents that overheat neutrals and transformers in a distribution system.
Question 2: Which ASHRAE 90.1 control requirement mandates automatic shutoff of lighting in most commercial spaces?
- Daylighting controls in all perimeter zones
- Occupant sensor or time-of-day schedule shutoff for interior spaces (Correct answer)
- Demand response interface at the main panel
- Manual-on switching for all exterior luminaires
Correct answer: Occupant sensor or time-of-day schedule shutoff for interior spaces
ASHRAE 90.1 requires automatic shutoff controls (occupancy sensors or scheduling) for interior lighting in most commercial occupancy types.
Question 3: In a DMX512 lighting control system, what is the maximum number of individual channels (slots) addressable on one universe?
- 128
- 256
- 512 (Correct answer)
- 1024
Correct answer: 512
A single DMX512 universe carries exactly 512 channels (slots), each carrying an 8-bit value from 0–255.
Question 4: A lighting control specification calls for 'bi-level switching' in a warehouse. What does this control strategy accomplish?
- It switches the space between full ON and full OFF only
- It allows the space to operate at two preset levels (e.g., 100% occupied, 30% unoccupied) rather than just on or off (Correct answer)
- It independently controls warm and cool LED channels
- It divides the space into two separately switched circuits
Correct answer: It allows the space to operate at two preset levels (e.g., 100% occupied, 30% unoccupied) rather than just on or off
Bi-level switching provides two pre-set light levels — typically full output when occupied and a reduced level during low-occupancy periods — satisfying energy codes with a simple relay-based approach.
Question 5: What is the purpose of a 'neutral conductor' in a modern electronic dimmer installation?
- It provides the ground fault return path only
- It supplies the low-voltage power needed by the dimmer's electronics without drawing it through the load (Correct answer)
- It carries the dimming signal to the driver
- It is not required for electronic dimmers
Correct answer: It supplies the low-voltage power needed by the dimmer's electronics without drawing it through the load
Modern electronic dimmers require a neutral to power their internal circuitry, preventing flicker or buzzing that occurs when the dimmer steals power through the load at low dim levels.
Question 6: A photosensor used for daylighting control is described as 'closed-loop.' What does this mean operationally?
- The sensor measures only daylight without regard to electric light contribution
- The sensor measures the combined daylight and electric light at the workplane and adjusts electric light to maintain a target illuminance (Correct answer)
- The sensor shuts off all electric light when daylight exceeds a threshold
- The sensor only responds to changes in outdoor illuminance levels
Correct answer: The sensor measures the combined daylight and electric light at the workplane and adjusts electric light to maintain a target illuminance
A closed-loop photosensor measures total light at the work surface (daylight + electric) and continuously dims or brightens electric lighting to maintain a set point regardless of external conditions.
Question 7: Which NEC article governs the installation of lighting track and specifies that it must not be used in certain hazardous locations or where subject to physical damage?
- Article 410 (Correct answer)
- Article 490
- Article 517
- Article 600
Correct answer: Article 410
NEC Article 410 covers luminaires, lampholders, and lighting track, including prohibitions on track use in wet or damp locations, hazardous locations, and areas subject to physical damage.
A lighting designer is coordinating with an electrical engineer on harmonic distortion.