CHI Electrical Systems Inspection 3 — Questions and Answers
Question 1: What is the purpose of an arc-fault circuit interrupter (AFCI) breaker?
- To protect against ground faults in wet locations
- To detect dangerous arcing conditions that can cause fires (Correct answer)
- To limit current draw to 15 amps on all circuits
- To replace GFCI protection in bathrooms
Correct answer: To detect dangerous arcing conditions that can cause fires
AFCI breakers detect the electrical signature of arc faults—unintended arcing in wiring—and trip the circuit to prevent fires.
Question 2: A home inspector finds a 240-volt dryer circuit protected by a 60-amp breaker with 10 AWG wire. What is the deficiency?
- The breaker is too small for a dryer circuit
- The wire is undersized for a 60-amp overcurrent device (Correct answer)
- 240-volt dryers require GFCI protection
- Dryer circuits must use aluminum wiring only
Correct answer: The wire is undersized for a 60-amp overcurrent device
10 AWG copper wire is rated for 30 amps maximum; a 60-amp breaker provides inadequate overcurrent protection for this conductor.
Question 3: Which location requires GFCI protection for receptacles under current NEC requirements?
- Bedroom circuits in homes built after 2000
- All 125-volt receptacles within 6 feet of a kitchen sink (Correct answer)
- Dedicated circuits for refrigerators
- Living room receptacles on exterior walls
Correct answer: All 125-volt receptacles within 6 feet of a kitchen sink
The NEC requires GFCI protection for receptacles within 6 feet of kitchen sinks to protect against shock from water contact.
Question 4: A home inspector observes open knockouts in the bottom of an electrical panel. What is the primary safety concern?
- Water can enter and corrode bus bars
- Rodents or pests can enter and damage wiring
- Both pest intrusion and loss of the panel's required enclosure integrity (Correct answer)
- The panel cannot be rated as weatherproof
Correct answer: Both pest intrusion and loss of the panel's required enclosure integrity
Open knockouts compromise the panel's enclosure, allowing pest entry and contact with live conductors, and creating a shock and fire hazard.
Question 5: What does the inspector look for to confirm that a 3-wire (black, white, red) multi-wire branch circuit is wired correctly?
- All three conductors should be on the same phase leg
- The two hot conductors should be on opposite phase legs with a shared neutral (Correct answer)
- The white conductor must be re-identified with red tape
- A dedicated 30-amp breaker protects all three wires
Correct answer: The two hot conductors should be on opposite phase legs with a shared neutral
A multi-wire branch circuit requires the two hots to be on opposite legs so the shared neutral carries only the imbalance current, not a doubled load.
Question 6: In which situation is it acceptable for a home inspector to find a non-metallic sheathed cable (Romex) stapled too tightly?
- When the cable runs through a conduit
- It is never acceptable — over-stapling can damage insulation and conductors (Correct answer)
- Only when the cable is 12 AWG or larger
- When the cable is protected by a 20-amp breaker
Correct answer: It is never acceptable — over-stapling can damage insulation and conductors
Over-stapling compresses the cable sheathing and conductor insulation, which can damage wiring integrity and create a potential fault hazard.
Question 7: A home inspector finds a junction box hidden inside a wall with no accessible cover plate. What should be reported?
- The box is acceptable if the connections inside are made with wire nuts
- Junction boxes must remain accessible and have a cover plate per NEC (Correct answer)
- The box is fine if the wall material is non-combustible
- Only outdoor junction boxes require cover plates
Correct answer: Junction boxes must remain accessible and have a cover plate per NEC
The NEC requires all junction boxes to be accessible and covered to allow inspection and prevent contact with live connections.
What is the purpose of an arc-fault circuit interrupter (AFCI) breaker?