Certified Energy Auditor Certification HVAC Systems and Controls 2 — Questions and Answers
Question 1: What is the primary purpose of an economizer cycle in an HVAC system?
- Reduce refrigerant charge
- Use outdoor air for free cooling when conditions allow (Correct answer)
- Increase compressor efficiency
- Preheat supply air in winter
Correct answer: Use outdoor air for free cooling when conditions allow
An economizer uses outdoor air for cooling when outside conditions are favorable, reducing or eliminating mechanical cooling energy.
Question 2: A chiller's coefficient of performance (COP) is defined as:
- Cooling output divided by electrical input (Correct answer)
- Electrical input divided by heat rejected
- Heating output divided by fuel input
- Total BTU capacity divided by tonnage
Correct answer: Cooling output divided by electrical input
COP equals the useful cooling energy output divided by the electrical energy consumed by the chiller.
Question 3: Which control strategy staggers the start times of multiple HVAC units to reduce peak electrical demand?
- Demand-controlled ventilation
- Optimal start control
- Load shedding / demand limiting (Correct answer)
- Night setback
Correct answer: Load shedding / demand limiting
Load shedding or demand limiting staggers equipment startups to avoid simultaneous peak demand spikes on the electric bill.
Question 4: What does a higher SEER rating indicate for a cooling system?
- Greater refrigerant capacity
- Higher seasonal energy efficiency (Correct answer)
- Faster cooling speed
- Louder compressor operation
Correct answer: Higher seasonal energy efficiency
SEER (Seasonal Energy Efficiency Ratio) measures cooling output over a season divided by electrical energy consumed; higher values mean better efficiency.
Question 5: In a variable air volume (VAV) system, reducing airflow to 50% of design typically reduces fan energy by approximately:
- 50%
- 75%
- 87.5% (Correct answer)
- 25%
Correct answer: 87.5%
Fan power follows the cube law: reducing airflow to 50% reduces power to (0.5)³ = 12.5% of full load, an 87.5% reduction.
Question 6: Which type of heat exchanger recovers energy between exhaust and supply air streams in an air handling unit?
- Shell-and-tube condenser
- Energy recovery ventilator (ERV) (Correct answer)
- Cooling coil
- Steam humidifier
Correct answer: Energy recovery ventilator (ERV)
An ERV transfers both sensible heat and latent moisture between exhaust and incoming outdoor air, reducing conditioning loads.
Question 7: What is the recommended minimum MERV rating for filters in commercial HVAC systems to balance IAQ and energy efficiency?
- MERV 1–4
- MERV 13–16
- MERV 6–8 (Correct answer)
- MERV 17–20
Correct answer: MERV 6–8
MERV 6–8 filters provide reasonable IAQ protection without excessive pressure drop that would increase fan energy consumption.
What is the primary purpose of an economizer cycle in an HVAC system?