CAT Alarm Technician Compliance Standards 3 — Questions and Answers
Question 1: Which NFPA standard specifically addresses the installation and testing of fire alarm and signaling systems?
- NFPA 25
- NFPA 70
- NFPA 72 (Correct answer)
- NFPA 101
Correct answer: NFPA 72
NFPA 72, the National Fire Alarm and Signaling Code, specifically covers installation, testing, and maintenance of fire alarm systems.
Question 2: What is the purpose of a Certificate of Completion required by NFPA 72 after a fire alarm system installation?
- It authorizes the AHJ to collect fees
- It documents that the system was installed and tested per the applicable standard (Correct answer)
- It replaces the need for permits
- It certifies the building owner's training
Correct answer: It documents that the system was installed and tested per the applicable standard
The Certificate of Completion documents that the fire alarm system was installed, tested, and verified to meet the requirements of NFPA 72.
Question 3: Under most state licensing laws for alarm contractors, which action would likely result in license revocation?
- Installing a system without a permit in a jurisdiction that requires one (Correct answer)
- Using manufacturer-approved substitutes
- Hiring a trainee to assist on a job
- Submitting as-built drawings after final inspection
Correct answer: Installing a system without a permit in a jurisdiction that requires one
Installing an alarm system without a required permit is a serious violation that can lead to license suspension or revocation under state contractor licensing laws.
Question 4: In the context of alarm industry compliance, what does 'false alarm reduction' ordinances primarily regulate?
- The type of equipment that can be used
- The fees and penalties assessed to properties with excessive false alarms (Correct answer)
- The hours during which alarms may be monitored
- The certification level required for technicians
Correct answer: The fees and penalties assessed to properties with excessive false alarms
False alarm reduction ordinances typically impose fines or service fees on premises that generate excessive false alarms to incentivize proper system maintenance.
Question 5: According to NFPA 72, how often must a fire alarm system initiating device (such as a smoke detector) undergo sensitivity testing?
- Every 6 months
- Every year
- Within 1 year of installation and every 2 years thereafter (Correct answer)
- Only when the AHJ requests it
Correct answer: Within 1 year of installation and every 2 years thereafter
NFPA 72 requires sensitivity testing of smoke detectors within the first year of installation and at least every two years after that.
Question 6: When a technician encounters a situation where local codes conflict with NFPA 72, what is the correct approach?
- Always follow NFPA 72 since it is a national standard
- Follow the more stringent requirement and consult the AHJ (Correct answer)
- Ignore both and follow manufacturer guidelines
- Apply whichever standard was adopted most recently
Correct answer: Follow the more stringent requirement and consult the AHJ
When conflicts arise, the technician should follow the more stringent requirement and seek clarification from the AHJ to ensure compliance.
Question 7: What is the primary purpose of alarm system licensing at the state level for alarm companies?
- To generate state revenue through application fees
- To ensure companies and technicians meet minimum competency and background standards (Correct answer)
- To limit competition in the alarm market
- To require use of state-approved equipment
Correct answer: To ensure companies and technicians meet minimum competency and background standards
State licensing ensures alarm companies and technicians meet minimum standards of competency, training, and background screening to protect consumers.
Which NFPA standard specifically addresses the installation and testing of fire alarm and signaling systems?