CAT Alarm Technician Wiring & Circuits 3 — Questions and Answers
Question 1: A normally closed (NC) contact connected across a zone loop WITHOUT an end-of-line resistor would cause the panel to:
- Show a normal supervisory state
- Report a trouble condition (Correct answer)
- Report an alarm condition
- Report a ground fault
Correct answer: Report a trouble condition
Without the EOL resistor the panel cannot distinguish between a resting NC contact and a shorted wire, triggering a trouble indication.
Question 2: What is the MAXIMUM recommended total loop resistance for most conventional initiating device circuits?
- 10 ohms
- 25 ohms
- 50 ohms (Correct answer)
- 100 ohms
Correct answer: 50 ohms
Most panels specify a maximum zone loop resistance of 50 ohms; exceeding this can prevent reliable alarm detection.
Question 3: Which cable listing is required for alarm wiring run in a plenum air-handling space?
- CM (Communications)
- CL2 (Class 2 general)
- FPL (Fire Power Limited)
- FPLP (Fire Power Limited Plenum) (Correct answer)
Correct answer: FPLP (Fire Power Limited Plenum)
FPLP-rated cable has low-smoke, low-flame characteristics required for installation in air-handling plenums per NFPA 72 and NEC Article 760.
Question 4: When daisy-chaining motion detectors on a single zone, the technician should wire the alarm outputs in:
- Parallel (NO contacts in parallel)
- Series (NC contacts in series) (Correct answer)
- A star topology with individual home runs
- Alternating NO and NC configuration
Correct answer: Series (NC contacts in series)
NC contacts wired in series form a continuous loop; any detector opening the contact breaks the loop and triggers an alarm.
Question 5: The purpose of a double-end-of-line (DEOL) resistor configuration is to:
- Increase zone current draw
- Allow the panel to distinguish between an open, a short, and a normal alarm (Correct answer)
- Replace Class A return wiring
- Reduce wire resistance
Correct answer: Allow the panel to distinguish between an open, a short, and a normal alarm
DEOL uses two resistors of different values so the panel can identify three distinct states: normal, alarm (contact change), open, and short.
Question 6: A technician is pulling wire through an existing metallic conduit. Which wiring consideration is MOST important?
- Ensuring the conduit is PVC-coated
- Verifying fill capacity (conduit fill percentage) is not exceeded (Correct answer)
- Using only solid conductors
- Grounding the conduit to the detector housing
Correct answer: Verifying fill capacity (conduit fill percentage) is not exceeded
NEC Article 760 and conduit fill tables limit how many conductors can share a conduit to prevent heat buildup and installation damage.
Question 7: Stranded wire is preferred over solid wire for alarm installations primarily because it:
- Has lower resistance per foot
- Is easier to route through conduit and more flexible in terminal connections (Correct answer)
- Carries higher voltage ratings
- Has a thicker insulation jacket
Correct answer: Is easier to route through conduit and more flexible in terminal connections
Stranded wire's flexibility reduces insulation cracking during installation and makes reliable terminations easier at device terminals.
A normally closed (NC) contact connected across a zone loop WITHOUT an end-of-line resistor would cause the panel to: