Air Conditioning Repair Refrigeration System Repair 3 — Questions and Answers
Question 1: What does a high subcooling reading combined with high discharge pressure most likely indicate?
- Low refrigerant charge
- Non-condensables in the system (Correct answer)
- Faulty TXV
- Low condenser airflow
Correct answer: Non-condensables in the system
Non-condensables such as air in the system raise discharge pressure and subcooling because they occupy condenser space without condensing.
Question 2: When recovering refrigerant from a system, the technician must use equipment certified to which standard?
- UL 94
- SAE J2788 (Correct answer)
- ARI 700
- UL 1995
Correct answer: SAE J2788
SAE J2788 certification is required for refrigerant recovery/recycling equipment used on motor vehicle AC systems; EPA Section 608 requires similar certification for stationary systems.
Question 3: A tech notices the evaporator coil is freezing up only at the inlet. What is the most likely cause?
- Overcharge of refrigerant
- Low airflow across the evaporator
- Metering device feeding too much refrigerant (Correct answer)
- High suction superheat
Correct answer: Metering device feeding too much refrigerant
When the metering device feeds excessive refrigerant, it floods the evaporator inlet, causing ice formation at the entry point where liquid refrigerant accumulates.
Question 4: What is the minimum evacuation level (microns) typically required before recharging a residential air conditioning system?
- 10,000 microns
- 5,000 microns
- 500 microns (Correct answer)
- 100 microns
Correct answer: 500 microns
Industry standard requires pulling the system down to 500 microns or below to ensure adequate moisture and air removal before charging.
Question 5: A compressor has a burnt motor winding. After replacing it, what additional step is critical before restarting?
- Adding extra oil to the compressor
- Flushing the system to remove acid and debris (Correct answer)
- Increasing refrigerant charge by 10%
- Bypassing the crankcase heater
Correct answer: Flushing the system to remove acid and debris
A burnt motor leaves acid contamination that must be flushed out and a liquid-line suction filter-drier installed to prevent damage to the new compressor.
Question 6: Which type of oil is used in systems charged with R-410A refrigerant?
- Mineral oil
- Alkylbenzene oil
- Polyol ester (POE) oil (Correct answer)
- Polyalkylene glycol (PAG) oil
Correct answer: Polyol ester (POE) oil
POE oil is required in R-410A systems because it is miscible with HFC refrigerants and properly lubricates the compressor throughout the system.
Question 7: What does a negative superheat reading at the evaporator outlet indicate?
- Metering device is underfeeding
- System is low on charge
- Liquid refrigerant is leaving the evaporator (Correct answer)
- Condenser is oversized
Correct answer: Liquid refrigerant is leaving the evaporator
Negative superheat means the refrigerant temperature at the evaporator outlet is below saturation temperature, indicating liquid refrigerant is leaving the coil.
What does a high subcooling reading combined with high discharge pressure most likely indicate?