During a commercial inspection, an inspector finds that the electrical contractor installed Class CC fuses in a motor branch circuit that requires branch circuit short-circuit and ground-fault protection. The motor FLA is 40A. What is the maximum permitted fuse rating using a Class CC dual-element time-delay fuse per NEC 430.52?
-
A
175% of motor FLA = 70A maximum for dual-element time-delay fuses
-
B
125% of motor FLA = 50A
-
C
300% of motor FLA = 120A
-
D
100% of motor FLA = 40A