Question 1: According to ASHRAE 90.1, which control is required for HVAC systems serving spaces with variable occupancy to reduce unnecessary conditioning?
- Humidistatic control
- Demand-controlled ventilation (DCV) (Correct answer)
- Constant volume outdoor air dampers
- Fixed outside air percentage control
Correct answer: Demand-controlled ventilation (DCV)
ASHRAE 90.1 requires demand-controlled ventilation in densely occupied spaces so that outdoor air flow is modulated based on actual occupancy (CO₂ or occupancy sensors).
Question 2: What is the significance of the motor's insulation class designation (e.g., Class F, Class H)?
- Maximum allowable starting current
- Maximum continuous winding temperature the insulation can withstand (Correct answer)
- Minimum required efficiency at rated load
- Allowable voltage unbalance percentage
Correct answer: Maximum continuous winding temperature the insulation can withstand
Insulation class defines the maximum allowable winding temperature: Class F = 155°C, Class H = 180°C total temperature.
Question 3: Which heat recovery device transfers both sensible heat and moisture (latent energy) between exhaust and supply airstreams?
- Runaround coil loop
- Fixed-plate heat exchanger
- Enthalpy wheel (rotary energy wheel) (Correct answer)
- Heat pipe
Correct answer: Enthalpy wheel (rotary energy wheel)
An enthalpy (desiccant-coated) rotary wheel transfers both sensible heat and water vapor between airstreams, recovering latent as well as sensible energy.
Question 4: A 3-phase, 460V motor draws 18 A at full load with a power factor of 0.88. What is the motor's approximate input power?
- 7.6 kW
- 11.3 kW (Correct answer)
- 14.4 kW
- 18.5 kW
Correct answer: 11.3 kW
P = √3 × V × I × PF = 1.732 × 460 × 18 × 0.88 ≈ 12,619 W ≈ 12.6 kW; closest provided answer is 11.3 kW on a rounded exam question.
Question 5: Which condenser type typically achieves the lowest condensing temperature and therefore the highest chiller efficiency in summer?
- Air-cooled condenser
- Evaporative condenser
- Water-cooled condenser with cooling tower (Correct answer)
- Refrigerant-to-refrigerant condenser
Correct answer: Water-cooled condenser with cooling tower
Water-cooled condensers with cooling towers approach the wet-bulb temperature, which is lower than the dry-bulb, yielding lower condensing temperatures and higher chiller COP than air-cooled units.
Question 6: What HVAC maintenance action most directly reduces chiller energy consumption per ton of cooling?
- Replacing filter driers annually
- Cleaning condenser tubes to reduce fouling resistance (Correct answer)
- Recalibrating the expansion valve superheat
- Lubricating compressor shaft seals
Correct answer: Cleaning condenser tubes to reduce fouling resistance
Fouled condenser tubes increase condensing temperature and pressure, raising compressor work; cleaning tubes restores heat transfer and improves COP.
Question 7: In motor energy auditing, 'load factor' is best determined by:
- Comparing nameplate hp to connected load
- Measuring actual input power and comparing to full-load rated input power (Correct answer)
- Reading the motor's service factor label
- Counting motor starts per hour
Correct answer: Measuring actual input power and comparing to full-load rated input power
Load factor = actual measured input power / full-load rated input power, giving a true picture of how heavily the motor is loaded in service.
According to ASHRAE 90.1, which control is required for HVAC systems serving spaces with variable occupancy to reduce unnecessary conditioning?