CFPS Water-Based Suppression Systems 2 — Questions and Answers
Question 1: Per NFPA 13, what is the maximum allowable coverage area per sprinkler head in an Ordinary Hazard occupancy?
- 100 sq ft
- 130 sq ft (Correct answer)
- 168 sq ft
- 225 sq ft
Correct answer: 130 sq ft
NFPA 13 limits Ordinary Hazard occupancy sprinkler coverage to 130 sq ft per head due to the higher fire potential compared to Light Hazard.
Question 2: What is the primary function of a water motor gong (mechanical alarm) on a wet pipe sprinkler system?
- Boost water pressure to remote sprinklers
- Provide a local audible alarm driven by water flow through the alarm valve (Correct answer)
- Automatically notify the fire department dispatch center
- Control the main system shutoff valve position
Correct answer: Provide a local audible alarm driven by water flow through the alarm valve
A water motor gong is driven by water flowing through a restricted orifice at the alarm valve, producing a loud local audible alarm without electricity.
Question 3: Which NFPA standard governs the installation of standpipe and hose systems?
- NFPA 13
- NFPA 14 (Correct answer)
- NFPA 15
- NFPA 25
Correct answer: NFPA 14
NFPA 14, Standard for the Installation of Standpipe and Hose Systems, covers design, installation, and maintenance requirements for these systems.
Question 4: Per NFPA 20, what performance criterion must a listed fire pump meet at churn (no-flow, shutoff) condition?
- Pressure must equal exactly 100% of rated pressure
- Pressure must not exceed 140% of rated pressure (Correct answer)
- Pump must deliver 150% of rated flow capacity
- Pressure must be at least 65% of rated pressure
Correct answer: Pressure must not exceed 140% of rated pressure
NFPA 20 requires that a fire pump's pressure at churn (shutoff) shall not exceed 140% of its rated pressure to prevent overpressurizing the system.
Question 5: What substance fills the distribution piping between the dry pipe valve and the sprinkler heads in a dry pipe system under normal (standby) conditions?
- Pressurized air or nitrogen (Correct answer)
- Antifreeze solution
- Foam concentrate pre-mix
- Inert gas at atmospheric pressure
Correct answer: Pressurized air or nitrogen
Dry pipe systems maintain pressurized air or nitrogen in the distribution piping to hold the dry pipe valve clapper closed until a sprinkler head opens.
Question 6: Which sprinkler system type is most appropriate for an unheated walk-in cold storage freezer room?
- Wet pipe system
- Dry pipe system (Correct answer)
- Pre-action (single interlock) system
- Deluge system
Correct answer: Dry pipe system
Dry pipe systems are used where piping may be subject to freezing because the distribution piping contains pressurized air, not water, during standby.
Question 7: Per NFPA 13, what is the minimum residual pressure required at the hydraulically most remote sprinkler during system discharge?
- 7 psi (Correct answer)
- 15 psi
- 20 psi
- 25 psi
Correct answer: 7 psi
NFPA 13 requires a minimum of 7 psi at the most remote sprinkler to ensure adequate water distribution from the deflector.
Per NFPA 13, what is the maximum allowable coverage area per sprinkler head in an Ordinary Hazard occupancy?