CEI Plan Review & Permit Processing 2 — Questions and Answers
Question 1: When reviewing electrical plans for a commercial building, which document takes precedence if the drawings conflict with the specifications?
- Specifications always govern over drawings
- Drawings always govern over specifications
- The more stringent requirement governs (Correct answer)
- The AHJ determines which document governs on a case-by-case basis
Correct answer: The more stringent requirement governs
When conflicts exist between drawings and specifications, the more stringent requirement governs to ensure code compliance and safety.
Question 2: A permit applicant submits plans for a 480V motor control center. Which NEC article primarily governs the review of this equipment?
- Article 430 (Correct answer)
- Article 480
- Article 408
- Article 445
Correct answer: Article 430
NEC Article 430 governs motors, motor circuits, and controllers, making it the primary reference for motor control center plan review.
Question 3: During plan review, an inspector notices that the submitted load calculations show a 200A residential service. The calculated load is 195A. What is the correct determination?
- Reject — service must be upsized to 225A
- Approve — 200A service is adequate since it exceeds calculated load (Correct answer)
- Reject — residential services must be 400A minimum
- Approve only if arc fault protection is included on all circuits
Correct answer: Approve — 200A service is adequate since it exceeds calculated load
A 200A service is adequate because it exceeds the 195A calculated load per NEC 220 demand calculations.
Question 4: What is the primary purpose of requiring a permit for electrical work?
- To generate municipal revenue
- To ensure work is inspected for code compliance and public safety (Correct answer)
- To track contractor licensing
- To document property improvements for tax assessment
Correct answer: To ensure work is inspected for code compliance and public safety
Permits exist to ensure electrical work is inspected for compliance with adopted codes, protecting public health and safety.
Question 5: An electrical plan shows conduit routed through a fire-rated wall without a listed fire stop. What action should the plan reviewer take?
- Approve with a note to the contractor
- Issue a correction requiring fire-stop specification before approval (Correct answer)
- Approve because the NEC does not address fire stopping
- Defer the issue to the fire marshal only
Correct answer: Issue a correction requiring fire-stop specification before approval
The reviewer must require a correction to specify listed fire-stopping materials before approving plans with penetrations through fire-rated assemblies.
Question 6: Which of the following best describes a 'deferred submittal' in the context of electrical plan review?
- Plans submitted after the permit is issued for subsequent review and approval (Correct answer)
- Plans that are rejected and must be resubmitted
- Plans submitted by a subcontractor instead of the engineer of record
- A permit application that is placed on hold pending fee payment
Correct answer: Plans submitted after the permit is issued for subsequent review and approval
A deferred submittal involves certain design elements submitted after initial permit issuance, reviewed and approved before that portion of work begins.
Question 7: A plan reviewer finds that the submitted riser diagram shows feeders without indicating wire size or conduit type. What is the correct course of action?
- Approve and note deficiency in the inspection file
- Issue incomplete submission notice and request corrected documents (Correct answer)
- Calculate the wire size independently and approve
- Approve if the general notes reference the NEC
Correct answer: Issue incomplete submission notice and request corrected documents
Incomplete submissions lacking required information such as conductor and conduit sizing must be returned for correction before approval.
When reviewing electrical plans for a commercial building, which document takes precedence if the drawings conflict with the specifications?