CEA Wiring Methods and Materials 3 — Questions and Answers
Question 1: Intermediate metal conduit (IMC) has walls that are thinner than rigid metal conduit (RMC). Which statement about IMC is correct?
- IMC cannot be threaded
- IMC uses the same fittings as RMC
- IMC is approved for all the same applications as RMC (Correct answer)
- IMC requires special couplings not interchangeable with RMC
Correct answer: IMC is approved for all the same applications as RMC
NEC 342 lists IMC as suitable for all environments where RMC is permitted, including concrete encasement and direct burial.
Question 2: What is the required minimum burial depth for rigid metal conduit (RMC) installed under a residential driveway?
- 6 inches
- 12 inches (Correct answer)
- 18 inches
- 24 inches
Correct answer: 12 inches
NEC Table 300.5 requires RMC and IMC to be buried at least 6 inches under residential driveways.
Question 3: Type UF cable installed as a direct-buried feeder to an outbuilding must be buried at least how deep under a one-family dwelling's yard?
- 6 inches
- 12 inches
- 18 inches (Correct answer)
- 24 inches
Correct answer: 18 inches
NEC Table 300.5 requires direct-buried Type UF cable to be at least 24 inches deep, reduced to 18 inches under a dwelling's yard in some applications; the standard general requirement is 24 inches.
Question 4: Which fitting must be used where electrical metallic tubing (EMT) enters a box to protect conductors from the sharp edge of the tubing?
- Locknut
- Bushing
- Connector with insulating throat or separate bushing (Correct answer)
- Set-screw coupling
Correct answer: Connector with insulating throat or separate bushing
NEC 358.46 requires fittings that protect conductors at EMT terminations, typically connectors with an insulating throat.
Question 5: Non-metallic sheathed cable (NM-B) is permitted to be installed in which of the following locations?
- Wet or damp locations
- Embedded in masonry
- Dry locations in wood-frame residential structures (Correct answer)
- Commercial kitchens
Correct answer: Dry locations in wood-frame residential structures
NM-B cable is restricted to dry locations and is most commonly used in wood-frame, one- and two-family dwellings per NEC 334.10.
Question 6: When installing service-entrance (SE) cable above a roof with a slope of less than 4 inches in 12 inches, the cable must maintain at least how much clearance above the roof?
- 6 inches
- 8 inches
- 18 inches (Correct answer)
- 36 inches
Correct answer: 18 inches
NEC 230.24(A) requires SE conductors to maintain 18 inches clearance over flat or low-slope roofs, with exceptions for steep-slope roofs.
Question 7: Liquidtight flexible metal conduit (LFMC) is required when used in outdoor wet locations primarily because it:
- Provides a higher ampacity than LFNC
- Has a PVC jacket that prevents moisture ingress (Correct answer)
- Is rated for higher voltage than standard FMC
- Can be buried without further protection
Correct answer: Has a PVC jacket that prevents moisture ingress
LFMC's outer PVC jacket seals out moisture and liquids, making it suitable for wet and outdoor locations unlike plain FMC.